Power cable and control cable in the same trench

06/15/2007 10:08 AM

hi, i am mad with our contractor to lay 10.5kv cable and control cable in the same trench... to me it's against electric code (BS, IEC) besides there is safety issue, however, the contractor doesn't want to seperate saying they have kept a distance according to Chinese electric code which I have no idea. any advices?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#1

Re: Power cable and control cable in the same trench

06/15/2007 1:15 PM

It's certainly not best engineering practice.


Have you tried bribing him?

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: Power cable and control cable in the same trench

06/15/2007 11:50 PM

First of all, look in the Chinese electric code to see if he's telling the truth. cnpower might have an answer to that.

In any case 10.5kV would probably require a very large separation distance from the control cables. We use three feet of separation between 440V and control cables so 10.5kV would probably require several dozen feet of separation!

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Participant

Join Date: Jun 2007
Posts: 2
#3

Re: Power cable and control cable in the same trench

06/16/2007 2:01 AM

Laying of control cables and power cable are not at all advisable, we have suffered a lot in Our Copper and aluminium rolling mills, we found abnormal hunting, we have checked the each and every hydraulic systems, etcc.... , after so much time loss finally we have detected problem is at electrical trench ,we have separated both the lines till then no such problems. any how application and accuracy of the process and your equipment senciblily influence this subject.

K.Srinivas.

Sr.Vice President (Manufacturing)

Register to Reply
Power-User

Join Date: Nov 2006
Location: SE MI USA
Posts: 105
#4

Re: Power cable and control cable in the same trench

06/16/2007 6:38 AM

Withhold some payment and tell him you're going to back charge him when it doesn't work and you have another vendor come in and do it right.

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#5
In reply to #4

Re: Power cable and control cable in the same trench

06/16/2007 1:05 PM

Electromagnetic Shield wrapped around control cables-if lead sheath is not enough- should keep every one happy.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Power cable and control cable in the same trench

06/18/2007 5:10 AM

It depends on the signal in the control cable and the structure of the cable. 4-20mA analog signals in shielded cable as either singles or multipairs are largely immune. If the cable is unshielded and carrying some elegant data signal then it's certainly not good practice. Most codes go for a separation distance and require crossings to be made at right angles.

Where is the cable supposed to run, and was the contractor instructed to do that instead of how it turned out? If so, then the contractor re-runs it in the previously-instructed manner at his expense before the final invoice is paid. If not, then the contractor is entitled to an 'extra' for re-running the cable in the manner that he wasn't told about prior to installing it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#7

Re: Power cable and control cable in the same trench

06/18/2007 8:11 AM

The best way to solve this would be to calculate the coupling impedance between the two cable systems.

Than you will calculate the induced voltage. If the calculated voltage exceeds the maximum cable strenght to 60 Hz aplied voltage, then you cannot allow him to install the cables this way.

In some cases, a possibility is to install barriers between the two systems.

But certainly the best way would be to install the two cable systems in different trays.

Regards

Register to Reply
Guru
United States - Member - I am a Yankee Doodle Boy. Engineering Fields - Manufacturing Engineering - Old School is the best school. Safety - ESD - Safety Mgr that keeps the peace Hobbies - DIY Welding - My Motto:

Join Date: Jan 2007
Location: Broken Arrow, OK, USA
Posts: 838
Good Answers: 26
#8

Re: Power cable and control cable in the same trench

06/18/2007 9:23 AM

I would have to say NO!!

If you run the control cables with the power cables you will get reference noise in the lines. Especially if your running VFD's off the controls. It causes a lot of difficulty when the are run in close proximity of one another and the signals will most definately get confused mainly from the EMF caused by high voltage.

__________________
If necessity is the mother of invention then is laziness the mother of necessity?
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 16
#9

Re: Power cable and control cable in the same trench

06/21/2007 8:08 PM

thanks all for the suggestions, now we requested our contractor to ensure good shield cable for data link, and we are checking the Chinese electric code.

another question: we asked the contractor to use twisted screen cable for data link, however, the contractor comes out with shield non-twisted cable, they say the shield cable (cables wrapped with a thin layer of copper) is better than the screen cable because there is "no leaking" comparing to the screen cable??? it such comment true? any advice?

Register to Reply
Power-User

Join Date: Jul 2006
Posts: 295
Good Answers: 4
#10
In reply to #9

Re: Power cable and control cable in the same trench

06/28/2007 11:19 AM

I always understood that twisted pair was intended as a less expensive alternative to shielded cable, meaning that if they prefer to use shielded cable for no additional cost that would be better. (maybe the shielded cable was left over from some other job so they don't need or want to buy twisted pair)

As for the 2 cables in the same trench, don't let them bury it until it has been proven to work to specs. If it doesn't work as specifieded it is easy to pull the control cable out of the trench creating the separation you have recommended and see if that makes it work.

Register to Reply
Anonymous Poster
#11

Re: Power cable and control cable in the same trench

06/30/2007 12:26 PM

My suggestion would be.

1) don't bury the lines until it is tested so that cables are taken out.

2) Shieldedcable sfor control cables should be ok.

3) Try to separate them with barricade wherever possible with physical distance.

4) TRY TO AVID IF AT ALL POSSIBLE AND CHECK THE CHINES E CODES.