Optimum Selection of One Common Spare Motor Against Three

01/27/2018 10:28 AM

What could be the best alternative (Electrical as well as mechanical) in form of one common spare motor (Motor - D) against undermentioned three VFD operated motors i-e Motor-A, Motor-B and Motor-C ?

ELECTRICAL DETAILS:

Sr #

MOTOR

NAMEPLATE RATING

PART LOAD

RUNNING RPM

APPLICATION

1Motor-A800 kW, 690 V, 1492 RPM50 %95 %Fan
2Motor-B700 kW, 690 V, 993 RPM66 %87 %Mill
3Motor- C590 kW, 690 V, 992 RPM77 %90 %Mill
4Motor- D? kW, 690 V, ? RPMFan / Mill

MECHANICAL DETAILS:

Sr #

MOTOR

FRAME SIZE

SHAFT HEIGHT

SHAFT DIA

A

B

E + C

1Motor- A4504501208001000460
2Motor- B4504501208001000460
3Motor- C4504501107501000565
4Motor- D450450??1000?

Mechanical dimensions are in mm.

It is requested that keep focused on technical aspect instead of posting like contact OEM etc. We are already working on it with different vendors. Purpose of this post is to share ideas regarding optimum choice and major points to be considered in such type of selection.

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: OPTIMUM SELECTION OF ONE COMMON SPARE MOTOR AGAINST THREE

01/27/2018 10:31 AM

Well, what do you think?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Optimum Selection of One Common Spare Motor Against Three

01/27/2018 4:57 PM

If a motor is process critical for a high value product you carry a spare on stock. Expensive it may be but what are the down time costs?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Optimum Selection of One Common Spare Motor Against Three

01/27/2018 5:55 PM

You'd be better off going with one of each if you can't decide. You don't have any head room with any of these and at those high loads what is your current efficiency?

Hopefully, you have provided your vendors adequate information to allow them to make an informed decision.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Optimum Selection of One Common Spare Motor Against Three

01/27/2018 7:21 PM

Please explain further about the Part Load entries. (One interpretation would be that all the motors are oversized.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Optimum Selection of One Common Spare Motor Against Three

01/27/2018 10:40 PM

Your highest torque requirement is the 700kW/993RPM motor; 6731 N-m. If you then translate that to your highest speed requirement, 1492RPM, your only way to have one motor take care of all three is to get a motor capable of 6731 N-m at 1492 RPM. That will result in an 1100 kW 4 pole motor, and may not fit in that frame size. I think you need two motors minimum; a 4 pole 800kW and a 6 pole 700kW, with the smaller shaft and an adaptor bushing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#7
In reply to #5

Re: Optimum Selection of One Common Spare Motor Against Three

01/28/2018 2:51 AM

Thanks to all participants.

ELECTRICAL SIDE:-

Sr #

MOTOR

NAMEPLATE RATING

PART LOAD

RUNNING RPM

RUNNING TORQUE

RATED TORQUE

1 Motor-A 800 kW, 690 V, 1492 RPM 400 kW 1415 2700.00 5120 N.m
2 Motor-B 700 kW, 690 V, 993 RPM 460 kW 865 4715.00 6732 N.m
3 Motor- C 590 kW, 690 V, 992 RPM 455 kW 893 4540.00 5675 N.m
4-i Motor- D-1 800 kW, 690 V, 1492 RPM 5120 N.m
4-ii Motor- D-2 800 kW, 690 V, 992 RPM 7694 N.m

We have two options

a. Either to select 800 kW, 1492 RPM motor.

i. Its rated torque is 5120 N.m.

ii. No issue for motor-A

iii. Motor-B & Motor-C running torques are 4715 & 4520 N.m.

iv. In simple words it will be 531 kW, 992 rpm motor.

OR

b. Select 800 kW, 992 RPM motor.

i. Its rated torque will be 7694 RPM.

ii. No issue for motor-B & Motor -C

iii. When operated at 1492 RPM for Motor-A , its rated torque will be reduced from 7694 N.m to 5120 N.m. Running torque demand of Motor -A is 2700 N.m

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #7

Re: Optimum Selection of One Common Spare Motor Against Three

01/29/2018 10:32 AM

I think one of us may have miscalculated the torque of the 2nd and 3rd motors. I assumed they were 6 pole based on the RPMs being nameplate, not as used, you likely assumed they were 4 pole and are being used at the lower speeds via the VFD.

In truth, the OP did clearly state it as the motor NAMEPLATE data, so motors 2 & 3 are 6 pole, making their rated torque HIGHER than the 4 pole motor in #1.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#13
In reply to #5

Re: Optimum Selection of One Common Spare Motor Against Three

02/02/2018 9:24 AM

Instead of selecting 50 Hz motor, 60 Hz motor looks a more suitable choice.

Let Selected motor is 800 kW, 690 V, 60 Hz, 1194 RPM

i. 800 kW Motor Rated Torque: 6400 N.m @ 1194 RPM

Meet rated torque capacities of motor B ( 6732 N.m ) & C ( 5675 N.m )

ii. 800 kW Motor Rated Toque: 5120 N.m @ 1492 RPM

Meet rated torque capacities of motor A ( 5120 N.m)

FACTORS NEED FURTHER INVESTIGATION:

i. It seems convenient to operate 60 Hz motor from 40-75 Hz as compared to operate a 50 Hz motor from 40-75 Hz.

ii. One factor that need to be investigated is that what would the noise level for motor operation between 40-75 Hz operation in case of 800 kW 50 Hz as well as 800 Kw 60 Hz motor.

iii. Variable frequency drive de-rating in span of 40-75 Hz operation.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6

Re: Optimum Selection of One Common Spare Motor Against Three

01/27/2018 10:41 PM

What is the probability your process will change enough within the lifespan of these motors that you might need all 800kW of your largest motor?

Or that your mill production might be increased with some easy modification, so that you might need 800kW at Mill B or 700kW at Mill C. In that case, an easy selection. The losses attributable to running an oversized motor will be very small, higher windage against lower I2R losses, don't look at efficiency numbers, calculate the actual kW losses for each motor and compare directly.

If you try over-speeding your 6 pole motors into constant HP range, you might squeak by, on the 4 pole application, easy calculation to see if it will work. Balance speed might be important to specify.

There is not enough information on what you can or cannot change for the motor envelope to evaluate the benefits of a single spare, you need to disclose your constraints. It is normally not as insurmountable as not having enough torque available.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Optimum Selection of One Common Spare Motor Against Three

01/29/2018 8:49 AM

All that one has to do is compare the value of the motor with the value of the down time while the replacement motor is ordered and delivered. As this is commercially-sensitive information, no recommendation can be found here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#10

Re: Optimum Selection of One Common Spare Motor Against Three

01/30/2018 4:05 AM

You said: It is requested that keep focused on technical aspect instead of posting like contact OEM etc. We are already working on it with different vendors. Purpose of this post is to share ideas regarding optimum choice and major points to be considered in such type of selection.

How would you know if the information that an anonymous person replying here would be correct?

If you had sufficient engineering knowledge within your local group, you would not need to reach out to an online forum, unless you believe that you can somehow beat or circumvent the local suppliers.

In my experience, large-company suppliers are better. Call them.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#11
In reply to #10

Re: Optimum Selection of One Common Spare Motor Against Three

01/31/2018 1:42 AM

1. In my view 715 kW, 690 V, 992 RPM is the best choice.

2. Delivery time of such motor may take 18-20 weeks therefore two cement lines cannot be stopped for such long time ( if one of above motor out of three fails ).

3. Every difficult situation is resolved in steps. I am really thankful to the all participants specially JRef for addressing the issue as needed.

4. Sorry to say but one of the most disappointing thing about CR4 is that in response, instead of sharing experience irrelevant stuff is shared which poster or reader already know. Engineers hesitate to ask or discuss technical issues since by default replies like contact to OEM etc are received within no time and no one is interested even to read these comments.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12
In reply to #11

Re: Optimum Selection of One Common Spare Motor Against Three

01/31/2018 1:54 PM

Don’t get worked up about it. As in all things, take what you need or find valuable, ignore the rest. In this age of “social media” people often seem to be compelled to react or respond to every post, be it positive or negative. Selective disinterest is the key to happiness now.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aghvel Niazi (3); Anonymous Poster (1); JRaef (3); lyn (1); Mikerho (1); PWSlack (1); rwilliams (1); TonyS (1); Tornado (1)