Why 4- 20 mA?

09/11/2015 12:33 AM

im a new student and new in this instrument n electrical field . i have a question why transmitter using 4- 20 mA ., isn't related with v=ir ? or else can anyone help give an explaination. thnx u

Register to Reply
Pathfinder Tags: instruments 4-20 mA signal
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: why 4- 20 mA

09/11/2015 3:45 AM

I would not generalise the use of 4-20 mA because there might be transmitters out there that use more and some less.

Also if you quote Ohms Law you might want to think about the resistance and Voltage.

What do you make out of it?

I'd also look the what a transmitter actually does. It basically an information gathering system.

So if you think about it in terms of how much you .... need to gather that information and if you want to spend that much.... Then you have the answer.

Fill in the blank and have fun!

__________________
Common Sense Dictates
Register to Reply
Participant

Join Date: Apr 2015
Posts: 4
#2
In reply to #1

Re: why 4- 20 mA

09/11/2015 4:02 AM

oh ! so its depends on how much information need to be gether and how much mA need to be used .. isn't rite ?

Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#4
In reply to #2

Re: why 4- 20 mA

09/11/2015 4:12 AM

Nope!

__________________
Common Sense Dictates
Register to Reply
Participant

Join Date: Apr 2015
Posts: 4
#5
In reply to #4

Re: why 4- 20 mA

09/11/2015 5:08 AM

still can't figure it out ��

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: why 4- 20 mA

09/11/2015 5:44 AM

That's like asking why traffic lights are green for go, amber for caution, and red for stop. There is no particular reason for those choices other than historically someone used them and they caught on. There is a bit more reason for 4-20mA, because it is a decent compromise among voltage and power needed to operate the system, wire size necessary to accommodate current flow, and achievable precision. From there, it caught on and became a common standard. Those numbers are fairly convenient for arithmetic, but there is no absolute reason why they couldn't be 3-30mA.

Not all "why" questions are meaningful.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2015
Posts: 4
#7
In reply to #6

Re: why 4- 20 mA

09/11/2015 5:53 AM

ok. so no such things as "MUST " it can be variable. just follow the range tht must be used in certain instruments.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: why 4- 20 mA

09/11/2015 6:12 AM

Maybe something like that, but your language is not expressing it well.

A uniform system such as 4-20mA can accommodate many ranges of input. For instance, a typical 0-100 psig pressure transducer might give an output of 4 mA for 0 psig, and 20 mA for 100 psig. Or a 0-1000 psig transducer might give 4 mA for 0 psig and 20 mA for 1000 psig. The inputs are different, but the signals transmitted are the same (and thus can use similar circuitry, wire sizes, PLC input modules, etc.) On the other end, instruments/software can restore the original psig value--but in between the protocol stays the same. On the instrument end, you need to do some calibration, but it's just y = mx+b simple algebra.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #8

Re: why 4- 20 mA

09/11/2015 10:53 PM

if full range is set at 20mA,what will be the current when over voltage occurs,current will exceed 20mA and will transducer get damaged.

__________________
pnaban
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#19
In reply to #6

Re: why 4- 20 mA

09/14/2015 8:45 AM

Those numbers are fairly convenient for arithmetic, but there is no absolute reason why they couldn't be 3-30mA.

Really? A 16ma range is convenient? Have you ever tried to set up a PLC using that range of numbers? I've had experienced programmers bog down trying to get the correct engineering units entered to cover that weird range. In RS5000, dividing 32767 by 16 does not work out very nicely. Then you have a pressure instrument with a 100psi range to also divide by 16 and things start to get nasty.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: why 4- 20 mA

09/11/2015 4:10 AM

One reason for the offset from zero is that low signals (e.g., <2mA) can then be flagged as out of range, as can high signals (such as >22mA).

There are other ranges that can be used, such as 1-5 VDC, 1-10 VDC, etc. Some interconversion is possible by having a resistor in the network. (For instance, 5V/20mA = 250 ohms (which is where the V=IR comes in).

Current-loop signaling (you can Google that) is relatively insensitive to electrical noise and interference, which is another reason for its use.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2015
Posts: 482
#9

Re: Why 4- 20 mA?

09/11/2015 1:28 PM

You may either use 4-20mA or 1~5V (its reversible) analog signal for industrial instrumentation. Analog is the simpliest way to go for a switching(on or off) and proportional communication only(0~100%).

Least complicated, robust and can not be easily affected by RFI (at minute level), but it's only limit is distance of transmission.

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#10

Re: Why 4- 20 mA?

09/11/2015 6:01 PM

1) The most important reason for 4-20mA is that 2 wire loop-powered transmitters operate on ~3.6mA of current, so that separate electrical wiring is not needed.

The 2 wires running out to the transmitter carry both the power needed to operate the transmitter (3.6mA), the signal (4-20mA) and the capability of fail-safe fault signaling (3.8mA Low or 21.5mA high)

The 2 wire factor is a huge factor in process plants using hundreds (electrical power generation) or thousands (steel mills, paper mills, refineries) of field transmitters. This is what put 4-20mA on the map.

Officially, 4-20mA is a standard, ANSI/ISA SP50, (revised as ANSI/ISA-50.00.01-1975 [R2002]), but the adoption of thstandard just recognized what had become the defacto commercial standard.

2) The 4:1 ratio of signal span or signal range to the live zero range just seems to work for both pneumatics and electronics.

3-15psi signal = signal:live zero = 12psi:3psi = 4:1
5-25psi signal = 20psi:5psi = 4:1
6-30psi signal = 24psi:6psi = 4:1
10-50mA signal = 40mA:10mA = 4:1

3) As others mentioned, current is far more noise resistant than a voltage signal, and a live zero is has its uses.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#11

Re: Why 4- 20 mA?

09/11/2015 8:00 PM

A general answer is that a current loop has good noise immunity, especially if a twisted shielded cable is used. The lower limit is not zero to allow for detection of an open circuit. Using current to indicate measurements means that the resistance of the wire loop has no effect on accuracy.

https://en.wikipedia.org/wiki/Current_loop

Register to Reply Score 1 for Good Answer
2
Guru
Popular Science - Weaponology - New Member Engineering Fields - Engineering Physics - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Dec 2007
Location: No. VA, USA (No, it does NOTu mean "won't go"!)
Posts: 1796
Good Answers: 75
#13

Re: Why 4- 20 mA?

09/11/2015 11:20 PM

To all the other reasons given, and they are good reasons, add this (I've read up through 12. If others come along, well, read accordingly).

When that signalling current was first selected, solid-state switches did not exist. Relays were in use extensively. This was at least as early as 1890, since one X-Y stepper plate on which I worked had that manufacturer's date stamped into it's body.

One problem with relays is that switching LARGE signals causes arcing, which hastens the death of the relay. And signalling relays, most commonly used back then (we're talking about the relays used in Teletype equipment (TTY) and Telephone switchgear (X-Y steppers were the first to use it extensively)) were small, lightwieght, and needed to have fairly delicate contacts which could sit idle for hours, days, sometimes weeks, and then move very rapidly in and out of contact for extened periods, and do so reliably. All of that mitigated against large current signals. 20ma was found to be a reliable upper value, which would not cause undue arcing, but could be reliably read as a digital high/one value.

But arcing causes relays to stick, and even 20ma would cause arcing over time, hence the 4ma minimum, in order to control the "stickiness" which results from light arcing. This small constant current, soon called a "sealing" current, was useful, in that it served the purpose of allowing for a "floating" out of band signal below the threshold (how can a system know the difference between and intentional zero value, and an open circuit zero value?), AND it delivers a sealing current.

As you will no doubt note, it is also wasteful of power, since even in prolonged periods of inactivity, the circuit still consumes power. And the comm centers in which I worked, on TTY gear in some, and on X-Y steppers in others, all had literally 3,000-5,000 circuits powered up at all times. Calculate the power losses there, even if all the circuits are idle 90% of the time.

__________________
Been away a while. Miss all my old friends. Some of you I KNOW are still around. Where are the rest?
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14

Re: Why 4- 20 mA?

09/12/2015 3:37 AM

I think that you should easily be able to answer your own questions, simply by using Google for example. Never heard of it???

I got 66,000,000 hits just by posting "current loop". I would guess that one or even two can answer all your questions.....

One of the main reasons for using current in a loop is very simple, at all points of the loop, the current is still the same, for quite long distances. Generally twin telephone cable is usually enough...

Whereas a voltage signal will generally be affected by distance and extra calibration will be needed.....and to reduce those effects over long distances, would need far thicker cables.

I quite liked this link myself:-

Current_loop

The second paragraph gives some really simple insight!:-

Given its analog nature, current loops are easier to understand and debug than more complicated digital field buses, requiring only a hand held digital multimeter in most situations. Using field buses and solving related problems usually requires much more education and understanding than required by simple current loop systems.

Is this a "Homework" question for school?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Engineering Fields - Engineering Physics - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Dec 2007
Location: No. VA, USA (No, it does NOTu mean "won't go"!)
Posts: 1796
Good Answers: 75
#15
In reply to #14

Re: Why 4- 20 mA?

09/12/2015 7:49 AM

Hmm. I missed that. I thought the OP was only asking why the 4-20ma limit? NOT why a loop, or why current controlled vs voltage controlled.

Subtle, Andy. Good catch.

__________________
Been away a while. Miss all my old friends. Some of you I KNOW are still around. Where are the rest?
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#16

Re: Why 4- 20 mA?

09/12/2015 11:54 PM

Just a comment on a defective current loop.

If the loop is open (like a broken wire) the current in the loop goes to zero which is an invalid state.

If the loop is shorted, the current will go to a very high value, which is another invalid state.

If the loop current is 4 - 20 ma. then the loop is good.

Bill

Register to Reply
Participant

Join Date: Sep 2015
Posts: 1
#17

Re: Why 4- 20 mA?

09/13/2015 10:20 PM

Two reasons. But first ... net signal = measured/generated signal + noise. 1. To make negligible the noise's contribution to net signal, minimum m/g signal value should not be zero. 2. Instruments measure variables that have square-root relationships with other variables. For example, fluid flow is very often proportional to the square root of pressure drop across an obstruction in a pipe. (For example, doubling the flow across the obstruction multiplies pressure drop by four). Useful pairs of numbers for reason 2 are: 2-4; 3-9; 4-16; and so on. After that, it becomes a case of choosing which non-zero minimum signal value to use and which pair of numbers to use for reason. "Elegant" possibilities include 1-5 (1 + (2x2)); 1-10 (1 + 3x3); 4-20; 5-30. A minimum value of 1 was deemed too low, so the people who set the standard decided on 4-20 mA. Voila! And good thing they didn't choose 4-13 mA!

Register to Reply
3
Participant

Join Date: Sep 2015
Posts: 3
Good Answers: 1
#18

Re: Why 4- 20 mA?

09/14/2015 4:51 AM

You may easily to get the answer from google.

The 4-20 ma range is a "standard" adopted by tradition and also ANSI 50.1, and most process instruments and controllers use it. It was developed during a time when teletypewriters used a 20 ma current loop for communications, so parts for that type of circuit were readily available.
It does have several advantages:

  • The 4 ma "bottom of span" signal allows the receiver to detect a broken wire or failed instrument.
  • Since the loop current never falls to zero, the instrument can be loop powered, allowing for two-wire devices.
  • 20 ma is low enough to be made intrinsically safe, making it easier to apply in hazardous locations.
  • The constant-current feature of a current loop cancels out voltage drop errors due to long wiring runs (of course this would also be true if you selected different current values for zero and span).
  • The 4-20 ma signal dropped across a 250 or 500 ohm resistor creates very convenient 1-5V and 2-10V voltage ranges, respectively, also fairly standard in the industry.
Register to Reply Good Answer (Score 3)
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#20

Re: Why 4- 20 mA?

09/18/2015 5:04 PM

why transmitter using 4- 20 mA ., isn't related with v=ir ?

What these guys are trying to say is the resistance really does not come into play with milliamperes. We are talking 4 thousandths of an amp to 20 thousandths of an amp. If you do add resistance, then it will change to volts instead of amps. Hence the IxR, so, it's not applicable.

Register to Reply Score 1 for Good Answer
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#21

Re: Why 4- 20 mA?

09/18/2015 5:37 PM
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#22
In reply to #21

Re: Why 4- 20 mA?

09/22/2015 9:19 AM

Excellent, hit the nail squarely on the head. If fact that was more like the Karate kid scene about driving a nail completely with one blow.

(No offense to Jackie Chan, but pat Morita will always be my 'Mr. Myagi.' besides, that remake was just Will Smith buying a 'staring role' for his kid.)

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#23
In reply to #22

Re: Why 4- 20 mA?

09/22/2015 9:24 AM

Thank you, sometimes these guys really over analyze simple questions.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#24
In reply to #23

Re: Why 4- 20 mA?

09/22/2015 9:40 AM

I remembered that 4-20mA was a current loop system, but it's been so long since I've actually worked with one, I couldn't remember the details.

All the stuff with PLCs tend to run on 24vDC, with 0v or Open Circuit being 'logic zero' and +24v or Closed Circuit being 'logic one.'

Current loops are great for long distance reporting, since they'll maintain the current, and therefore the signal integrity, regardless of the added resistance of long wire runs. Up to the maximum voltage the current source can run at, of course.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Participant

Join Date: Nov 2015
Posts: 1
#25

Re: Why 4- 20 mA?

11/26/2015 10:39 PM

It doesn't start from 0 bc when value what is measured 0 the current is 4 amp .that is for safety to sense disconnection if there is some issue like disconnected wire current goes to 0 it means there is issue.

Register to Reply Off Topic (Score 5)
Member

Join Date: Oct 2014
Posts: 7
#26

Re: Why 4- 20 mA?

02/23/2016 2:32 AM

it has two reasons,

1. If you increase the cable length then there will be more voltage drop so voltage signal strength will decrease but it's current value will be almost unchanged. So 4-20mA is independent of cable length and its resistance.

2. its easy to troubleshoot the signal error with this. At zero signal value you will get minimum 4mA but if your signal cable has broken from anywhere in field then you will get 0mA so you can distinguish that either your signal value is zero or signal wire is broken from somewhere.

Register to Reply
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: