24 VAC

09/05/2014 9:24 AM

We have a favorite tank light manufacturer with whom we keep making the same mistake. They offer a halogen light in both 24VDC and 24VAC. Engineering specifies 24V and the order gets processed for the AC version every time. (I know - it's time we learn better)

My question concerns the availability of the 24VAC light. Next time I build a process skid or control panel with 24VAC in it, and it's been 25 years of doing so, it will be the first time. Who uses 24VAC control voltage????

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: 24 VAC

09/05/2014 9:58 AM

24VAC is used a lot on equipment that has no electronics. Just relays. Cuts cost. Transformer is less expensive then a DC power supply.

If the engineers just specify 24V shouldn't AC or DC both work? They didn't specify one or the other.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#2
In reply to #1

Re: 24 VAC

09/05/2014 10:05 AM

Well we're (I and my fellow workers) the "engineers" and we want the 24VDC version. We just are stupid and forget to mark it correctly. Don't know why the AC version doesn't work on DC. You would think that wouldn't make a difference to a resistive load, would you?

I got one here right now - I can try test this.

Relays only - makes sense.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#14
In reply to #2

Re: 24 VAC

09/06/2014 5:22 AM

There is no reason of which I am aware as to why a standard Halogen globe will not work on AC or DC. There is some argument that DC causes a bit more migration of the tungsten, but this would not stop it from working at all as seems to be your problem.

The only concern associated with DC operation is that, should the filament break, then the globe may arc between the internal posts, which can draw quite high currents, so adequate fusing is advisable.

I assume that there is no soft start circuitry involved here so is it possible that the globe incorporates half wave rectification (don't ask me why - maybe for lamp life (not sure this would work as the globe glass may not then get hot enough to recycle the tungsten) or maybe it's for colour rendition?), but this is the only reason that I can see why the globe would not work on DC. Try reversing the connections to the globe and see what happens, alternatively meter the terminals of the globe for continuity.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: 24 VAC

09/05/2014 10:14 AM

I'm dropping back to some of my fading chemistry/physics schooling memories but the only thing different I would expect a halogen light would care about AC or DC supply would possibly be filament vaporization. Thus the lifetime of a lamp maybe attenuated if using the wrong type. The inductance impedance current limiting of a filament would not make much difference in the current draw.

As for 24 VAC as a control voltage, I've only seen it done with some very simple process control systems that required just a few relays and switches for use. With the drop in price of switching supplies today a simple 24 VAC transformer can be more expensive.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#6
In reply to #3

Re: 24 VAC

09/05/2014 10:42 AM

I was afraid in reality it was a 12V bulb with internal circuitry in the housing - nope. It works fine on 24VDC. Problem we have now is we have customers that particular they will insist on a label on the fixture that says 24VDC.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#12
In reply to #6

Re: 24 VAC

09/06/2014 12:38 AM

Boy, do you have OCD customers!

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#10
In reply to #3

Re: 24 VAC

09/05/2014 11:42 PM

For information on 24VAC controls ask an electrician who is at least 55 years old. If he worked on controls 30 years ago, 24VAC is what was almost always used. There were very few solid state controls at that time and the systems entailed mostly relays and step-down transformers with a whole lot of push button switches. The machine transformers were usually very big due to the many taps both on the primary and secondary. They supplies a lot of current so that was a big weight and size contributor.

If you ever come across one of those transformers they can easily be made part of a high current battery charger (lead-acid), a bench top low voltage high current linear power supply, door weights or row boat anchors. Just don't drop it on your foot!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Popular Science - Weaponology - New Member Engineering Fields - Engineering Physics - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Dec 2007
Location: No. VA, USA (No, it does NOTu mean "won't go"!)
Posts: 1796
Good Answers: 75
#11
In reply to #10

Re: 24 VAC

09/06/2014 12:23 AM

And be careful not to short one out. They don't burn very well, but the oil used to cool them makes a LOT of really smelly smoke!

Ask me how I know!

__________________
Been away a while. Miss all my old friends. Some of you I KNOW are still around. Where are the rest?
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4

Re: 24 VAC

09/05/2014 10:33 AM

OK, I've done a little searching to find the difference in driving a halogen lamp with AC or DC, and so far all I've found is hearsay. Does the electric field influence where the tungsten bromide disassociates and deposits tungsten back on the filament? Or what is the difference?

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7
In reply to #4

Re: 24 VAC

09/05/2014 10:44 AM

See response to post before you - only difference is the model number and posted voltage on the housing. As I stated to Redfred - we have customers that will find the label and insist on changing it.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: 24 VAC

09/05/2014 10:34 AM

Sometimes in marine or dockside locations, 24VAC controls are used to minimize shock hazards from pendant stations and the like. A small control transformer (say 480/24 or 240/24) provides the lower voltage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#8

Re: 24 VAC

09/05/2014 2:12 PM

Pretty much all of the home and business Central AC and Heating systems installed in the US use 24VAC.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#19
In reply to #8

Re: 24 VAC

09/12/2014 2:42 PM

Yes. And do they have need for a tank light in these systems?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#20
In reply to #19

Re: 24 VAC

09/12/2014 4:34 PM

Your question was "who uses 24vac control voltage?".

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
Popular Science - Weaponology - New Member Engineering Fields - Engineering Physics - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Dec 2007
Location: No. VA, USA (No, it does NOTu mean "won't go"!)
Posts: 1796
Good Answers: 75
#9

Re: 24 VAC

09/05/2014 11:19 PM

Without regard to the availability of 24VAC lights, I seem to remember that one reason automotive bulbs (All running on DC) have a problem with filament notching that causes them to require a more robust filament (meaning one that provides less actual light at a specified voltage, since the filament is thicker, and designed not to get AS hot). If you run that bulb on AC (same voltage), it will provide more light for longer without replacement.

But my memory may be faulty. I can't right now remember why it might develop filament notches, and thus weak spots in the filament.

Anyone else remember hearing this, or know why it might happen?

__________________
Been away a while. Miss all my old friends. Some of you I KNOW are still around. Where are the rest?
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#16
In reply to #9

Re: 24 VAC

09/09/2014 2:28 PM

Yeah - you're right. the cheap thermostat in my house runs on 24VAC - forgot about that.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#17
In reply to #16

Re: 24 VAC

09/12/2014 2:33 PM

how about the door bell?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#18
In reply to #17

Re: 24 VAC

09/12/2014 2:40 PM

Yes, door bells are 24VAC, but when do we use a tank light in a house? I am trying to figure out what industry needs a tank light and still uses 24VAC instead of 24VDC.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#21
In reply to #18

Re: 24 VAC

09/12/2014 5:27 PM

There appears to be an obsession here with the tank light needing to be DC.

If I were designing the system, then I would most likely use AC if the light was the over-riding consideration and provided it fitted with the electrical requirements of the other equipment. Does the rest of your componentry particularly require DC?

Contrary to what has been said here, lots of electronic circuitry, both basic and complex, uses AC input and control, I personally prefer it when using SCRs as it provides a convenient switch off method on the negative half cycle. For example, quite a few commercial switch mode power supplies are designed around an AC input for this very reason of easy control, they just won't work with a DC input.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#22
In reply to #21

Re: 24 VAC

09/15/2014 8:38 AM

I am a process skid controls engineer and heavily into analog instrumentation. AC is not a good thing with 4-20ma control. I can't even run it in the same wireway and have to segregate in the panel. Nearly everything we build has a PLC involved somewhere, if not on the immediate piece of equipment we are building, definitely somewhere nearby and our equipment will be connected to it, and ALWAYS some 4-20ma instrumentation on it. The tank in question with the 24VAC light has a temperature transmitter, a level transmitter and a pressure transmitter running on 4-20ma loop power and a point level with 24VDC signal. This is very common in the pharmaceutical and bio-tech industries.I sure don't want to run another conduit up the side of the tank and install a stepdown transformer in my panel for one piece of equipment.

The question here was who still uses 24VAC control, as I don't ever see it in the above mentioned disciplines, nor in the occasional food processing industry skids we get either. I haven't seen any analog instruments running AC lately, and all the discrete instruments we use are generally 24VDC. I can see where these could be 24VAC, but I never see them.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#23
In reply to #22

Re: 24 VAC

09/15/2014 11:02 AM

Material Handling Equipment. Example trash compactors, balers and elevating docks use 24VAC where it may be a hazard to the operator to run higher voltage. Like a remote switch out in the weather. A lot of time these panels are the same so the design is for one panel to fit all applications.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#24
In reply to #23

Re: 24 VAC

09/15/2014 11:15 AM

Thank you. To that I'll reply as to several before you, "where is there a need for a tank light in those applications?" This is most definitely a sanitary design for use with tank sight glasses. I still don't see any uses listed that would require a sanitary tank light, and 24VAC wiring. Perhaps the elevating dock people can use it? Think it would be a tad bit weak on lumens for this operation.

Still looking for where there is an industry using 24VAC and requiring sanitary tank lighting.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#13

Re: 24 VAC

09/06/2014 2:53 AM

Stepping down the 220V or 110V AC to minimal magnitude for safety and significant value just for activation gases of light bulbs is reasonable. Putting up a rectifier and filter on the supply adds up inefficiency or losses of electrical energy, when all your goal is to activate the gas filled bulb to produce photons. Operating at lower AC voltage is material wise and cost wise also, wouldn't it. It depends on its use. 24 AC is not commonly used to industrial process instruments so to speak.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#15

Re: 24 VAC

09/06/2014 11:09 AM

I would think that the manufacturer would rate their lights 24 V AC/DC.

Now, there is no difference in using AC or DC. DC MIGHT cause the lamps to last longer. Certain sensors can pick up the intensity variations of AC. Low voltage lamps tend to me more vibration resistant. I used a lot of ELH 120 V Halogens on AC and DC and EYC low voltage Halogens on DC for doing measurements on sensors.

What COULD be different is the switch and switch protection. Not all switches can switch DC.

Ask them what the difference is. Take on apart and compare the switch and switch protection components.