Electrical Switch Gears & Assembly

09/17/2014 8:51 AM

I had a problem in one of our site, the problem is we had loaded the 4000A ACB up to 2200A through sandwith Busduct after 1hour run we had noticed the temp. (90k)at MS supports which is used to support the FRP insators carrying 4000A busbars. Most interesting thing is MS support temp. Is more than the AL Busbar temp.say Busbar temp. Is 55k . Kindly give us the sune tip. If any

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Electrical switch gears & assembly

09/17/2014 8:57 AM

Use a thermal imaging camera.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Electrical Switch Gears & Assembly

09/17/2014 9:36 AM

You need to hire an intelligent engineer to guide you at your sites.

Without one you will continue to fail.

90°K is equal to -185°C or -297°F.

Get a competent electrician to trouble shoot your problems.

Asking an anonymous forum to do your work for you will only end in more failure.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Electrical Switch Gears & Assembly

09/17/2014 10:27 AM

Could it be due to eddy current losses ? Unlikely, but you need to rule out.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Electrical Switch Gears & Assembly

09/17/2014 12:11 PM

How are the conductors of various phases arrayed with respect to the steel supports?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#5

Re: Electrical Switch Gears & Assembly

09/17/2014 1:02 PM

90k? Is this the thermal color temperature?

If so, you are doing some pretty far-out work there!

What equipment did you use to determine the temperature?

Please try to use units which are more readily understood, such as Fahrenheit or Celsius. If you have used infrared camera to determine those temperatures, capture an image and if possible post it here.

Your difference in temperature between your aluminum busbar and the MS (steel?) supports is understandable. The aluminum will dissipate more evenly which should reduce hotspotting.

Do you see any hotspots?

__________________
common knowledge...less common than common sense
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6

Re: Electrical Switch Gears & Assembly

09/17/2014 1:14 PM

For conventional Busduct for any current rating above 2500A it will be advisable to provide non magnetic enclosure to restrict the Eddy Current circulation on the enclosure.Also the magnetic path of the supports fixing brackets to be broken, then only Eddy current circulation can be minimised.Also for heavy duty busducts say 4000 A and above Aluminum Enclosure would be preferable.

I was a Bus duct manufacturer from 1981 to 2006, during my days I used provide Sheet steel enclosure for busduct upto 4000 A ,but break the magnetic path by providing stain less steel strips and using stainless steel hardware.For above 4000 A I used give Aluminum Alloy enclosure.

In your case it is sandwich Busduct, the temperature rise problems are noticed in many sites, these have to be addressed by the sandwich busduct manufacturer.

I had raised these issues in many forums but no convincing replies were given by the manufacturer, but many Projects are being installed with Sandwich Busducts

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Electrical Switch Gears & Assembly

09/17/2014 3:41 PM

I am assuming you mean 90 deg C and 55 deg C temperature rise above ambient.

Is this something a professional switchboard manufacturer has supplied or made for you or something someone has just designed or assembled that (shall we say) is not experienced in electrical bus work design and assembly?

Are the other sites bus work of the same construction but don't have the same problem? If so, what's different?

Can you post a photo of the bus work area in question?

__________________
jack of all trades
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Electrical Switch Gears & Assembly

09/17/2014 7:06 PM

& when pstg ur FU info, pls refrain from using 2LAs and 3LAs that we m/mnot understd, i.e. "MS" etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13
In reply to #8

Re: Electrical Switch Gears & Assembly

09/18/2014 2:54 AM

Like "etc", you mean?

__________________
Good moaning!
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9

Re: Electrical Switch Gears & Assembly

09/17/2014 9:52 PM

In partial defense of the OP.... 0K means Degrees Kelvin which is the correct temperature scale for scientific and engineering fora (as opposed to 'forums' quite often used, but is somewhat wrong) However. it starts from Absolute Zero, which is -273.150C. So technically, he should have mentioned 363.150K if he wanted to say 900C. Fahrenheit is cumbersome for us who use Celsius/Centigrade.

'MS', i thought, is a universal acronym for mild steel, but i see that it is not.

i am all for elimination of acronyms on CR4. Except things like RTFM, ROTFLMAO and so on

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #9

Re: Electrical Switch Gears & Assembly

09/18/2014 12:27 AM

Seriously, what are the chances this is an application using 2200A bus work (and aluminium at that) operating at cryogenic temperature levels?

Negligible I say, surely the op means temperature rise above ambient.

__________________
jack of all trades
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #10

Re: Electrical Switch Gears & Assembly

09/18/2014 1:24 AM

In our engineering courses, we are taught to use the Kelvin scale for showing temperatures, and temperature rise. As you say, the OP should have said 900K over ambient, which would have been correct. Celsius/centigrade scales are used by others, for example the weather bureau. Doctors use Fahrenheit when measuring body temperature. Contrary to western opinion, Indians also have a normal body temperature of 98.60F- neither hotblooded nor cold So, we use all the scales. But we don't mix them up, like say, miles per litre or kG per square inch or something like that.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: Electrical Switch Gears & Assembly

09/18/2014 1:21 AM

Refer www.copper.org or www.copper development association for busbar chamber design/construction

__________________
pnaban
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#14

Re: Electrical Switch Gears & Assembly

09/18/2014 4:44 AM

I am impressed by anyone who can make any sense of this posting and offer a sensible answer. 'Up the garden path' is applicable here. I can possible see an issue at the post insulators with creepage, but to be sure and offer a sensible answer to help. Well, perhaps re-posting the question properly written, is most advantageous to all.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#15

Re: Electrical Switch Gears & Assembly

09/18/2014 5:00 AM

Couple of small points:-

K (Kelvin) does not have degrees. It just is. (Small k = 1000).

K with respect to switchgear is usually referring to temperature rise, above ambient, which makes sense of the original post.

It is very common for busduct (bustrunking) to run at very high temperatures, a fact not always made clear by the manufacturers. The problem then comes when it is connected to a system which cannot necessarily handle such high values of K and a buffer zone is required with oversize conductors, ventilation etc.

In this case there may be another problem altogether e.g. bad design, bad manufacture, bad installation.

__________________
rogerggbr
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#16
In reply to #15

Re: Electrical Switch Gears & Assembly

09/18/2014 11:09 PM

Thank you very much. i did not know that the degree has been dropped ! How stupid in this day and age, with so much on Wiki etc.

Coming to OP's problem, i have only seen eddy currents cause this. There should be no currents at all in the steel enclosure anyway, unless steel happens to be between phases.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#17
In reply to #16

Re: Electrical Switch Gears & Assembly

09/18/2014 11:19 PM

My fault. I knew better, too. Kelvin is an absolute value. No superscript needed.

Register to Reply
Register to Reply 17 comments

"Almost" Good Answers: