Convert 600 Volt Stamford Alternator Output to 400 Volt

06/20/2016 3:59 PM

hi

Can we change the output of a HC.I634H2 , 963KVA ,60 hz,6 winding leads, star connected STAMFORD alternator from 600 volt to 380-400 volt output.

What if we change it from star to delta can we get this output ? if we can ,what are the drawbacks?

Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: How do i covert 600 volt Stamford alternator output to 400volt

06/20/2016 4:09 PM

You won't have a neutral any more, but I think a relatively small zig-zag transformer can provide that. [??]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#2

Re: How do i covert 600 volt Stamford alternator output to 400volt

06/20/2016 4:10 PM

If you want to be covert, don't tell anybody.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: How do i covert 600 volt Stamford alternator output to 400volt

06/20/2016 4:39 PM

This is probably doable with changing some things around but the exact configuration and other recommendations I would contact the manufacturer for...

http://stamford-avk.com/products/hc6-4-pole

http://stamford-avk.com/sites/default/files/literature/manuals/A040J849_HC_EN.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#4

Re: How do i covert 600 volt Stamford alternator output to 400volt

06/20/2016 5:01 PM

The manufacturer will be the best authority to answer this question. I have no idea how their voltage regulation circuitry is configured. I doubt a simple switching between star and delta wiring will work. This is because 600V/√3≅346V This is less than your lowest desired voltage by nearly 9%.

I recommend you get the correct 3 phase step down transformer.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: How do i covert 600 volt Stamford alternator output to 400volt

06/20/2016 6:44 PM

You probably can get this output. But to get 380V rather than the 600/√3 = 346 V you get by changing to delta connection is only possible by increasing the excitation current above the normal value. This causes an increase of rotor temperature rise and rotor operating temperature.

This could easily reduce the rotor life to a fraction of normal, that is 25%, being optimistic. If the generator is well used, that could be a short time.

It depends on the real rating of the generator relative to the engine kW. The standard engine rating was at 15 Celsius continuous, sea level to 150m, while generator rating is continuous at 40 celsius to IEC or British standards.

Many makers gave ratings which were the maximum engine rating for 1 hour in every 12 hours to give a more impressive rating (about 10% higher). Of course, they did not point out the considerable effect on life of pushing the engine to maximum, think 10% normal life. The generator might have been down-sized for 1 hour at the rating at 15 celsius too.

It also matters whether you really need that 963 kVA (which would be 770 kW at 0.8 power factor) or whether your load is 770 kW resistive (1.0 power factor) or less. Such a change may bring the generator back to normal rotor limits.

You need to look carefully at the engine and generator rating plates and the maker's rating curves. You have said nothing about your site temperature or altitude above sea level.

As has been commented, going to the manufacturer with your proposed winding connection change, load requirements, site environment and serial numbers of engine and generator is the sensible course.

Taking a used set, which has not been overhauled, and making changes equivalent to an overload is likely to result in a short, unpredictable, life before expensive damage.

Optimism and "It'll be alright on the day, Bluey!" have no effect on hardware.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#6

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/20/2016 9:23 PM

Hopefully your instructor is supervising you while your your playing with expensive equipment! Have you even checked Stamford's web site? What happened to the old Volvo? Did it get smoked? It seems that you know just enough to be a danger to yourself ! and the innocent equipment.

The internet can be your friend and you should learn how to use it. If still in doubt then call the equipment manufacture

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Member

Join Date: Oct 2014
Posts: 6
#9
In reply to #6

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 7:32 AM

I have emailed the manufacturer before i posted it(waiting for the reply) but i thought it is a good thing to learn from someone who knows about it or even practical experience about it. even if it is not possible you may learn a good alternative solution.Most importantly I BELIEVE BY ASKING THIS I MAY LEARN ABOUT A LOT OF RELATED IDEAS IT SHOULDN'T NECESSARILY BE ABOUT WHETHER ABOUT THESE ONE IS POSSIBLE OR NOT.

about the Volvo generator it has been working for more than one year and as i posted i use a resistor between the synchronization module out put and the governor input and it gave it stability.If you are familiar with these you would understand what i mean.Sorry my friend your comment is a judgmental,harsh comment , and no need to write for every question but thanks for your comments .i think it is better to keep all answers or suggestions technical and related.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #9

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 7:42 AM

Still frightened to use the telephone, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #2
#16
In reply to #9

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 3:41 PM

Why?

Register to Reply
Member

Join Date: Oct 2014
Posts: 6
#10
In reply to #6

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 7:36 AM

I have emailed the manufacturer before i posted it(waiting for the reply) but i thought it is a good thing to learn from someone who knows about it or even practical experience about it. even if it is not possible one may learn a good alternative solution.Most importantly I BELIEVE BY ASKING THIS I MAY LEARN ABOUT A LOT OF RELATED IDEAS IT SHOULDN'T NECESSARILY BE ABOUT WHETHER ABOUT THESE ONE IS POSSIBLE OR NOT.

about the Volvo generator it has been working for more than one year and as i posted i use a resistor between the synchronization module out put and the governor input and it gave it stability.If you are familiar with these you would understand what i mean.Sorry my friend your comment is a judgmental,harsh comment and no need to write for every question but thanks for your comments .i think it is better to keep all answers or suggestions technical and related.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 2:45 AM

Undefined: <...we...>. Logically, if <...we...> need to ask, then the knowledge lies outside <...we...>, therefore the answer is no.

Is the equipment manufacturer embraced within <...we...>? Do <...we...> have a telephone at hand and the skills with which to use it? CR4 does not offer training in the use of the telephone, despite overwhelming evidence of need for it from a fair percentage of CR4 postings; is this an opportunity for LynDoor Industries or the KrisDel Corporation (rhetorical question - NNTR)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 6:47 AM

If you convert it to delta you will get 346V 91% of what you’re wanting, is that close enough?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Oct 2014
Posts: 6
#11
In reply to #8

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 7:39 AM

cant it be increased using the AVR

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 7:46 AM

A simple

telephone call to the equipment manufacturer can answer that one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14
In reply to #11

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 9:57 AM

Maybe. First it assumes that the range of the AVR will allow for operation/control outside of its nominal range, not all do. Second, because of the change in the winding configuration and your desire to raise the voltage, the field current required may exceed the long term ratings of the excitation system, thirdly, which causes operation into deeper saturation of the iron. And don't forget to derate the machine to 67% of its original ratings.

Call the manufacturer for exact details of how this will affect the stability and life of the machine as well as violate any warranty that's left.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#15

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 12:46 PM

In my opinion, I would say yes you can set it up to get the lower voltage out of it without any real problems.

Going by the spec sheet for the HCI634G units Stamford HCI634G.pdf Switching the 600 VAC Wye connection over to a 340 VAC Delta and then adjusting the AVR up to compensate for the voltage loss should still be well within its designed operation limits assuming that the unit you have now is not simply a standard unit set for 480 VAC output with the AVR turned up to produce 600 VAC output.

As for rotor overheat concerns, I would not worry about it to any degree unless the unit is being ran at maximum output for hours at a time and even then as the data sheet shows the AVR units they use have built in overexcitation protection as a standard feature.

Now as for setup if it was me and the AVR did not have a setting for making the delta connection work at 400 VAC, Manual here suggests it should Stamford generators with MX321 AVR setup. the simple cheat for that would be to put a small transformer or resistive voltage divider on the sensing lines to cheat the AVR into thinking that it's seeing the correct voltage it wants when you have the actual generator output where you want.

That's my thoughts.

Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#17

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 4:59 PM

They have these things called transformers. You might want to invest in one.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#18
In reply to #17

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/21/2016 5:40 PM

Okay?

You got any spare 1 MVA capacity three phase step down or buck/boost units laying around?

Odds are the OP doesn't either and probably doesn't want to spend the money to buy one if the generator unit can be reconfigured and adjusted to do what he needs.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19
In reply to #18

Re: Convert 600 volt Stamford Alternator Output to 400 volt

06/22/2016 12:14 PM

my guess: hard to turn that generator down.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: