Sizing of Inverter

04/01/2015 10:46 PM

hello everyone.

I have a solar panel work to install. The total load of 3500 watt is drive through solar panel.I want to know the panel size,battery size and inverter size used in this installation. The panel rating is 1ooW panel,voltage-17.4V,current-6amp.

Thank you

__________________
ee.saurav@yahoo.com
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: sizing of inverter

04/01/2015 11:05 PM

Is the load of a critical nature? Is there any backup planned? Like say a generator or grid power available....What is your geographical location? Is your space limited? How much money is your budget?

http://www.wholesalesolar.com/inverter-system/solar-power-center-2135219.html

http://www.solar-electric.com/1waofsoposyw.html

http://www.bluepacificsolar.com/home-solar/solaredge-3500w-solar-kit.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: sizing of inverter

04/01/2015 11:27 PM

Driving a 3500 watt load with a 100 watt panel will be a cute trick, unless the load is active only 1/35 of the time.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
5
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3

Re: sizing of inverter

04/02/2015 12:02 AM

Is this a resistive or reactive load? That answer will impact on inverter sizing.

As for the rest....3500w at 12v is around 290 amps.

Depending on whether your charge controller is PWM or MPPT type, a 100w panel will input anywhere from 6 to 8 amps to your battery during peak sun times.

Dependent on time of year, weather conditions etc, you might get 6 peak sun hours per day plus a little on the peripheries, so that's a maximum of from 40 to 60 amp hours per day from your panel. Convert that to watt hours if you like and you get 480 to 720 watt hours per day, and that's on a good day.

Your 3500w load will draw at least 290 amp hours from the battery in just one hour.

If you installed 300 Ah (3600Wh) of battery capacity - this is the minimum that would even allow you to maintain 12v terminal voltage at start with that load (assuming resistive only) - you would get only about 18 minutes of use before the battery voltage dropped below 12v, and about 40 minutes to flat (10.5v), the inverter would switch off on low voltage at around the 25 minute mark.

Your 100 watt panel will then require around 7 good days to recharge the batteries with no load on them.

You see where this is going??

To allow daily use of this system for just 1 hour per day (@50% DOD) with a 5 day inclement weather allowance, would require 11 x 100 watt solar panels and 3000 Ah of battery capacity. To extend to 2 hours per day you would need 31 panels and 6100 Ah of battery capacity. Reducing the 5 day backup would reduce those amounts.

Register to Reply Good Answer (Score 5)
Anonymous Poster #1
#4

Re: sizing of inverter

04/02/2015 12:38 AM

You already said PV size.

Battery size for 3.5KW depends on ampacity of battery.

Identify the voltage levels and balance the power on both side. Go for more capacity than load.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Sizing of Inverter

04/02/2015 9:12 AM

It responds to a little arithmetic. So the inverter needs to be larger than 3500W. The panel is therefore too small by a factor of 35 to drive it continuously. It can, however, supply this load continuously for somewhat less than 1/35 of the day. Is this satisfactory?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2014
Posts: 113
Good Answers: 4
#6
In reply to #5

Re: Sizing of Inverter

04/02/2015 10:30 PM

The panel is not nearly big enough for a 3,500 watt load.
We also need to know the voltage of the load.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#7
In reply to #6

Re: Sizing of Inverter

04/02/2015 11:09 PM

I got the impression from the OP that he wants to know how many 100 watt panels he needs. This statement -"I want to know the panel size, battery size and inverter size used in this installation" - appears to indicate that, and then he goes on to tell us what sized panels he wants to use - "The panel rating is 100W panel"

The voltage of the load should be immaterial. The power requirements from the panel and batteries will be identical for a 3500w load no matter what the output voltage of the inverter is. He will need to get an inverter with the correct output voltage and frequency to suit the load, but we would hopefully assume he knows that much at least.

That was my take on the questions, but as the OP has not been back, it's probably a moot point anyway.

Register to Reply
Power-User

Join Date: Jul 2014
Posts: 113
Good Answers: 4
#8
In reply to #7

Re: Sizing of Inverter

04/02/2015 11:17 PM

We need to know the kwHr load per day

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#10
In reply to #8

Re: Sizing of Inverter

04/02/2015 11:43 PM

I suspect he meant his total load was 3.5Kw hrs per day.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Member
United States - Member - If it broke, then you didn't weld enough metal on!

Join Date: Mar 2015
Location: The channel scablands of Washington State
Posts: 5
Good Answers: 1
#9

Re: Sizing of Inverter

04/02/2015 11:38 PM

We need more information. You say you want to know panel size then give the panel rating. Question...do you mean to say that 100w panels are available to you? Is your 3500w load continuous or is it the peak power?

Having some experience with solar, and this would be just a suggestion, for a continuous load I would size my array to produce 3 times the load. This would produce the extra power stored in the batteries for at night and also allows for cloudy days and the reduced power generated in the mornings and evenings.

For a continuous load I would also have enough batteries to store about 4700 amps hours, assuming 12v batteries.

Assuming the continuous load is a motor then the inverter should handle the surge probably a 5000w inverter.

If this is for a residence then an array producing 3500 watts may be just big enough but I would likely want about 5000w to be comfortable. You would need to know the watt-hours all of the appliance need in a day to help calculate the size of the battery bank. I would probably stay with the 5000w inverter.

This is just a rough estimate of what I would do, others may have a better idea. Good luck!

__________________
When you feed the bull, remember to watch where you step.
Register to Reply
Power-User

Join Date: Jul 2014
Posts: 113
Good Answers: 4
#11
In reply to #9

Re: Sizing of Inverter

04/02/2015 11:47 PM

Solar electricity (energy) is very expensive.
A 3500 watt load is far too much.
Turn off the 2,400 watt radiator. Get rid of your 2,000 watt kettle and make your cup of coffee on a wood stove.

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Sizing of Inverter

04/03/2015 12:49 AM

Dear Mr. ee.saurav,

You have referred "I want to know the panel size,battery size and inverter size"

For Battery Size, it depends upon the No. of Hours you want to use your electrical load, since if sun shine is not there, the battery has to supply the power through the inverter.

If you assume that you intend to use for 10 Hours 3.5 x 10 = 35 KWHr. For 3.5 KW, if the Batttery is of 24 Volts, the current will be 3500/17.4 = 201.4 Amps say 202 Amps to maintain for 10 Hours., to meet your demands. Hence you need 202 x 10 = 2220 Amp.Hrs rounded to 2500 Amp.Hrs.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#14
In reply to #12

Re: Sizing of Inverter

04/03/2015 2:44 AM

I think you may be a little confused there.

The 17.4v figure that the OP mentions is the knee or maximum power voltage of the solar panel. That voltage will satisfactorily charge a 12v battery via a suitable controller, but it will not service a 24v battery.

Therefore for a 12v system the discharge current will be 3500/12= 291.7 amps.

The panels may be connected in a series parallel array to service 24v batteries, again through a suitable controller. The discharge current would then be 3500/24 = 145.8 amps.

In your scenario, using your figures, drawing 202 amps from a 2500Ah bank for 10 hours would see the battery terminal voltage drop below its rated value (24v, 12v, etc., the battery voltage doesn't matter) in less than 6 hours and the bank would be seriously discharged (1.9v/cell or 10% SOC) at the 10 hour point. The inverter will likely quit on low voltage disconnect before the 10 hours are up.

You can check those figures on any LA battery voltage/time discharge graph, just look for a 0.08C curve or pick a spot midway between the 0.05C and 0.1C curves.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13

Re: Sizing of Inverter

04/03/2015 12:49 AM

Hey Guys, FAR too much truth and accuracy here, the OP is apparently GONE.....!

If we tell him that it will work (with a little bit of adjustment!), maybe he will come back?

Have a great Good Friday everyone.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Nov 2008
Location: Bohol Island, Philippines
Posts: 65
#15

Re: Sizing of Inverter

04/03/2015 4:52 AM

It is also possible that the 3.5kw figure is the amount of electricity consumed in a day. (A figure that would cover many homes in the Philippines, for example).

If that is the case then 10 x 100watt panels, a 2-3kw inverter and 600 AH battery storage should suffice.

__________________
Green to Brown & Blue to Bits
Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#16

Re: Sizing of Inverter

04/03/2015 8:16 AM

15 replies. Not a single answer that indicates any understanding of the structure of the solution.

For once, I agree with Lyn. Call a solar builder (someone who has built many systems) and read some books. The answer is complex and knowable, but not on IHSE.

I'll get you started.

What are your expectations for electricity supply when you are finished. You must answer this question first, which means you must find answers to

1 total load per device

2 peak load per device

3 voltage requirement per device.

You can then identify inverter options. (it is possible that you don't need an inverter)

1 is the system going to be grid tied

2 what kind of quality/longevity are you able to afford

3 what are the location options for equipment

I suspect at this point, you are making assumptions that have multiple choices, and which choice you make will have an enormous impact on the reliability, cost and usefulness of your system. You are about 3% through the design process.

Read, read, read.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jun 2014
Posts: 59
Good Answers: 1
#17

Re: Sizing of Inverter

04/03/2015 7:34 PM

The sun's radiation, at the Equator, is 1KW/square meter. Since you don't indicate where you are located and the received Solar Radiation number is, an accurate calculation cannot be made.

As previously pointed out, unless you have a means of solar tracking, the maximum radiation will only be when the sun is normal to the surface of the panel. The panel will only produce 100w if the temperature of the panel is =< 25* C. The 1704V panel rating is open circuit and the 6A is short circuit. There is no Power Factor.

The output of the panel is probably 9V under resistive load, < 4A at best.

Clouds, haze, dust, etc. will further reduce the efficiency of the panel.

As to the Battery:

It is recommended that the core battery voltage never drop below 80% of full charge.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#18
In reply to #17

Re: Sizing of Inverter

04/03/2015 9:37 PM

That irradiance figure of 1kW/m² is only true for when the sun is perpendicular to the surface, and that can shift from roughly 23° North to 23° South of the equator during the course of the year and is therefore only perpendicular at the equator during the equinoxes. Because equatorial regions are generally hotter and wind speeds generally lower, solar panel efficiency is reduced due to increased panel temperature.

Whilst panel current rises slightly with a hotter panel, open circuit voltage falls considerably, thus reducing overall power output. Typical losses would be 0.5% per °C rise above 25°C so that could reduce panel power by as much as 15% at times.

The 17.4v that you mention is the normal maximum power voltage (Vmp) of a panel used for 12v battery charging. Its open circuit voltage (Voc) will be closer to 22v. The panel will only produce 100w if it is used in conjunction with an MPPT type regulator which will maintain the panel's operating point at its "knee" or maximum power point.

A solar panel produces its maximum power at only one point between open circuit voltage and short circuit current, it produces no power when open circuited and no power when short circuited.

Connecting a 100 watt (17.4v Vmp, 6 amp Isc) panel to a 12v battery that is at 12.1v or 50% depth of discharge (DOD) via an MPPT regulator will produce around 8 amps charge current to the battery. 12.1v x 8 amps = 96.8w

Connecting that same panel to the same battery at the same DOD via a series or PWM type regulator will produce only 6 amps charge current to the battery. 12.1v x 6 amps = 72.6w.

Unless the regulator is faulty (in the case of an MPPT device), or the battery is down to 9v (in the case of a series regulator), or you are erroneously connecting the panel directly to a load, you will never see 9v at the panel during decent insolation.

Whilst I agree that maintaining battery state of charge at never less than 80% is good for battery longevity and works best for standby systems, best economy - ie cost of battery replacement vs Ah till replacement - is achieved by sizing the bank for a 50% DOD. Inclement weather factors have to be considered.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20
In reply to #18

Re: Sizing of Inverter

04/04/2015 5:08 AM

It may interest you to know, that because of the problems you correctly outlined with regard to excessive temperatures of Solar panels reducing efficiency, there are also available in some parts of the world, what are basically "normal everyday" solar panels, but with water cooling added on the back, which keep the cells to a far more reasonable temperature, even in strong midday sun AND furthermore supply warm water for the central heating, baths/showers and the like....it seems that keeping the cells to 85°C or less, promotes/allows higher efficiency.

The warmed water is basically free once the higher cost of the panels has been amortized. Many are installed here now in Germany....

IBM has also made some big strides in further concentrating more Sunlight (using optical methods), onto smaller, therefore cheaper cells, so much sunlight, that in itself would normally cause them to overheat to over 1300°C (which would possibly melt them!), but when force water cooled to around 85°C, produce vastly increased efficiencies.....

The trick is it seems, is to use a very thin quantity of "liquid" metal as the heat transfer "contact" to prevent local excessive heating, as for example the various "pastes" use in PCs do not transfer the heat quickly enough to work properly at the efficiencies required..

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Jun 2014
Posts: 59
Good Answers: 1
#25
In reply to #20

Re: Sizing of Inverter

04/05/2015 1:27 PM

Thank you for the additional information. The installations I had seen utilized heat sinks mounted to the back of the panel. Not very efficient for the face temperature.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#26
In reply to #25

Re: Sizing of Inverter

04/05/2015 2:04 PM

I am only too happy to assist, you appear to know most of the right stuff already, more than the rest of us put together!!

Nice to make your acquaintance.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Jun 2014
Posts: 59
Good Answers: 1
#21
In reply to #18

Re: Sizing of Inverter

04/04/2015 11:25 PM

Normal is perpendicular

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #17

Re: Sizing of Inverter

04/04/2015 3:33 AM

A really good and to my mind totally "real world" post, I thank you (even though I am totally unaffected!) and I give you a GA for it!!

Hopefully a few more here will also reward you for a bit of simple to understand and clear thinking for the OP!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#22
In reply to #19

Re: Sizing of Inverter

04/05/2015 5:32 AM

Interesting, at least someone here did not understand why my post was needed and gave me an OT. Nobody else mentioned it, even though the Poster had earned at least 1 or more GAs for a very accurate and correct assessment...

The OT poster of course knows who he is (I have a very strong suspicion too!!), he is also VERY ignorant in any way shape or form with regard to the technology mentioned and apparently simple good manners.... He also has serious personal problems as we have seen demonstrated rather often here on CR4.....

But having broad shoulders, I can handle it.... One could say, "Water off a duck's back basically."

As J.J. always says, "Sticks and stones.......!"

Do remember though, such a person is only to be pitied by us all...!

And I would guess that most of you here know who it is too!! It is not too difficult to work out!!

Happy Easter to everyone!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#23
In reply to #22

Re: Sizing of Inverter

04/05/2015 9:23 AM

I know the feeling. # 19 was given 6 OT's before it ever hit the board. Never even posted. It is striking that an engineer would not embrace expertise. That is an unusual engineer indeed.

I found your post interesting.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#24
In reply to #23

Re: Sizing of Inverter

04/05/2015 11:44 AM

If I had waited an hour, I wouldn't have bothered to post, but I got the bit between my teeth.......

I have to admit that I have "shot him down" on SO many occasions because of his stupid an inaccurate comments, its just about the only way he can hit back....its actually quite sad....

Its like him going to a gunfight armed only with a knife!!! Each and every time!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Register to Reply 26 comments