Did I Screw Up?

11/12/2016 5:54 AM

Okay, the answer is almost definitely "yes", but I'm wondering if there's a lazy way out..

Here's what I did:

Mom buys a new house, decides she wants a "switchable" light for the back yard.

Access is very poor, so last week I end up buying one of those wireless remotely switched outlets from Lowe's, placing the little circuit board inside a gray PVC conduit box, and mounting the light (with 2 standard bulb receptacles) to the box. That way, all I need to do is get "full time" power to the box so the wireless switch can turn the light on. I'm actually quite sure this part of setup is fine, I'm just describing it for context.

Here's where I think I may have screwed up... To power the "box" described, I tapped into an "end of the line" outdoor outlet box on the outside of the house (everything is in conduit, even the new stuff) using 14/2, but the circuit is 20 amp. Yes, yes, I know it's wrong, but my reasoning was, with a couple of 13 watt (actual) LED lights plugged into the "box", the max draw is far less than 15 amps (less than 1, in fact), and therefore safe. There are no outlets or any other load on that final 10 foot run.

In the current configuration, I have zero concern about the safety.

However, I was thinking about it tonight and it occurred to me that conceivably, 10 years from now after everyone's forgotten, someone could screw in one of those "light socket to outlet" converters, plug in a million Christmas lights, and over current that last 10 feet of 14 gauge wire.

So, here's my question: Is it sufficient to "placard" the box (something like "2 lightbulbs ONLY" or "15A max")? Or do I really need to make a change to the circuit? I could upgrade the added wire to 12/2, but even that won't completely solve the problem, since the little remote-controlled unit inside the box is only good for 15A.

The other option of course is to change the circuit breaker to 15A, but it seems a little extreme to reduce the entire circuit just for that last bit of wire.

Finally, I considered whether to just place a little 15A breaker after the outlet but before the "box", but again, that would cost money, and frankly requires work I don't want to do.

In short, is "placarding" enough? Or, am I being too lazy? What do you guys recommend?

Thanks all for a great forum!

Register to Reply
Pathfinder Tags: 15A 20A circuit breaker placard
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#1

Re: Did I screw up?

11/12/2016 6:50 AM

I'd be lazy like you; I'd placard it and not worry about it.

These days Christmas lights are LEDs and are getting more efficient, so even if someone ignored the placard and plugged in a bunch of lights it's not likely they'd overload the line. And usually the light strings have their own current limit fuses. (I bet they're limited to 15A anyway.)

When the house is eventually sold a home inspector will note the situation in his report, and then it will be up to the new buyer to ask you to upgrade the circuit or to live with it.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#2
In reply to #1

Re: Did I screw up?

11/12/2016 7:58 AM

Anyone. Trying to plug a heavy load into a light socket addapter should have their head examined.

Consider adding an outdoor 20 amp gfi outlet and get rid of that pulling elbow. If needed..

__________________
High Tolerance is Beautiful
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#7
In reply to #2

Re: Did I screw up?

11/12/2016 12:13 PM

Agreed, it will happen.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #2

Re: Did I screw up?

11/12/2016 6:49 PM

That would be incorrect procedure.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#3

Re: Did I screw up?

11/12/2016 9:36 AM

Maybe we should ask, Donald Trump.

Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Did I screw up?

11/12/2016 10:26 AM

The NEC says, "unless specifically permitted in Section 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG".

It'll be fine!

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#5

Re: Did I screw up?

11/12/2016 10:34 AM

At 10 feet the voltage drop would be negligible. Also technically 14 ga wire in a residential application is good for 17 - 18 amps and a 20 amp circuit should not be run over 80% capacity which put it rat that the working limit.

Also a screw in light socket adapter or light socket itself and its related wiring is not rated for even 15 amps continuous duty anyways so if someone did try and run a 18 amp load off one it would burn up way before the 14 ga feedline ever got close to be too hot to be dangerous.

I call it a non issue 'what if' concern. Take you OCD meds and forget about it.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Did I screw up?

11/12/2016 11:13 AM

Your display size and choice of bulbs, whether incandescent or LED, will influence your energy bill the most. For example, a 100-count string of incandescent mini lights runs at 40 watts, while a 70 count of 5mm Wide Angle LEDs is approximately 4.8 watts total. In fact, because incandescent wattage is 80-90% more than LED wattage, the cost to power an incandescent can be up to 90x greater than powering an LED.

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#16
In reply to #6

Re: Did I screw up?

11/12/2016 11:44 PM

'.... For example, a 100-count string of incandescent mini lights runs at 40 watts, while a 70 count of 5mm Wide Angle LEDs is approximately 4.8 watts total. In fact, because incandescent wattage is 80-90% more than LED wattage, the cost to power an incandescent can be up to 90x greater than powering an LED.....'

.

Want to try that again? Go ahead, everyone needs a do-over, every once in a while.

Look, if you ignore the bulb count and just declare the strings equivalent for comparison, then the incandescent wattage is 8.333 times the LED wattage. So not 80-90% more, 733% more (833% of the LED wattage).

That would cost more than 8 but less than 9 times as much than powering the LED string. That is still a significant difference, even if it isn't quite the 90% you were swinging for.

.

If you compare on a per bulb basis, the difference is still large but quite so.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Did I screw up?

11/12/2016 12:46 PM

Technically it's a code violation as it stands. You can easily fix that by changing the 20A breaker to a 15A breaker. The higher wire size is totally irrelevant. Outlets are rated 15A anyway, and the screw in adaptors for light sockets are often not even rated for that; I'm looking at one right now that says 10A max.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#10
In reply to #8

Re: Did I screw up?

11/12/2016 7:17 PM

..really? wouldn't he have 20A receptacles?

And you're asking him to downgrade at the panel?

That's a HUGE! no-no.. technically.

__________________
High Tolerance is Beautiful
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #10

Re: Did I screw up?

11/12/2016 7:42 PM

That's twice now that you don't know what you are talking about.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#12
In reply to #11

Re: Did I screw up?

11/12/2016 7:45 PM

Oh I've been wrong a lot more than twice.

..I caught it. I was thinking the other way around and with 14G

I've seen it so many times that I can't get it right.

...I was just testing your knowledge.

..it still depends on ther situation

__________________
High Tolerance is Beautiful
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: Did I screw up?

11/12/2016 10:00 PM

That table is not very rational; I wonder who dreamed it up.

Apart from that, it is not relevant to the point I was making.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#14
In reply to #13

Re: Did I screw up?

11/12/2016 10:40 PM

well I'm glad you're enjoying yourself.

-take a hike

__________________
High Tolerance is Beautiful
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #14

Re: Did I screw up?

11/12/2016 11:12 PM

Not until you cease posting incompetent material.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#17

Re: Did I Screw Up?

11/13/2016 12:34 AM

I'm sorry.. did I offend you?

If all you're going to do is twirl around like an annoying tornado.

PLEASE don't comment.

If you would like to comment and contribute to the community in a constructive and friendly manner. Please feel free to do so.

-everything is interesting but your more

__________________
High Tolerance is Beautiful
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18
In reply to #17

Re: Did I Screw Up?

11/13/2016 2:20 AM

Please feel free to edit that illiterate post before asking for a real response.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#19
In reply to #18

Re: Did I Screw Up?

11/13/2016 9:32 AM

You are not friendly

-sorry for you and yours

__________________
High Tolerance is Beautiful
Register to Reply Score 1 for Off Topic
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#20
In reply to #17

Re: Did I Screw Up?

11/13/2016 10:49 AM

Hey, hey hey, can't we all just get alone... I have an idea, let's have a square dance.... everybody likes square dancing.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#21

Re: Did I Screw Up?

11/13/2016 11:41 AM

Replace either the breaker (with a 15 amp) or re-pull the wire.

The codes are written to take into account things you might not consider (like water getting into your box).

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#22

Re: Did I Screw Up?

11/13/2016 1:12 PM

"placard" the box and get on with life.

In the highly unlikely event that the box gets wet a 20 AMP circuit breaker will still trip before 10 feet of 14 ga wire will catch fire.

I get codes. I used to work at an OEM where we had to specify all equipment electrical installations to accommodate the FLA loads on every piece of equipment in the line, which might be 100 feet long even though there was never an occasion that they would run anywhere near total FLA. It drove our customers crazy, but it was "the code".

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#23

Re: Did I Screw Up?

11/13/2016 6:31 PM

The UK wiring regulations allow another method.

If the wire of reduced section at the end of the circuit [or on a spur] is protected against Short Circuit by the source breaker then it is permissible to put the Overload protection for the "reduced section"at the end of the circuit/spur, in your case, the "gray box".

For example, 1.5 sq.mm twin cable is rated 16.5 amp in conduit and is used with 16 amp distribution board MCB which magnetic trips on short-circuit with a maximum circuit loop impedance of 2.25 ohms @230V.

1 sq.mm twin cable is rated 13 amp in conduit and can be overload protected by a 13 amp ceramic fuse (breaking capacity for the common domestic 1" x 0.25" fuse is actually 6 kA - as much as the usual domestic board MCB).

20 metres of 1 sq.mm is 0.88 ohm loop which gives a short circuit prospective current of 230/0.44 = 262 amps.

Use of adiabatic equation or a chart shows that short circuit limit of standard 1 sq.mm PVC insulated copper cable is ~0.2s @ 260 amp & >1 sec @100 amp, compared to the 16A breaker trip time of less than 0.1 sec at 80 amp.

Register to Reply Score 1 for Good Answer
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); gutmonarch (1); JE in Chicago (6); JRaef (1); lyn (3); phoenix911 (2); tcmtech (1); Tornado (5); truth is not a compromise (1); Usbport (1); WJMFIRE (1)