Anonymous Poster #1

Low Current, High ACB Rating

08/03/2014 5:01 AM

I have got a panel of ACB incomer as 2500 A SIEMENS 3WT 52 5UB04 5AB2.Since the load is only 350 A we want to set the release to 350 A.The local siemens engr saya not possible adn recommends to replace the breaker.

Any suggestions

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 5:24 AM

The current sensing elements used inside of that breaker that give info to the trip unit are accurate within a range that goes down to 40% of the maximum setting. So a 2500A breaker will have sensors that can be used down to 1000A. Below that, the output value of the current sensors, like CTs, becomes such a small value that it cannot be effectively used.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 5:45 AM

The local Siemens engineer knows what he's talking about. Replace the breaker.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 6:16 AM

In addition to what JRaef says, there is a risk of the ACB getting into the "critical current" zone. Not that it is very likely in this case, the numbers don't seem to indicate that. However, every switching device has a critical current, whose value is much lower than the max short circuit current, but which the device struggles to break. Mainly because the magnetic forces are too weak to blow the arc away, and the arc persists. Most easily seen in fuses, where the standards specify a test for I2, the critical current, at which the arcing I2t is the maximum. Prudent for you to use a properly sized breaker.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 6:44 AM

What is the cable rating? The breaker is there to protect the cable!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Feb 2009
Posts: 16
#6
In reply to #4

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 10:30 AM

We have 3 runs of 400sqmm copper cable.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 11:49 AM

3 runs of 400 mm2 for 350A? i sure am missing something here

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 1:03 PM

His wiring is well protected with 350 AMP breakers.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 1:15 PM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#11
In reply to #7

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 2:18 PM

On that basis he does not need to reduce his breaker setting. I have no idea why he should want to, then I'm funny that way.

__________________
Good moaning!
Reply
Active Contributor

Join Date: Feb 2009
Posts: 16
#14
In reply to #11

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 9:26 PM

The utility services demand it.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#28
In reply to #7

Re: LOW CURRENT ,HIGH ACB RATING

08/09/2014 2:16 AM

That too, Copper!!!!

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 9:12 AM

Buy the correct panel.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10

Re: LOW CURRENT ,HIGH ACB RATING

08/03/2014 2:03 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12

Re: Low Current, High ACB Rating

08/03/2014 8:47 PM

For some strange reason I'm confused by the OP's reasoning in this decision.

Although 3 x 400mm² is small for 2500A, they're ridiculously over sized for 350A

__________________
The reports of my death are greatly exaggerated.
Reply
Active Contributor

Join Date: Feb 2009
Posts: 16
#13
In reply to #12

Re: Low Current, High ACB Rating

08/03/2014 9:18 PM

The setup was for higher currents. Is it possible to modify the ACB for current loads?

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#15

Re: Low Current, High ACB Rating

08/03/2014 11:29 PM

Try to install additional CT in the circuit of ratio 400/1. Have Simple IDMT relay similar to CDG31 relay. Wire up the relay to Shunt trip coil of ACB. This will retain your ACB intact so that in case you revert back to your original load of 2500A you can restore. This suggestion will not cost much comparing to cost of replacement of ACB.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2009
Posts: 16
#16
In reply to #15

Re: Low Current, High ACB Rating

08/03/2014 11:34 PM

Can we use an Overload relay instead ?

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#17
In reply to #16

Re: Low Current, High ACB Rating

08/03/2014 11:40 PM

HIRE AN ELECTRICIAN.

You really need one.

Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#18
In reply to #16

Re: Low Current, High ACB Rating

08/03/2014 11:42 PM

Indicate type and make of overload relay.CDG31 type relay will protect over current, earth fault and more reliable than bimetallic overload relays.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#19
In reply to #15

Re: Low Current, High ACB Rating

08/03/2014 11:48 PM

When a high (fault)current flows, 400/1 CT will burn.

__________________
pnaban
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#20
In reply to #19

Re: Low Current, High ACB Rating

08/04/2014 12:28 AM

It is more likely to saturate. Not burn.

However, the OP does not seem to be reading all the posts. He seems to be only concerned with using a cheap bimetallic overload relay in combination with a suitable CT and make do.

Like buying a Ferrari, and running it on kerosene.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
2
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#21

Re: Low Current, High ACB Rating

08/04/2014 4:10 AM

In forty years as an electrical engineer I have never come accross a customer who can reliably predict what his power usage will be 5 years ahead. Leave the existing breaker in place and add a second series breaker to cope with your 350A load. You then have the option of adding further loads in the future. As the alternative option is to purchase a 350A breaker there is no cost penalty going with this solution.

Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#22
In reply to #21

Re: Low Current, High ACB Rating

08/04/2014 10:01 AM

That makes perfect sense!

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#23
In reply to #21

Re: Low Current, High ACB Rating

08/04/2014 11:32 AM

Instead of in series if you put in parallel,you can any of the two according to the load

__________________
pnaban
Reply Score 2 for Off Topic
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#24
In reply to #23

Re: Low Current, High ACB Rating

08/04/2014 12:08 PM

NO! If connected in parallel, most of the current will pass through the larger breaker, because it has heavier conductors. Because of interconnection variations, it is impossible to predict what fraction of the total current will pass through each breaker, but the smaller breaker will certainly not open until the total current is several times the rating of the smaller breaker.

In series, all of the current must pass through both breakers, but since the larger breaker has heavier conductors, and is set to open at a much larger current, It is essentially just a short piece of heavy wire, and the lower current breaker will always be the one to open in case of an over-current.

In the original post you said the load was 350 Amps, so you were considering a 350 Amp breaker. There must always be some room for variation. For a 350 Amp load, you need at least a 400 Amp breaker.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#25
In reply to #24

Re: Low Current, High ACB Rating

08/04/2014 12:17 PM

In my comment(23) the word "select" was omitted.You can select any of the two CBs according to the load.

__________________
pnaban
Reply
Active Contributor

Join Date: Feb 2009
Posts: 16
#26
In reply to #25

Re: Low Current, High ACB Rating

08/04/2014 1:06 PM

I am considering to add 500 A cts, which will be hooked on to the electronic release of the breaker.i suppose that should work. Only problem Siemens ct for that rating doesn't fit on the busbars.

Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#27
In reply to #25

Re: Low Current, High ACB Rating

08/04/2014 1:15 PM

To 'select' one or the other would require either major switching or rewiring. Since you mentioned bussbars, the lower current CB probably won't connect to them correctly anyway. You must do some rewiring/rerouting.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Reply to Forum Thread 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); dkwarner (2); electricalexpert65 (1); jhhassociates (1); JohnDG (1); JRaef (1); kvsridhar (4); lyn (4); pandan27 (5); pnaban (3); PWSlack (1); ramvinod (2); SolarEagle (1); TonyS (1)

Previous in Forum: AVK Alternator 1240 kva Type DIDBN 130H/10   Next in Forum: Earthing Of Pump And Vessel

Advertisement