Motor Overload

03/24/2008 5:39 AM

I have 3-Ph 400 volts 50 Hz AC induction motor full load amp was 24 amp trip on over load and current reach to 43 amp balanced I compare with other similar one work for same condition ( both of them are water pump) take 21 amp I disconnect the motor from the pump take about 8 amp (ie no load amp) mega test was okay 1 M Ohm resistance for three phase was balance about 11.5 Ohm no lose connection

pleas can you help on solving the problem

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: MOTOR OVER LOAD

03/24/2008 7:17 AM

Ok been there..done that...now ,...

a) Check rpm of motor it could be double than the pump design rpm.

b) Can you interchange just the motor of the two pumps and then check the results, if the problem persists then it is the pump problem.

Do post your results.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Reply
Power-User

Join Date: Dec 2006
Location: Buffalo, New York
Posts: 142
Good Answers: 1
#2

Re: Motor Overload

03/24/2008 9:45 AM

Your motor is harder than it should. Check to see if you have a plugged system (i.e., clogged filter??), also, check to be sure you have all you valves open like it should. One more thing, is there any bearing associated with the pump?? You would have a bad bearing which cause the motor to work harder, too. Please let us know your finding.

MidniteFigther

__________________
My mind is full of useful knowledge, I just don't know how it applied.
Reply
Anonymous Poster
#3
In reply to #2

Re: Motor Overload

03/24/2008 9:56 AM

I did replace the bearing although I did take pulse shock for bearing which okay

8 amp with no load accepted ?if not what should the motor amp reading

Reply
Power-User

Join Date: Dec 2006
Location: Buffalo, New York
Posts: 142
Good Answers: 1
#4
In reply to #3

Re: Motor Overload

03/24/2008 10:15 AM

Without knowing the size of you motor (hp??), I know know if 8 amps is high or not, but if your FLA is 24, then 8 amps seem to be a bit high for no load. Take a look at your motor's name plate data, it will tell you more infomation then I can. You mention you have two motor that is identical and do the same function, can you check the other motor and compared it to the problem one?? i.e., no load amps?? What is the reason you change the bearing?? Was it worn?? How about the housing?? Is it clean?? Warpped?? Sometime a new bearing won't help if the housing is warp, and not lined up.

MidniteFigther

__________________
My mind is full of useful knowledge, I just don't know how it applied.
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #3

Re: Motor Overload

03/24/2008 10:18 PM

There is no way of knowing what your unloaded amps will be, it varies by motor design. But as a gross generalization, 20-35% of the nameplate FLA is not unusual. So 8A out of 24A is 33%, probably normal.

You did not specify the type of pump, and it makes all the difference.

If it is a centrifugal pump (sometimes called a quadratic load), then the two main reasons for overloading are as follows:

  1. Open channel; too much flow. The load on the motor (and by definition the current draw) is proportional to the flow (Q) of the system. So if your system normally is pumping into a high head pressure, and a pipe or flange is ruptured so that the fluid is leaking profusely, the flow through the pump increases and the load on the motor increases exponentially. This by the way is exactly the opposite of what most people think of, but if the output of a centrifugal pump is blocked, there is no flow, so there is LESS loading on the motor.
  2. There is some kind of mechanical binding in the pump, i.e. a bad bearing or seriously misaligned coupling.

It it is a Positive Displacement (also known as progressive cavity or gear driven) pump, then besides mechanical binding again, overload can occur when there is a blockage of flow. Fluids can't compress so any blockage is the same as a locked rotor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Motor Overload

03/25/2008 5:22 AM

3. It might be going backwards (been there, done that, etc. ).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11
In reply to #8

Re: Motor Overload

03/25/2008 10:21 AM

I thought of that but dismissed it, maybe too quickly. Would the OL be that high? Usually you get less flow, meaning less motor loading, but just not the desired outcome.

But then, that would again depend on the pump design wouldn't it?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Jan 2008
Posts: 127
Good Answers: 5
#6

Re: Motor Overload

03/24/2008 10:58 PM

The problem is most likely with your water pump if it a new installation check the rpm of the motor to the rated rpm of the water pump. If the motor behaves normally with no load and all 3 phases tong the same this also points to the water pump.THe electric motor will pull as many amps as it can to get to its rated RPM eg no load not a lot of amps needed water pump clogged bearing seized etc motor pull as many amps as it can to get to rated speed

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: Motor Overload

03/25/2008 2:43 AM

First motor rating in KW and RPM is essential.Normally on low speed motors no load currents will be high like a 6P machine will have a higher no load amps than 4P.Normally it varies from 20 to 60% high end being on 8P etc.so this information is required.I hope you have the manufacturers test certificates which will give the value at the time of testing and a comparison can easily reveal the problem.Everyone should ensure that when electrical equipment is purchase all documents like type , routine test certificates are collected and also maintenance check records are maintained.Thse will be helpful.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #7

Re: Motor Overload

03/25/2008 9:33 AM

"Everyone should ensure that when electrical equipment is purchase(d) all documents like type , routine test certificates are collected and also maintenance check records are maintained."

If only the world worked like that...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#10

Re: Motor Overload

03/25/2008 10:09 AM

'Took me a while to understand the question. There's not even one punctuation in the question, not even at the end.

I must be on a slow day today, decoding rcapper's code drained me.

This question's answered as far as I can tell. I'm just typing...don't mind me.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#12

Re: Motor Overload

03/25/2008 11:53 AM

If it is a centrifugal pump, are the 2 motors running in the same direction?

It sounds creasy, but a mechanic man told me the following story; they bought a pump which was much too big for the motor, so to decrease the needed motor torque, they let the pump run in the opposite direction. The efficiency of the pump blades is then less, and the motor needs less power…

Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#13
In reply to #12

Re: Motor Overload

03/25/2008 2:19 PM

Your question is not clear but it seems you are saying the motor trips the circuit breaker at 24 amps of load.

It is not clear, at least to me, what the run load of that motor should be nor the rated load bearing capacity of its breaker.

Nonetheless, one thing I note has not been suggested, and which I have come across many times in industrial situations, is that breakers sometimes become derated, i.e., they tend to trip at lower loads then rated.

j.

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14

Re: Motor Overload

03/26/2008 8:02 AM

The original poster has not to my mind taken the time to place a correct, understandable question on CR4.

I for one have little idea of the requirements of the two motors.....

More precise infos please. Make short simple statements, check each for validity, then maybe we can help.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Reply to Forum Thread 14 comments