Sensitivity of ELCB

01/27/2015 1:49 PM

How do we select sensitivity of ELCB? Earth leakage current is the current flowing from the live parts of the installation to earth in the absence of an insulation fault. Now by this definition magnitude of current flowing in this case would be V/Rc here V = LV voltage 230V, Rc = body path resistance in the range of 2000 to 3000Ohm so current is = 230/2500 = 92mAmps .one can consider 100mAmps So it seems 100mAmps is universal requirement but then ELCB is commercially available with various values of sensitivity. Why?

Register to Reply
Pathfinder Tags: earth leakage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Sensitivity of ELCB

01/27/2015 2:09 PM

You don't. It's already done for you in your national electrical standards. All you have to do is hire a Qualified Electrician to follow them.

100mA? What's the point of that? The poor soul would be dead before it trips!

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#2
In reply to #1

Re: Sensitivity of ELCB

01/27/2015 2:15 PM

But on what basis national electrical standards select the sensitivity value?

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Sensitivity of ELCB

01/27/2015 2:16 PM

Avoiding death by electrocution!

Ye gods....

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#4
In reply to #3

Re: Sensitivity of ELCB

01/27/2015 2:20 PM

Electrocution occurs at 30mA then why do we have ELCB of 100mAmp and 300mAmp

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5
In reply to #4

Re: Sensitivity of ELCB

01/27/2015 2:23 PM

Er, could be that your circuits are not compliant?

Could be that these items are not intended for final circuits?

Could be that your national standards are out of date?

I can't see what you're doing. You tell me!

__________________
Good moaning!
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13
In reply to #4

Re: Sensitivity of ELCB

01/27/2015 9:49 PM

30mA was chosen because it is below the threshold of atrial fibrillation, it is below the "can't let go" threshold for muscle spasms, and most healthy individuals can tolerate it for the milliseconds required for the ELCB to respond. Your 92mA calculation ignores the contact resistance of skin and the different pathways through the body. It does however come close to the lower limit where atrial fibrillation has a high probability of starting.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Apr 2013
Posts: 188
Good Answers: 1
#20
In reply to #13

Re: Sensitivity of ELCB

01/28/2015 4:04 AM

Hello RAMconsult. I wonder if you meant Ventricular fibrilation.? The reason I ask is that I have, and have had for several years now, Atrial fibrilation. It is a flaming nuisance, but doesn't seem too deadly.

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#32
In reply to #13

Re: Sensitivity of ELCB

01/28/2015 1:32 PM

Thanks for analysing the 92mA calculation. You are right healthy individual can tolerate 30mA till the time ELCB operates

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#21
In reply to #4

Re: Sensitivity of ELCB

01/28/2015 4:21 AM

One possibility is circuits for which human contact is unlikely, but electromechanical damage must be prevented. (And also minimizing nuisance trips.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Sensitivity of ELCB

01/27/2015 2:38 PM

You've been coming here since 2012 and asking questions that any electrician should already know.

You appear to have "projects" which implies that other people are paying you to know the answers already.

I suggest that you either:

1. Stop taking money to do jobs for which you are not qualified.

2. Hire a qualified electrician, who is qualified.

3. Purchase the applicable code books and LEARN THE CODE REQUIREMENTS yourself.

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#7
In reply to #6

Re: Sensitivity of ELCB

01/27/2015 3:03 PM

Sorry lyn you are grossly mistaken. It is not about following electrician blindly. You may be doing not me. If you are not aware about the exact explanation I will furnish in this forum correct explanation with back up from IEC within next 24 hours.

Thanks & Regards

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8
In reply to #7

Re: Sensitivity of ELCB

01/27/2015 3:18 PM

So, why on earth did you post if you already have the answers?

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#12
In reply to #8

Re: Sensitivity of ELCB

01/27/2015 9:39 PM

Why on earth I have posted it? Because to know the basis behind following electrician blindly or understand reasoning behind codes. Not only me everybody knows what are the standard sensitivity of ELCB used. Not everybody like you knows reason behind them. Some people acknlodge llke me and try to search some people do not like you and give out of context reply.

Thanks

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #12

Re: Sensitivity of ELCB

01/27/2015 10:42 PM

I'm still waiting for you to, "furnish in this forum correct explanation with back up from IEC".

Where is your latest project? I'd like to monitor the progress.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #14

Re: Sensitivity of ELCB

01/28/2015 12:29 AM

24 hours have not elapsed yet.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#23
In reply to #15

Re: Sensitivity of ELCB

01/28/2015 9:08 AM

Who's counting?

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#33
In reply to #14

Re: Sensitivity of ELCB

01/28/2015 1:41 PM

Lyn dont waste time writing crap. You may have plenty of time to waste, unfortunately I do not have. Other sincere people have responsibly given enough answers/inputs and there technical interpretation accompained by hands on experience. You can go through so that from next time onwards there is no dependency on electrician for proper selection of ELCB.

Good luck

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #12

Re: Sensitivity of ELCB

01/28/2015 3:39 AM

Qualified Electricians follow national standards so that the risk of electrocution, injury, property damage, fires, loss of business, insurance claims and prosecution is negligible.

National standards are based upon best practice, predictive calculation, loss prevention and learning from mistakes.

It's all about liability.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#19
In reply to #18

Re: Sensitivity of ELCB

01/28/2015 3:56 AM

Everybody already knows all of that. However, codes seldom if ever tell the specific whys for their provisions, which is what the OP was legitimately asking. Only RAM has offered any actual rationale, rather than snideness.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #7

Re: Sensitivity of ELCB

01/27/2015 3:42 PM

Thanks! That would be great.

It would also be great if you did that every time you come to the forum to ask questions that make it sound like you don't know the answers to those questions you ask.

Regards

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10
In reply to #7

Re: Sensitivity of ELCB

01/27/2015 4:05 PM

What nonsense.

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 18
#11
In reply to #10

Re: Sensitivity of ELCB

01/27/2015 9:34 PM

Your comment is non sense. Before writing something on technical forum think.

Thanks

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#16
In reply to #11

Re: Sensitivity of ELCB

01/28/2015 12:41 AM

30mA for adults,used in final circuits(BS) in CU.. In USA it is 6ma at sockets (receptacles).Infants will be hurt at low levels. There are higher ratings up to 500mA.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#27
In reply to #11

Re: Sensitivity of ELCB

01/28/2015 11:24 AM

Sparky....hmmm

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#17

Re: Sensitivity of ELCB

01/28/2015 12:44 AM

Refer BS 7671. We don't divide 230 by body resistance but by EFLI(earth fault loop impedance) from transformer including resistance of earth electrode,resistance of wires etc

__________________
pnaban
Register to Reply
5
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#22

Re: Sensitivity of ELCB

01/28/2015 8:03 AM

It is to protect people, or assets. TO protect only assets, we will see some mA going up to 1A . To protect people, this is a statistical protection (not all humans are equal facing electricity..) . THe effects on the human body are given in the IEC/TS 60479-1 as per the table attached.The value of the current varies from individual to individual, and is usually taken from the resistance hand to foot . If you lay on your back in water and come with the line direct on your chest at heart level, this may be much worse ...ANd of course the effect is linked to the speed of the breaker.This is why IEC defines 30mA for most places, 10mA for high exposure . NEMA specifies 6mA ... but allows electronic detection which is usually less reliable than pure electromecanic....

Register to Reply Good Answer (Score 5)
Active Contributor

Join Date: Nov 2012
Posts: 18
#31
In reply to #22

Re: Sensitivity of ELCB

01/28/2015 1:30 PM

Thanks Obouill IEC 60479 is informatve

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#24

Re: Sensitivity of ELCB

01/28/2015 10:09 AM

This is my memory, I don't remember the which code has this application guidance -

30mA is best for human protection and is recommended for all sockets where hand tools / appliances can be connected and for those circuits dealing with water such as geyser in bathrooms.

100mA also can offer human protection to some extent and is recommended at a higher level (not at individual circuit / socket level). This is a practical necessity as the 30mA ELCB can maloperate with more extensive wiring (and corresponding leakage current exceeding the 30mA threshold under cetain conditions).

300mA can offer no protection for humans but is good enough as a protection against electrical fires.

Just to share.

__________________
Raghunath
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#25
In reply to #24

Re: Sensitivity of ELCB

01/28/2015 10:21 AM

Alternatively they can be used for effective discrimination-300mA at Main panel, 100mA at sub panel and 30mA at consumer unit or final circuit,6mA in each socket.

__________________
pnaban
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#26
In reply to #24

Re: Sensitivity of ELCB

01/28/2015 10:27 AM

with respect, Raghun, yes 300mA is good enough for protetection against fires when those are due to earthe leakage, yes. But the ultimate protection against fires is AFDD (or CAFI, as named un the NEMA world).

About AFDD : http://www.electrical-installation.org/enwiki/Arc_Fault_Detection_Devices_(AFDD)

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#28

Re: Sensitivity of ELCB

01/28/2015 11:54 AM

WHY? Because 6 millamps of electrical current is lethal for/to human beings.

This value is known from actual medical research testing and is not a disputable variable.

Body path resistance/impedance to current flow varies with ambient conditions, applied voltage level, and individual body characteristics.

This is not something anyone in their right state of mind would even consider altering or not complying with.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#29

Re: Sensitivity of ELCB

01/28/2015 1:06 PM

Back in the old days when the quality of insulation was often poor and suspect, especially heating elements, 100mA or more was required otherwise the ELCB (usually in series with the earth wire) would keep tripping out in normal use - and not helped by doubtful practice of earthing the neutral at point of use.

Modern wiring and equipment (made and tested to modern standards) have nigh on infinite insulation resistance, meaning there is little or no earth leakage to talk of, allowing RCD's with very low leakage protective currents with precise tripping times to be used.

Just as importantly, to be specified in the regulations to prevent people unwittingly inventing their own less safe standards.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2012
Posts: 18
#30

Re: Sensitivity of ELCB

01/28/2015 1:29 PM

Sncere thanks for giving technical inputs. I went through some catalog and IEC. I think:

  1. 30mA for 30msec is deemed as the safe cut-off point to avaoid fatalities. 100mA is used to prevent fires. 300mA with adjustable time delay is used for the upstream device to provide discrimination between devices and to protect plant. 300 mA ELCB is used for apps like Lifts since its extremely isolated.
  2. To be within zone of the IEC curve as shown in attached curve. It is necessary for the ELCB to operate within 50ms at 240 mA and 150ms at 80mA. Both these conditions are satisfied by 30mA ELCB For households, Individual outlets, Wet areas and temporary installations, ELCB with sensitivity not exceeding 30mA is advisable
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#34
In reply to #30

Re: Sensitivity of ELCB

01/28/2015 9:43 PM

When testing rCD in buildings as per BS 7671,at 50% of rated trip current=15mA,it should not trip and at 200% of trip current,it should trip within...mS.

__________________
pnaban
Register to Reply
Register to Reply 34 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (5); eqbal.asif (9); horace40 (1); Jacko the Aus (1); Kulas (1); lyn (4); obouill (2); pnaban (4); PWSlack (1); raghun (1); RAMConsult (1); SHOCKHISCAN (1); Tornado (3)

Previous in Forum: Asynchronous Motor   Next in Forum: Analog Address-able Internet Enabled Fire Alarm Control Panel

Advertisement