Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/26/2007 10:12 PM

Dear Sir,

At our site we use 110 V DC supply as our control relay supply. But I coudn't find Contracts with 110 V DC coil supply from the market for replacements, but they have 110 V AC coil supply contactors. Therefore I want to know whether I can operate 110 V AC coil contactors from 110 V DC supply without any problems.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/26/2007 10:46 PM

In a word, No.

AC coils and DC coils are wound in completely different manners.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/26/2007 11:55 PM

No.

Is it 110 V DC coil dc contactors.or 110v DC coil ac contactors.

Generally these contactor coils are slow moving items ,will not be readily available in the open market.May be you can contact the manufacturer of the contactor and they can supply ,but they may require lead time.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#3

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/27/2007 12:15 AM

If you are desperate you could use a variable voltage DC supply and monitor current & voltage. Run it up until the contactor just pulls in reliably and go about 20% higher with the voltage. Then use your voltage and current readings to calculate the value needed for a dropping resistor to drop the 110VDC to this voltage--110V-(pull-in voltage + 20%)divided by current reading=resistance in ohms. Then multiply this voltage by the current to get the power that will be dissipated by the resistor and at least double it to get the necessary power rating of the resistor for reliability. Check the wattage rating of the coil to be certain you are not exceeding it by multiplying the new DC coil voltage by the new DC current.

If you do not have a variable DC supply you could use a variac feeding an unregulated fixed supply as long as it is not a switching type or you could feed a bridge rectifier with the variac and filter it with a large value electrolytic capacitor of an appropriate voltage rating. It would also be possible to use a rheostat to drop the 110VDC for this calculation if you have one.

Register to Reply
Guru

Join Date: Dec 2005
Location: Etats Unis
Posts: 1871
Good Answers: 45
#9
In reply to #3

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/28/2007 4:27 AM

This is probably not a good idea. It is likely that the amount of current you would need with the fewer number of turns likely to be on an AC coil would create excessive power dissipation in the coil.

I would say if you are desperate try rewinding the coil with more turns of smaller wire, assuming you can disassemble the device.

__________________
The hardest thing to overcome, is not knowing that you don't know.
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/27/2007 2:21 AM

Hello Asitha,

AC Contactors/Relays and DC Contactors/Relays have different magnetic circuits too.

AC Contactors do not require any extra small airgap, because being AC supply,the magnetic circuit is switched through zero, each time the polarity of the applied AC reverses - The return springs then quickly pulling the poles apart on power-off to the operating coil.

DC Contactors normally require a small air gap, sometimes retained by a small non-magnetic "button or rivet", between the opposing pole faces.

This airgap prevents the two pole faces from making full contact, with the attendant risk of the poles sticking together, upon power removal to the operating coil.

Yes, I do know that springs are there to ensure pole separation on power removal to the operating coil.

If you look at the Contactor/Relay construction, you should normally see the small article, which maintains a tiny airgap, on DC Contactors.

AC Contactors/Relays must therefore be used on AC sinewave supply (What they are designed for)

DC Contactors/Relays must therefore be used on DC supply (What they are designed for)

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Commentator

Join Date: Dec 2006
Posts: 88
#5
In reply to #4

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/27/2007 4:28 AM

Dear All,

Thank you very much for all your valuable supports.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #4

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/28/2007 11:55 AM

Well put! As usual!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#6

Re: can 110 V AC contactor coils operate from 110 V DC supply?

12/27/2007 5:08 AM

http://cr4.globalspec.com/comment/124127

if you are still desperate and can calculate the resistor value (don't forget the power rating of the resistor) using a KTBG DC contactor as a reference, this is another option.

Register to Reply
Anonymous Poster
#7

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 12:38 AM

No , if you use 110v Ac contactor coil , it shall chatter and shall make & breakas the contact per the supply frequency.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#8

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 1:08 AM

Hi Asitha,

DC: Direct Current; AC: Alternative Current.

So they are different and you have to use DC equipment for DC power supply and AC for AC.

If you want to use 110 VDC power supply for Contactor with DC coil you can build a circuit that transform 110 VDC to 48 VDC or 24 VDC e.g. adding a resistance in serie to coil; or serial connecting 2 coil of 2 contactors with 48 VDC,.....

good luck

__________________
Nature is unlimited, human's knowledge is limited
Register to Reply
Anonymous Poster
#10

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 6:26 AM

We can use one additional an other type of relay/cotactor of 110DC supply whichever available. That cantactor may support to opperate the second contactor (in place of original 110DC Contactor) of available voltage range.

Register to Reply Off Topic (Score 5)
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 6:50 AM

AC coils will not cause a DC contactor to chatter.

You will probably find that a 220 Volt AC coil fitted in your DC contactor will operate ok at 110 volt DC give it a try out of circuit to prove it.

Or if you cant find an AC coil for your contactor a 220 volt AC contactor will probably be ok but be careful with the current rating you will probably have to up size for DC power.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#12

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 7:26 AM

Dear Friend

We manufacture battery chargers for power plants and substations and regularly use 110 V DC rated contactor with 110 V DC coil in same. We have supplied these equipment in India & abroad. In our design we have found that these coils very very rarely fail and therefore cannot comment on why the coil has failed, in the first place, in your equipment. Failure of DC coil is a serious failure. Please send me contactor part no. or the make and current rating so that the right solution can be suggested.

Thanks and regards

Ashok Toshniwal, Bangalore, India

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#13

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 8:47 AM

The Coil will fail. AC coils have impedance which is due to the inductance and resistance of the coil.In Dc current is limited by Resistance only.So u can understand now.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#14

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 9:06 AM

We use AC solenoids on DC supplies for many projects with one important caveat. The coil dissipates more power and will burn out in short order. Therefore, we only use this arrangement in applications where the solenoid is activated for short time intervals at low duty cycle. Do NOT consider leaving the coil activated for any length of time.

Register to Reply
Member

Join Date: Dec 2007
Location: Black Hawk,sd
Posts: 5
#15

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 10:18 AM

What computer program do you recommend to control the relays for a bio-diesel plant? The type of computer program will also set the control voltage for the relays that are used for control motors, valves, heaters, etc. What control voltage should these relays be?

Thanks for the info. D Fuller

__________________
Bio-Bill/Algae Andy
Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#17
In reply to #15

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 8:08 PM

Probably Programmable Logic Controllers (PLC) could do the job.

To arrange their programs you need:

  • to have the lists of relays / contactors / heaters i.e. outputs in entire system
  • to have the list of inputs as push buttons, sdensor, meters etc
  • selected type of PLC (e.g. Rockwell, Siemens)
  • software for these PLCs
  • have a knowledge to enter the program (Logic Ladder, Block or other) from the computer (download) to PLC memory.

Some of gen-sets have their own controllers.

Again your question is not clear enough to give more specific suggestion.

Register to Reply
Anonymous Poster
#19
In reply to #15

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 8:57 PM

You could use a plc, however i am using a basic stamp micropocessor and a custom

made controller to run a sawdust fired furnace to heat poultry houses.

email me at slowtell@farmerstel.com for more info

Register to Reply Off Topic (Score 5)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#20
In reply to #19

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/29/2007 12:07 AM

Some of my students. after taking Programming in (Q)Basic downloaded available other version of Basic e.g. FBasic that is the part of Stamp micro. In Stamp's Instruction manufacturer usually writes its programming language and it must be used. I have done a few simple programs (e.g. 4 In + 4 Out) several years ago. At this time there were some books, I believe you may find still them on eBay. Some could be eBook very cheap - downloadable.

Aha... Outputs to motors or any other loads with inductive impedance (relays, valves) must have surge protecting diodes. If Output voltage is 5 Vdc but your valve is 24 Vdc you must add an extra transistor power amplifier also with protecting diode reverse biased.

Register to Reply Off Topic (Score 5)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#18

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/28/2007 8:18 PM

From the experiment: "DC voltage for AC relay coil"

For relay/contactor with 110Vac needs less DC Volts:

1. to close (energize) e.g. 30 Vdc

2. to hold (keep closed) e.g. 11 Vdc

so for continuous work (holding it closed long time) you need to have;

1. Dc Power supply about 35 Vdc or specially selected resistor to drop 110 Vdc- 35 Vdc = 75 Vdc for relay coil inrush current

2. Additional resistor to holding branch (to keep holding current) just above measured (in this example 11 Vdc) dropping value. This branch uses usually auxiliary contacts of the relay.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#21

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/30/2007 2:59 PM

First response is NO.

But, some small AC coils the winding wire is so fine the dominant term is resistive and not inductive, and those will work OK on DC also. This can be checked by taking the DC resistance of the coil, then dividing VAC/R and noting if it is the same current that the coil draws when energized with AC. If the AC current is much less then you have a large inductive component to contend with.

If you use series resistors with the coil you can limit the current to the coil. If you need momentary high current to pull in the contactor, then use less dc resistance and a normally closed contact of the contactor that will open and add the remaining resistance for holding levels. If the contactor tends to stick closed due to the residual magnetism in the contactor increased spring pressure, or the introduction of aluminum or brass shim stock into the gap of the armature will reduce the residual forces.

It is a fun bench experiment and gives good understanding of what is involved.

As an aside, an AC electric door solendoid lock was bothering people in an office. A small rectifier was put in place to drive DC to the solenoid, so rather than a buzz it was a click. It worked great!

Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#22

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/31/2007 12:56 AM

Dear Friend

Are you looking for contacts of the DC contactor or the coil of DC contactor. PLEASE NEVER EVER USE CONTACTOR WITH AC RATING POWER CONTACTS FOR DC APPLICATION. YOU STAND A VERY HIGH CHANCE OF CONTACTS GETTING BURNT DURING MAKING/BREAKING IF AC RATED CONTACTS ARE USED FOR DC APPLICATION. DC RATED CONTACTORS are COSTLIER compared to AC RATED CONTACTORS.

Your problem is not a serious issue, just a question of PROPER SOURCING. Please give the contactor make, part no. & rating and we can EASILY supply same or tell you where to get it from.

We manufacture battery chargers for power plants and substations and regularly use 110 V DC RATED CONTACTS with 110 V DC COIL in same. We are approved by ALMOST ALL LEADING ENGINEERING CONSULTANTS IN INDIA & have supplied these equipment in India & abroad. In our design we have found that coils & contacts very very rarely fail and therefore cannot comment on why the coil/contact has failed, in the first place, in your equipment. Failure of DC coil & contact is a serious failure.

For any further details please contact.

Thanks and regards

Ashok Toshniwal, Bangalore, India 9448491293

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#23
In reply to #22

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/31/2007 8:42 AM

Which is why I mentioned to up size the contactor for DC power.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#24

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/31/2007 7:37 PM

Once again,"If you are desperate" to use a contactor with an AC rated coil,I had a chance to experiment today with an old Arrow-Hart ACC430UM30 3-pole 50 amp contactor with a coil rated 208-240VAC with about 238 ohms DC resistance. It pulled in at 50 volts DC and dropped out at 5 volts DC. The power dissipation at 50 volts DC is about 10 watts and that seemed a little high for continuous use so I tried using a 2200 ohm resistor in series on 120VDC to give about 11 volts on the coil with about 1/2 watt dissipation and added a 330 microfarad capacitor across the resistor to give the coil a momentary jolt to pull the contactor in and the steady state 11 volts kept it in until power was removed. It dropped out reliably every time. Don't be afraid to experiment. I am assuming you are aware of the dangers involved in playing with these voltages but once again good luck and have fun. The resistor will dissipate around 5 watts so a 10 watt power resistor should be OK and the capacitor I used was rated for 200VDC. And watch polarity.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#25
In reply to #24

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/31/2007 9:13 PM

I am happy to see someone actually applies theory and tests with experimentation.

Too many people on this forum obviously have little knowledge of what they are talking about!

(The safest professional engineer is the one that knows what he does and does not know!)

Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#29
In reply to #25

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

01/03/2008 9:59 PM

I am happy to see someone actually applies theory and tests with experimentation.

Too many people on this forum obviously have little knowledge of what they are talking about!

In response to this, thanks-maybe it's because I'm not an engineer but a maintenance tech. who often has to make do with what is available or get a piece of equipment up & running until correct parts come in. I also began each comment with "If you are desperate" and of course normally the original part would be easier and usually better but often something that should not work can be substituted if some mods are made. I've done this often with good results.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#30
In reply to #29

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

01/06/2008 12:45 PM

I have run across many "techs" with far superior application and technical knowledge and have believed they would have been a fair candidate for a PE license. I have also run across many PE that I think they got their license in a Cracker Jack box!

Register to Reply Off Topic (Score 5)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#26
In reply to #24

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/31/2007 10:20 PM

This is IT!

I did similar experiments but used two resistors:

First to energize the coil /close contactor with NC (NORMALLY CLOSED) contact in series , and second as a second branch (parallel) just to hold.

Better is to draw a diagram with values than just write dozens of statements that many times may confuse. But person asking for advise must state exact requirements and, of course in this case all available data.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#27
In reply to #26

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

12/31/2007 11:23 PM

Hooray!

We now have at least 2 engineers with a practical bent!

Register to Reply
Anonymous Poster
#31
In reply to #24

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

06/10/2010 8:47 AM

Hi I did tried what has explained by you. In mine case, contactor is switching on at 80VDC. I want to utilize this application at BTS telecom sites where battery bank voltage is 48VDC (max 60VDC). Is there any way out to lower the pick up voltage of this contactor? I know there are DC contactors available in this voltage but still I want to use AC contactor coil with DC voltage due to some specific reason. I am not a registered member, could u pls mail me at shamy_one@yahoo.co.in.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#28

Re: Can 110-VAC Contactor Coils Operate from a 110-VDC Supply?

01/02/2008 6:30 AM

Here's another vote for 'no'.

They are wound in different ways, and not intended to be used on other types of supply.

At best, control fuses will blow.

At worst, .

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 31 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Anonymous Poster (4); ashoktoshniwal (2); Asitha (1); garth (2); GW (4); HUX (1); JRaef (1); kittrellbill (1); lrsheldon (3); nam70 (1); nesubra (1); PWSlack (1); ramvinod (1); rcapper (1); southern123 (4); Sparkstation (1); welderman (1)

Previous in Forum: cable size   Next in Forum: AC Engine Alternator Conversion Project

Advertisement