Moisture Content in Compressed Air

03/04/2014 11:50 AM

Hi

I need help to calculate ppm level of moisture in compressed air at 7 bar pressure and ambient temperature . the compressor have dessicant dryer designed for -20 Deg C Pressure Dew point. The temperature of air at outlet is 40 Deg C.

It is further cooled down by refrigerated dryer to below 10 Deg C.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: moisture content in compressed air

03/04/2014 12:13 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13
In reply to #1

Re: moisture content in compressed air

03/05/2014 11:24 AM

That set of equations and graphs may tell you the water vapor density, so I guess you are supposed to figure out the mass content from the ideal gas law or other equation of state for water vapor, where the partial pressure is known in a control volume?

Somewhere, I saw tables that reveal the saturation moisture content in g/m3. Try:

http://www.fstweb.de/Water-vapour-content-table.170.0.html?&L=1 and then use the relative humidity to get an idea of how much mass is present.

Example: at 30°C, 30.078 g/m3 represents 100% humidity. If the ambient humidity is 45%, then moisture content I estimate to be 13.5 g/m3 . Seems rather straightforward to me, until another "guru" corrects me on that.

Since the air dryers discharge some condensed water, I suppose you could try to collect this, but I expect the air behind it will spray it out of the container. There are moisture detectors for compressed air. Get one.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Power-User

Join Date: Mar 2011
Posts: 238
Good Answers: 14
#2

Re: Moisture Content in Compressed Air

03/04/2014 2:48 PM

I would think it should be measured, not just calculated.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Moisture Content in Compressed Air

03/04/2014 6:40 PM

Well, it would rather depend upon the atmospheric conditions, the pressure and the temperature of the air upstream of the compressor, which details haven't been stated in the original post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 12
#9
In reply to #3

Re: Moisture Content in Compressed Air

03/05/2014 9:47 AM

Thanks , the atmospheric conditions are 30 Deg C, pressure at upstream is atmospheric

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Moisture Content in Compressed Air

03/05/2014 9:53 AM

Oh, good. Follow #8 below for a Job Done Sticker.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Moisture Content in Compressed Air

03/04/2014 11:13 PM

It will depend on how wet the air going into the compressor is.

Is that desiccant dryer on the suction or HP side of the compressor? How is that desiccant drier reactivated?

Calculating...not sure. Measurement would be the better bet.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#5

Re: Moisture Content in Compressed Air

03/05/2014 12:05 AM

The weight of the water that you put into the compressor will be equal to the weight of the water that you get out or the compressor. Take the tables for relative humidity, temperature, volume of air and calculate it.

The performance of the desiccant dryer is dependent on several things. There should be a performance curve by the manufacturer that will show you its efficiency. Also put the refrigerated dryer before the desiccant dryer. It will extend the cycle of the desiccant dryer so that it doesn't have to be regenerated as often. This will also reduce the moisture in the compressed air.

Combine the two and you have your answer. Better answer could be obtained if more information was given in original posting. Such as what is the volume of air being handled?

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Moisture Content in Compressed Air

03/05/2014 12:25 AM

Concur with you on the order of placement for the 2 drying processes. That's why I asked where the desiccant doohickey was actually located.

Where's that OP?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Moisture Content in Compressed Air

03/05/2014 6:22 AM

Probably drying out somewhere...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#12
In reply to #6

Re: Moisture Content in Compressed Air

03/05/2014 10:18 AM

Wal-

Good questions! Better answers if more information was given.

The placement of the desiccant dryer should be in the discharge line as the final treatment after a filter, a automatic condensate drain, the refrigeration dryer and then finally the desiccant dryer. If the drying is done on the inlet you have to use a lot of drying power to get the water vapors out of the air.

When the drying is done after the compressor, the compression of the air/water vapor makes much of the water vapor turn to liquid because of the increase in pressure. That pressurized water condensate is easy to reduce by simply using an automatic condensate drain, a simple mechanic means. It is a unit that uses no energy and will do a better job than the desiccant dryer on the inlet and need no regeneration.

It would also be prudent to locate other condensate drains within the system piping at appropriate locations. With this, if there was a dryer failure the moisture that got into the system could be removed automatically instead of having to do it manually or left in the piping where it could possibly do damage to other equipment.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Moisture Content in Compressed Air

03/05/2014 8:37 AM

Do it the same way as any Process Engineer would: carry out a mass balance between all the inlet streams and all the outlet streams.

Simples!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#11

Re: Moisture Content in Compressed Air

03/05/2014 9:56 AM

As the water vapour in the atmosphere is not likely to be below 12.5%RH you can assume the air when compressed to 7 bar and over will be fully saturated at 100%RH

You need to look up water density v temperature tables for the exact amounts.

When leaving the compressor at 40°C, the air will hold 51 g/m3 plus any surplus water as a liquid. 40°C is hot - you need an after-cooler to protect the fridge dryer.

(Borrowed from Wiki) T = temp in K. M = molar mass = 18 for water.

ppm = mg/m3 x 0.08205 x T/M

Therefore 51 g/m3 is 73,000 ppm at 40°C (in round figures)(watch the base units)

Generally speaking, ppm is not much use in everyday practical terms.

Dropping the temperature to 10°C reduces the vapour to 9 g/m3.

Leaving 1 g/m3 at -20°C when the desiccant does it's job.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#14

Re: Moisture Content in Compressed Air

03/05/2014 3:25 PM

Since this is a calculation it's on paper. The lowest temperature is -20C which is the ideal working specs of the desiccant dryer. If you look up the % of moisture in tables of dew points. You will find that the moisture content is 0.1%. Percent is just parts per hundred so an easy conversion to ppm. 1000 ppm

This figure is only good on paper. It has no real value in a working system. To many variables and nothing works ideally. If you want to an accurate measure you have to test the air.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"