Starting a 250KW Y-D motor with 1MW Generator

07/09/2007 9:33 AM

Is it possible to run 2 nos. 250KW LT motor (415V), having star-Delta connection, with 1MW Generator.

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Starting a 250KW Y-D motor with 1MW Generator

07/09/2007 9:44 AM

Can the star-deltas be changed for soft-starts and the motors started in sequence, so that motor 2 is delayed until motor 1 is up-to-speed? This change would improve the chances, as would substituting variable-frequency drives [VFD]. VFDs have rather more configurable parameters than soft-starters.

The mechanical nature of the load is also of interest; if the motors are connected to something having a big flywheel then the starting effect will be more severe than if they were connected to a low-inertia device like a centrifugal pump, for example.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 19
#2

Re: Starting a 250KW Y-D motor with 1MW Generator

07/09/2007 8:02 PM

Is it possible to run 2 nos. 250KW LT motor (415V), having star-Delta connection, with 1MW Generator.

Regards,

What is the LRI for the motors? I assume that you would not attempt to start both motors at the same time. Intuitively I would say you could run the motors, but it is unlikely that you would start them.

You will need to specify the "load " starting torque to determine the minimum starting torque of the motor

Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#3

Re: Starting a 250KW Y-D motor with 1MW Generator

07/10/2007 5:19 PM

They should run ok depending on what other load you have connected to the generator. Starting would be far better if you change the star delta starters for electronic. Especially important if you are starting centrifugal pumps as the changeover timing s-d can be critical if you get it wrong the generator could drop out at this point. More likely when you start the second motor. If you are running Centrifugal pumps or Fans cut the star time down to as short as possible. If you have a high inertia load leave the star time long.

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#4

Re: Starting a 250KW Y-D motor with 1MW Generator

07/10/2007 8:22 PM

One to full load-PAUSE.

Then same way y/ for #2 !

Sure

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#5

Re: Starting a 250KW Y-D motor with 1MW Generator

07/12/2007 6:49 AM

Yes, but both the motors not simultaneously. You should ensure that Generator excitation and governor should be able to provide extra power and have capacity for providing short time duration power more than the motor acceleration time. Better do some ETAP study, giving detail of Generator, motor/load characteristic curve etc.

__________________
BNDas
Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#6

Re: Starting a 250KW Y-D motor with 1MW Generator

07/16/2007 11:22 AM

You should have no problem starting 2 250kw motors at the same time with a 20-25% voltage dip assuming not flywheel loadings.

__________________
A day without a smile is a day lost
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 19
#7

Re: Starting a 250KW Y-D motor with 1MW Generator

07/17/2007 12:17 PM

One 250 kW motor if started DOL would draw approx 2.4 mVA and if started in star then approx 1.3mVA. Some other form of assisted would be required. An auto transformer starter on 50% tap [assuming FLI = 500amps] would draw about 600.0kVA starting and should not represent a problem for the generator. Will this provide sufficient torque to accelerate your load? It will depend on the load torque/speed curve. Other options are VVVF drive as has already been mentioned. A primary reactor starter may also do the job, as the starting current could be limited to the FL amps. Again, will this provide sufficient torque to accelerate your load? It will depend on the load torque/speed curve.

Greg lynch

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#8

Re: Starting a 250KW Y-D motor with 1MW Generator

08/28/2007 3:56 AM

I would suggest using one motor (one which is used first) on star-delta and the second one on softstarter. Another way is to use softstarters ( with bypass contactors to bypass the softstarter) on both motors. 1 MW gennie ( unless it is brand new) will be stretched if use both motors with star-delta starter. Good luck !! Chaterpilar

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire