Exposed Installations on Ceilings

04/26/2014 12:25 AM

Hi dears,

At ceilings of basements of residential and commercial buildings , the design shows that

all installations shall be of the exposed type ( surface and pending mounted ones ).

I know that the levels of the installations are to be coordinated on site.

As usual , the trades are : Lighting Fixtures , Air conditioning Ducts , Fire Fighting Pipes,

Cable Trays of Power and Low Current Systems , Water Pipes , Fire Alarm

Devices ..... Etc.

The Question is : Are there any recommendations and / or particular considerations

are to be taken into account in this respect?

For example : the inverted height level of the Light Fixtures is to be adjusted

in a manner that none of the other installations is to be in contradiction with

the light angles ?

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Exposed Installations on ceilings

04/26/2014 12:38 AM

Yes.

Depends who installs last.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#2

Re: Exposed Installations on ceilings

04/26/2014 2:39 AM

It depends on the:

1) MEP (Mechanical, electrical and plumbing) coordination.

2) Electrical should take precedence/

3) An electrical composite or coordination drawing must be prepared

4) An electrical engineer or the drafting supervisor must adjust position of the overlap components etc.

5) Etc.

__________________
--
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#6
In reply to #2

Re: Exposed Installations on ceilings

04/27/2014 4:12 AM

< 2) Electrical should take precedence>

We normally gives priority to drainage.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#7
In reply to #2

Re: Exposed Installations on ceilings

04/27/2014 9:23 AM

The general "rule of thumb" is that the services most difficult to relocate or location being critical are given higher priority in their location. Some, such as VHAC are bulky and very inflexible. Similarly some others would be drain lines from storm drains or sewage. These are normally dependent on gravity or distances to work correctly. Plumbing supply lines are usually pressurized so they can normally be located anywhere. The numerous types of fittings, including some flexible ones, facilitates rerouting normally easily. If draining of lines is necessary adequate space for personnel to reach fittings is necessary.

Piping such as compressed air which accumulates water must be piped for proper drainage and removal of condensate from the piping. It can though be located in a relatively easy manner due to available flexible fittings.

Electrical wiring can normally be located anywhere there is adequate space. Since it is not dependent on gravity, it can be located almost anywhere that conditions permit. There are a proliferation of flexible fittings and techniques available to make most installation feasible. Conduit and EMT can be bent with a bender or a hickey to take almost any shape. There are also flexible conduits and armor such as BX that are extremely flexible. In many locations rubber insulated cords can be used if permitted by building codes.

If in question, consult an engineer of the applicable service or an inspector.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#3

Re: Exposed Installations on Ceilings

04/26/2014 10:37 AM

Yes. Check the local building codes. If not available check with the town/city building inspector of the appropriate trade.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Exposed Installations on Ceilings

04/26/2014 2:28 PM

Higher priority usually goes to items that are large and or geometrically critical, such as ductwork and grade-sensitive plumbing. Other piping, electrical raceways, and larger conduits would be intermediate. Small conduit and wiring have lower priority, because they are relatively easy to route around other obstacles.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#5
In reply to #4

Re: Exposed Installations on Ceilings

04/26/2014 11:30 PM

Tornado is generally correct. You do have to honor the larger mechanical trades, simply because they require the most real estate; but astheticlly the designers will want to have a say as to location of lighting fixtures and where smoke detectors should go. And of course codes determine where several things have to be. Alan

Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#8

Re: Exposed Installations on Ceilings

04/28/2014 11:40 PM

All depends upon the site condition except for drainage (plumbing and equipment drain such as hvac, air compressor etc).

Light fixtures; better to consider to match with services having the lowest IL (Invert Level).

Air Conditioning Duct: can be adjusted according to the other services; but keep clearance around the duct for maintenance due to air leakage especially at corners and tap offs.

Fire Fightings, Water Pipes, Fire Alarm: can be adjusted according to the other services; but consider accessibility to all operating devices such as valves, measuring meters etc.

Electrical Cable Tray for Power & Low Current; Provide as low IL as possible because frequent additional works are expected along the tray for extra cabling. But some Utility Provider does not allow to run any other service above or below their HV Cable route, if it is happened to run its pathway through basements. This has to be considered during the installation of drainage system. All other services can be coordinated according to their requirements.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#9

Re: Exposed Installations on Ceilings

05/03/2014 11:35 AM

The best design engineers will have the layout completed for the location of all the trades.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abasins (1); lyn (1); Munster (1); Musthafa (2); old salt (2); Tornado (1)