Sensor For Zinc Plating Fumes

09/09/2014 4:16 AM

We have a zinc plating line with a large extraction fan motor. I would like to add a variable speed drive to the motor but I'm unsure what sensor is required.

What type of sensor is required to sense the fumes of zinc plating?

Register to Reply
Pathfinder Tags: sensor zinc plating
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Sensor for zinc plating fumes

09/09/2014 4:38 AM

I would approach one or more companies that produce gas-detecting instruments for such places as mines and confined spaces. Some that come to mind include Bacharach, Beckmann, Drager, Ex-tech, Manning, and MSA (Mine Safety Appliances). If they don't have what you need, they might still offer good referrals.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Sensor for zinc plating fumes

09/09/2014 4:54 AM

A zinc plating fume sensor will work.

Now really, if your company is so desperate to save a few pennies that they would spend money to vary the speed of a safety exhaust fan, I'd quit.

How long will it take to recover the cost of the sensor/VFD speed controller/installation/maintenance and replacement as needed of the whole speed controller system?

The costs probably won't be recovered before it fails and kills someone.

Bad idea!

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Sensor for zinc plating fumes

09/09/2014 6:16 AM

A sensor is not required unless the fan speed is to be varied continuously. It is possible to vary the fan speed without feedback by using the manual function of the drive, possibly putting upper and lower limits in the parameters.

Before doing any of this, though, it is best to do a cost-benefit analysis to obtain a buy-in for the proposal. It starts by writing a short statement, say no more than 500 words, as to why the current situation is unacceptable and what needs to be done to improve it. Then publish it internally so as to obtain buy-in.

It's time to look at the issue from a helicopter, so to speak, rather than on the ground.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: Sensor For Zinc Plating Fumes

09/09/2014 10:11 AM

What makes you think the ventilation exceeds requirements?

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2011
Posts: 11
#6
In reply to #4

Re: Sensor For Zinc Plating Fumes

09/10/2014 8:34 AM

Thank you for all your excellent replies.

I think the ventilation exceeds requirements because we can switch it off for about 15 minutes before you can smell the fumes.

Also, we only work 12 hours per day, 5 days per week. In my opinion the ventilation could be reduced during the off hours.

I fully understand all the safety aspects raised - safety comes first.

Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#5

Re: Sensor For Zinc Plating Fumes

09/10/2014 5:56 AM

The sensor required is the one that indicates that the fan is off which should trigger an evacuation alarm. The sensor needs to sense movement of the fan.

Switching off the fan is not permitted.

Running slower than needed to exhaust all the fumes should be indicated by a secondary alarm.

Switching off the fan is not permitted.

A process evaluation will tell you what the require exhaust flow rate is. Ask the process engineer.

From earlier posts you are the electrical engineer which should not alone decide about critical safety equipment.

Switching off the fan is not permitted.

Unless

The zinc plating line is idle or at halt.

__________________
Common Sense Dictates
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#7

Re: Sensor For Zinc Plating Fumes

09/10/2014 11:45 AM

You shouldn't rely on the sensing of fumes to control the extractor; if you have to save on energy consumption, consult with EHS about using an OMRON 24/7 timer.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#8

Re: Sensor For Zinc Plating Fumes

09/10/2014 10:16 PM

Adapt a Fume Hood Monitor sensitive to Zinc fumes.

http://www.phoenixcontrols.com/en-US/solutions/Documents/FHMX30%20(MKT-0044).pdf

It will take some modifications to do it but isn't that one of the many tasks for engineers.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: