Compact Fluro Lamp Flashing When Switched Off

11/21/2007 2:00 AM

on two occations as an electritain i have come accross when a incandecent lamp is replaced by a compact flurocent lamp that when it is switched off that it will flicker intermitently once every minute or so. O testing the voltage at the lamp holder on both ocations i have found what appears to be an induced voltage aprox 30 -50 vac tested using a high impeedance meter (240vac 50 hz system). My theroy is that within the compact fluro there is a capacitor which charges on the induced voltage and once charged discharged through the lamp. Am i on the right path ? if i am corect is there a lamp which is designed to deal with this problem or is there any other way i can fix this problem with out having to modify the wiring to remove the induced voltage ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: compact fluro lamp flashing when switched off

11/21/2007 3:35 AM

You did not give your location, but looking at your User-name, plus the voltage/frequency given, it appears you live on the "West Island" of New Zealand (= the Land of Oz).

So, any induced voltages would be either from leakage at the switchboard, induction from parallel cable runs, or leakage through the off/on switch.

The off/on switch can be checked easily by removing it from the circuit, switching the switch to "open = off" position,and using a 500VDC Megger, measure across the open circuited terminals. Often a high humidity, dust or other contaminants can give a low resistance across an "open" switch, thus enough leakage when switched "off" to give your symptoms.

Leakages at the switchboard, likewise induction from parallel runs of cabling is harder to track down. What I have done in the past, is to use an oscilloscope to locate the actual leakage voltage, then put a resistor across the oscilloscope terminals, with a sensitive current meter in series with that resistor. From this, the actual power leakage may be calculated.

Of course, it is possible you have old leaky cables, or new faulty cable in the installation, or some enterprising builder has spiked a cable with a nail.

Faulty new cables are more common than you think, and in over 45 years in the "trade" have discovered over 20 installations,in which the new cables were insulated with plastic compounds which were somewhat conductive, due to faulty batching at the various cable factories.

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#2

Re: Compact Fluro Lamp Flashing When Switched Off

11/22/2007 6:14 AM

Some good answers already posted by others, other possibilities are a powerful Radio or Radar transmitter within a few miles of your position.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Active Contributor

Join Date: Nov 2007
Location: SoCal
Posts: 15
#3
In reply to #2

Re: Compact Fluro Lamp Flashing When Switched Off

11/22/2007 12:16 PM

That's what I was thinking. The florescent light in the hangers clear across the flight line used to flash with each up/down of the 'Height finder' radar when it pointed that way.

But I'd think that would be isolated bulbs and less visible in the wiring.

Register to Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#4
In reply to #2

Re: Compact Fluro Lamp Flashing When Switched Off

11/22/2007 12:52 PM

It could be the radio signals as I noticed that my old car radio was picking up a humming noise every time the heathrow radar dish thing on top of the tower was facing me. THE RADIO WAS OFF!!!!!

The other thing that makes lamps go berserk is microwave energy. If you have a leaking microwave device you might have a problem altough you might have noticed in other ways such as exploding finger tips

If you do have a induction problem in the wires you could easily check by unscrewing the lamp from the socket but keeping it in the same position. If the blinking stops it must come from the wiring somewhere.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5
In reply to #4

Re: Compact Fluro Lamp Flashing When Switched Off

11/22/2007 1:01 PM

It does not have to be at such high frequencies, any radio transmitter will do this at almost any frequency, it is just a question of power and the correct distance....even a long wave station will do it I am lead to believe, though i have no personal experience here to call on.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#6

Re: Compact Fluro Lamp Flashing When Switched Off

11/22/2007 11:37 PM

Hi, ausiandy!

Sometimes there is a measurable residual voltage across the neutral lines in a household.

Mark

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#7
In reply to #6

Re: Compact Fluro Lamp Flashing When Switched Off

11/23/2007 12:13 AM

Australia has a MEN = Multiple Earthed Neutral Mains Power system.

Everywhere the Neutral wire arrives at a main switchboard, it is permanently connected to an earthed spike, pipe,or buried earth electrode.

That means the Neutral line can never rise above a few Volts with respect to "ground", even under major fault conditions.

It makes for a safer installation, requiring only single pole switches and circuit breakers.

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#8
In reply to #7

Re: Compact Fluro Lamp Flashing When Switched Off

11/23/2007 12:49 AM

Hi, Sparkstation!

Same here in Canada. And yet I have measured as much as 30+ volts across a properly grounded neutral line coming off that "switchboard", which in this case is usually a point at which all the neutral lines are sent to ground on the house panel.

I have never given any thought to why this is so. But it would appear on the surface of things that the resistance to ground is not completely at zero, and with energy flow through lines that are not in the open position, there might be some back flow being available, when grounded (again!) through those that are open, measureable on the meter placed back to ground.

Whether that is enough to flash a grounded light or not I can't say.

Mark

Register to Reply
Member

Join Date: Nov 2007
Posts: 5
#9

Re: Compact Fluro Lamp Flashing When Switched Off

11/23/2007 2:04 AM

Thanks for your comments,

In the site where i have come across this occurring there are also other compact fluros which do not flash which i guess rules out radio frequency causing the lamp to flash.

Having replaced the switch and performing IR testing from the switch board on the installation with a reading on >1M ohm. i believe that the most likely cause is a leaky switch wire as mentioned by Sparkstation.

The voltage was only read on a high impedance meter with no reading while using test lamps. Told the client to install a incandescent lamp problem fixed LOL.

Sparkstation you are correct I am writing from the land of oz, Did my trade in NZ but the mining money over here was to much of a temptation and it is too bloody cold in NZ

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#10
In reply to #9

Re: Compact Fluro Lamp Flashing When Switched Off

11/23/2007 3:22 AM

Many years ago, I nearly went to the Blackwater coal project in Queensland.

A couple of years later, I almost went to Mt Newman in the Pilbara.

Because we had young children my wife was not prepared to shift across at that time, but as we now look at the relative state of living in Australia or New Zealand, we wish we had moved across the Tasman some 35 years ago.

Ah well, we don't seem to have droughts here, and don't require air-conditioning either.

Here's a nice picture, somewhat local to me:


Did you know that under the Constitution of Australia Enabling Act, that New Zealand is a State of Australia.

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Register to Reply 10 comments