Anonymous Poster #1

Resistive Load Connected Between Two Phases

05/13/2015 11:02 AM

The resistive load is connected between R and S phases (see Fig.).

We see that the resistive load absorb the reactive power on the phase S but returning it to the source on the R phase without modifying the reactive power flow on all three phases.

the power factor per phase is Cosphi = 0.86

is there, realy, a reactive power flow on RS phases?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Resistive load connected between two phases

05/13/2015 11:51 AM

Part of the problem with blogs (this image was copied from an INTECH article) is that they are not checked for content and/or accuracy. You are right to question this, but rather than answer directly, I'm going to ask a few questions.

Shown is a single phase resistive load:

1. yet the power factor is stated as 0.86?

2. how does a resistor draw reactive current?

3. the load is unbalanced while the phasor diagram is shown as balanced?

4. without knowing anything about the source and the relative size of the load, how can you determine the power factor, power flows, degree of imbalance?

Go into a real textbook, not a blog, for the answers.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Resistive Load Connected Between Two Phases

05/13/2015 12:03 PM

Dear Friend,

You have stated that a resistive load is connected between two phases. Since it is pure resistive load, the current drawn will be in phase with the voltage, developing pure heat and hence no reactive power.

The unbalanced current will flow through the neutral. Magnitude of the current will be 1.732 x V where V is the voltage of single phase.

DHAYANANDHAN.S

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Resistive Load Connected Between Two Phases

05/13/2015 1:55 PM

If a resistive load is connected across two phases, and the original poster has given nothing about the other connections, please explain how a current of any sort other than that induced by electromagnetism from the connected phases, flows in the neutral at all?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Resistive Load Connected Between Two Phases

05/13/2015 1:36 PM

The current through a resistor is in phase with the voltage across the resistor. How does the phase of the voltage across the resistor compare with the R phase voltage and S phase voltage?

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #3

Re: Resistive Load Connected Between Two Phases

05/13/2015 8:41 PM

The voltage across the resistor doesn't "compare" with anything, it is simply the vector difference between the voltages applied at each end. If the circuit element is purely resistive then the voltage across it and the current through it are in phase.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #5

Re: Resistive Load Connected Between Two Phases

05/14/2015 7:34 AM

You are in my estimation fully correct in what you say.

Some people make the error (I believe) in seeing this as a "single phase" question, when in fact it is (as you said) the vector sum of two phases at 120° to each other......

In training many years ago now, we would actually plot the voltage (and the polarity of course) for a whole 360° revolution of both of the two phases, a total of 480° in this case.

The voltage across the resistor at any point being easily read off by using a ruler (inches in my day) to see the value. The current being in phase of course with the voltage....

I personally found it far easier to understand, as a visualization is important I feel for many people. I am one of those who sincerely believe in a picture being worth a 1000 words.....

But I also had a few colleagues who could visualize such things in their heads perfectly, without any help!! (Always finishing first, time wise, in exams! But making the same errors as some others too!!)

I would not be surprised to learn that you are one of those people too who can instantly visualize such questions..... Its very useful if you can do it!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7
In reply to #5

Re: Resistive Load Connected Between Two Phases

05/14/2015 10:07 AM

I was trying to lead the OP to figure out the answer without spelling it out, hoping he would understand about phasors.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Resistive Load Connected Between Two Phases

05/14/2015 4:46 PM

Since G voltage it is VRS no current will flow through neutral. That means the single-phase projection it is a virtual one only. You could project on RT or TS also in the same time, but this it is a geometrical exercise only.

Let's say Zload=Rload+jXload and Xload/Rload=tan(fi).

fi=30 degrees cos(30)=sqrt(3)/2 sin(30)=0.5 tan(30)=1/sqrt(3).

Zload=Rload*(1+tan(30).j); IR=IRS=-IS.

IRS=VRS/Zload=VRS/Rload/(1+1/sqrt(3)j)=VRS/Rload*(1-1/sqrt(3)j)/[1^2+1/sqrt(3)^2].

S=VRS*VRS*(1-1/sqrt(3)j)/(1+1/3)=VRS^2/Rload*(1/4*3-3/4/sqrt(3)j)

P=VRS^2/Rload*3/4 ; Q=VRS^2/Rload*sqrt(3)/4

If Rload=1/G than SRS=3/4*VRS^2*G-sqrt(3)/4*VRS^2*G.

No meaning for SR or SS only for SRS.

__________________
Julius
Reply Score 1 for Good Answer
Anonymous Poster #1
#9

Re: Resistive Load Connected Between Two Phases

05/15/2015 4:29 AM

Hi

When we have two load like in fig below

We took the reference, the simple voltage system (VRN, VSN, VTN)

Then

For R1

Ib1 = Ib1 Ð(phi + 0°)

For R2

Ib1 = Ib1 Ð(phi + ∏/6)

Ib2 = Ib2 Ð(phi + 7∏/6)

this is general treatment to calculate the total power consumption and the power factor.

But we can't obtain the correct power flow per phase. (No meaning for SR or SS only for SRS.)

thanks to everyone.

Reply Score 1 for Off Topic
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10
In reply to #9

Re: Resistive Load Connected Between Two Phases

05/15/2015 6:10 AM

OK. In this case indeed Itot=VRN/R1+VRS/R2*[cos(30)+sin(30)j]

ItotRe=VRN/R1+VRS/R2*sqrt(3)/2

ItotIm=VRS/R2/2

However you have not a common voltage and then S=VRN^2/R1+VRS^2/R2 [only active power, reactive power it is still 0].

__________________
Julius
Reply
Member

Join Date: Apr 2015
Posts: 5
#11

Re: Resistive Load Connected Between Two Phases

05/15/2015 9:36 AM

Me again, :)

Using the symmetrical components i have calculated the primary side current of Dyn11 Transformer supplying unbalanced resistive (100 A) load connected between R and S phases. (see the figure below)

the generator gives a balanced voltage system.

how obtain the power factor in each phase of primary side, using the phasor diagram?

we took simple voltage system us reference.

Thank you.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #11

Re: Resistive Load Connected Between Two Phases

05/26/2015 1:18 PM

Sorry for the delay. Very busy days!

Let's take from the beginning.

In every transformer Np*Ip+Ns*Is=Np*Io

where Np=number of turns on primary winding; Ns=no.of turns in secondary and Io=no load current. Since Io is very small we may neglect it and Ip/Is=Ns/Np .

Let's label the primary terminals as R,S,T [upper case] and secondary terminals as r, s, t[lower case].

If we stated VR/Vr=1 then VRS/Vr=sqrt(3) and then Np/Ns=sqrt(3)

Then [in your case DYn11] IRS=-Ir/sqrt(3) , IST=-Is=Ir/sqrt(3) and ITR=0.[As stated by you Ir=-Is =projected on Vrn].

From the attached phasor diagram :

absolute value Ir=Irs=Is=sqrt(86.6^2+50^2)=100 [approx].

Then Ir=100*[cos(30o)+jsin(30o)=86.6+50j

Is=-Ir=-86.6-50j

On the primary side at point R,S,T -according to Kirchhoff law-sum of all currents entering the point=0.

ITR-IRS-IR=0 in point R ; ITR=0; IR=-IRS=Ir/sqrt(3)

IRS-IST-IS=0 in point S; IS=IRS-IST; IST=-Is/sqrt(3)=Ir/sqrt(3); IS=-Ir/sqrt(3)-Ir/sqrt(3)=-2.Ir/sqrt(3)

-ITR+IST-IT=0 in point T; IT=IST=Ir/sqrt(3)

If IR it will be projected on VRN [instead of Vrn]-from the attached sketch:

Absolute value IR=100/SQRT(3)=57.735

IR=57.735*COS(60)+57.735*SIN(60)i=28.868+50i

IT=IR=28.868+50i

IS=-2x[28.868+50iI]=-57.735-100i

__________________
Julius
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: Resistive Load Connected Between Two Phases

05/26/2015 1:30 PM

I'll try to attach the sketch once again :

__________________
Julius
Reply
Member

Join Date: Apr 2015
Posts: 5
#14
In reply to #13

Re: Resistive Load Connected Between Two Phases

05/27/2015 3:15 AM

Thank you.

What about the power factor per phase?

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15
In reply to #14

Re: Resistive Load Connected Between Two Phases

05/28/2015 9:15 AM

If you will represent the voltage VRN,VSN,VTN and the currents IR,IS and IT on a phasor diagram you will get the following:

IR=28.86751+50i cos(fi) with respect to VRN cos(fi)=28.87/sqrt(28.87^2+50^2)=0.5 fi=acos(0.5)= 60o ;

In the same way IS fi=120o ; IT fi=60o.

So per phase you have IR-VRN 0.5 IS-VSN 1 IT-VTN 0.5

__________________
Julius
Reply
Member

Join Date: Apr 2015
Posts: 5
#16
In reply to #15

Re: Resistive Load Connected Between Two Phases

05/28/2015 10:48 AM

a power factor for resistance load.
there is a theoric transit of reactive power for unbalanced resistive load

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17
In reply to #16

Re: Resistive Load Connected Between Two Phases

05/28/2015 12:03 PM

No[total] reactive power is involved. Reactive power from phase R is positive , reactive power from phase T is the same but negative[capacitive] and reactive power in phase S is zero. Total reactive power is zero. Total active power at primary side[173.2*Voltage] it is equal with the active power in the secondary side.

__________________
Julius
Reply
Reply to Forum Thread 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (6); Andy Germany (1); Anonymous Poster (1); dhayanandhan (1); FALI (3); PWSlack (1); RAMConsult (2); Rixter (2)

Previous in Forum: 10" Display Screens + Sensors   Next in Forum: NAT FW with Cisco Router 2911

Advertisement