Anonymous Poster #1

Electrical

02/11/2015 6:11 AM

Dear Sir,

I am facing the problem in Main DG panel 4000A capacity.

The problem is there is ACB 4000A capacity in DG panel which is feeding the supply to Main LT panel through Busduct.

As we noticed that there is temperature (around 90degrree)on MS angle which is used for Busbar support mounted with FRP.but busbar temp. is around 50degree at the load of 2500A.Kindly help me out why the temperature occured only at MS angle .

Regards

Murali

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Electrical

02/11/2015 6:18 AM

Look for "loops" in the conductors and the supports that might induce currents in the steel, which is magnetic.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: Electrical

02/11/2015 8:04 AM

I would suggest you analyze the bus for a loose connection at the point of high temperature and also check the support insulators for cleanliness and condition.

A high resistance joint can cause heating.

The support insulators may be dirty and/or breaking down allowing current to leak to ground causing heating. A meggar or DC Hypot can be used to determine if the insulator is breaking down.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#3

Re: Electrical

02/11/2015 8:45 AM

Loss connection probably.. if not electrons passing through a curve experience centrifugal acceleration

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Reply Off Topic (Score 4)
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Electrical

02/11/2015 9:05 AM

MS angle is too close and/or at right angles to magnetic field field from bus conductor and has induced/eddy currents flowing in it and heating it up. Situation will be made worse if MS angle has more than one grounding point.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Electrical

02/11/2015 11:32 AM
  1. Certainly it is the case of partial failure of insulator, which allows current to flow through the MS angle. This will continue until the insulator totally fails and draw high current till the breaker trips.

DHAYANANDHAN.S

Reply Score 2 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Electrical

02/11/2015 2:37 PM

You have the equivalent of an induction cooker.

Induction cooking - Wikipedia, the free encyclopedia

In an induction cooker, a coil of copper wire is placed under the cooking pot and an alternating electric current is passed through it. The resulting oscillating magnetic field induces a magnetic flux, producing an eddy current in the ferrous pot, which acts like the secondary winding of a transformer. The eddy current flowing through the resistance of the pot heats it.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7

Re: Electrical

02/12/2015 12:20 AM

This is due to eddy currents in the magnetic path. The brackets which supports the FRP supports acts as magnetic path. You have to break the path by introducing non magnetic material say aluminum strips and also stainless steel hardware for fixing the brackets.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Electrical

02/12/2015 3:37 AM

I agree with the opinion that could be steel losses some where to rise the local temperature.

However, in my opinion if the phase currents are balanced and no neutral -or grounding wire-current will flow through the steel enclosure the steel losses have to be minimal influence.

First of all we don't know what represents 90oC and 50oC.Is it the air temperature or the equipment temperature? Equipment temperature of 90oC could be a normal temperature-mainly the cable connection.

__________________
Julius
Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); dhayanandhan (1); Kulas (1); lyn (1); RAMConsult (1); ramvinod (1); SHOCKHISCAN (1); Tornado (1)