Generator Frequency Dips

05/13/2008 9:13 PM

Need some immediate help! This may be too general question...but I will try an provide as much information as possible....

Why would make the frequency dip on a 500 KW (480 V) Diesel Generator? So much so, that the generator will stall out during testing.

This is a generator for a hospital in the USA so if there are any suggestions for testing standards, codes, etc that you can send me...that would be appreciated.

The ATS switches are operating as they should. The bigger issue is the drop in frequency from the generator. The generator electronic steady state frequency regulator has a variance of +/- .25%. Which means the generator frequency should be in the range of 59.85 to 60.15 Hertz, it is well below this. The load of the critical branch and life safety branch is minimal, these loads should not cause the generator to bog down and drop the frequency low enough to affect the ATS switches. However, there are VFD's on one of the ATS's.

I apologize if this is too general of a question...but any suggestions or even questions would be a great help at this time.

Thanks for all the help

badski

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#1

Re: Generator Frequency Dips

05/13/2008 10:39 PM

If all is working as it ought to be, really, like phase balance of load, then I would suggest checking to make sure that the ground and neutral are good.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: Generator Frequency Dips

05/13/2008 11:10 PM

Basically the speed (frequency of alternator)of the machine will come down as you load the machine.When the speed comes down the controller(governor) will try to increase the speed to the required level,provided the drop in speed is within the range.

In your case there are two probables, 1) Speed drop is beyond range,2) controller not correcting the speed drop.

Speed drop beyond range will occur when the load is very high

Therefore ,you have to check the Load on the machine or the controller for malfunction.

If the generator is stalling then there should be very heavy load on the generator.try and load the generator in stages say 25 %,50 %75% and 100% and watch the performance.

Let us have feed back,if there is any thing.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
3
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#3

Re: Generator Frequency Dips

05/14/2008 1:49 AM

I would also be inclined to check some of the simple stuff first.

1) Check the govenor/throttle.
It is not unusual for a Generator on a load with very little variation to "Notch" the throttle. This means that as the load increases the fuel is not increase to maintain the RPMs and thus the Stall.

2) Check the Fuel inlet from the tank and also the Filter.
I have to admit to being bitten by this one.
There was a piece of "Slime" or "Black Death" in the Fuel Tank, this is a fungus that grows on diesel if not treated.
As the fuel uptake increased with load it would lift and get stuck to the inlet, blocking the fuel and stalling the motor. Since it only partially lifted, it acted as a flap and at 35% load (almost exactly) the motor would stall.

It took a sight glass in the fuel line to see it happen.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply Good Answer (Score 3)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4
In reply to #3

Re: Generator Frequency Dips

05/14/2008 6:41 AM

Hello Sapper

I've run into the diesel fungus problem years earlier, in several installations.

New Zealand Railways got a load of fungus contaminated diesel, back in the early 1970's, and it took them a few weeks before they realised what the trouble was.

Generally these days there is a fungal inhibitor included in diesel fuel, also jet fuel, which used to get the same bug.

Petrol back in the early 1970's, when there were carless days in New Zealand, and because you could not fill up "extra containers" with fuel at the Service Station, caused me to fill three 13 gallon drums with petrol, via siphoning from the car tank, so that an urgent trip could be made, in emergency.

The fuel already had the bug, and when a year later I went to use the petrol, there were spider-web-like threads all through the fuel, and over half was wasted, trying to strain out the fungus.

If the fuel is contaminated, all traces of that fuel need to be removed, the tank and pipelines cleaned with detergent, then washed thoroughly with undiluted bleach.

Fuel filter elements need to be burned.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#5
In reply to #4

Re: Generator Frequency Dips

05/14/2008 7:52 AM

Sparkstation,

I Know what you mean...It took two days of running a mix of Detergent, Disinfectant and Kero through the Tank & Fuel system.

The only Upside was that it was a Containerised Generator on Hire and the hire company wore the cost...They didn't charge us for the Hire either, but it still blew the project time lines that it was supporting out.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#14
In reply to #4

Re: Generator Frequency Dips

05/15/2008 7:18 AM

Sparky

There is a device which was invented right there in NZ which I have seen to overcome the problem of 'bug' in diesel fuel, even heavily contaminated stuff. I've just forgotten the name, but it's an array of rare earth magnets in an alloy housing through which passes the fuel. The guys say that it 'implodes' the 'bug' at a cellular level.

I argued, originally, but it works. I was amazed that the 8V92 just roared on better than ever.

For what it's worth.

Cheers,

Stu.

__________________
"Nothing, is as it seems." Dr Wally.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #3

Re: Generator Frequency Dips

05/15/2008 2:23 AM

A really good post.

Sometimes its the basics that bite us in the Butt, yours was a good "Head up" !!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#13
In reply to #3

Re: Generator Frequency Dips

05/15/2008 7:12 AM

Sorry Sapper,

I put my 2cents worth in before reading yours.

I think you're on the money. GA

Cheers

Stu

__________________
"Nothing, is as it seems." Dr Wally.
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#6

Re: Generator Frequency Dips

05/14/2008 11:04 PM

Fuel/filter would be the first place I would look, also, especially for a standby generator where the fuel has been sitting for an extended period in an isolated tank. You should have ammeters on the system- it would be pretty obvious if the problem were electrical load.

Register to Reply
Member

Join Date: Apr 2008
Posts: 7
#7

Re: Generator Frequency Dips

05/14/2008 11:56 PM

I understand today's fuel is only stable for a short period in storage. A diesel engine may idle fine, even with some problems in the chain, but when a load is applied, it may falter or stall for a shortage of any of the 3 items needed for a fire to burn: fuel, air, and an ignition source. The greater the load, the more you need. The fuel gauge may indicate that there is sufficient fuel, when there isn't. When the engine runs out of fuel, it may take some time to get it primed. I've had diesels stall for a number of reasons, but during my limited experience with generators, the power source only stalled when the load was too great or it was applied all at once, rather than in steps. Remember to start the hungriest loads first in order of their starting power requirements.

good luck.

Register to Reply
Power-User
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2006
Posts: 451
Good Answers: 16
#8

Re: Generator Frequency Dips

05/14/2008 11:58 PM

Contaminated fuel would be the first thing I would be looking for.

The next step is to run at no load idle, then progress through to full throttle no load gradually. This will eliminate the possibility of it being caused by the load interface with the governor. If you can see your exhaust fumes while this is happening monitor the colour. I had a case with a 500 kW gen set that at idle was a dream but as the revs increased even without load it would start to miss behave.

It turned out to be a faulty injector that only played up as more was expected of it. The dripping caused the exhaust fumes to indicate a rich mixture (Blue Black Smoke).

The fuel or fuel system is the most likely culprit, but it may be worth checking your air inlet for a bird nest or other obstructions. Again you could get a situation where at idle there is enough air to perform but not when the load increases and the need for air increases.

I have this theory that diesel gen sets are all female and that if you keep that in mind when you are dealing with them it helps you to get along much better.

Please keep us informed as you eliminate the possibilities.

BAB

__________________
Make it so.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#9

Re: Generator Frequency Dips

05/15/2008 1:51 AM

I agree with BAB injectors should be checked for peak performance re seat them if required. If the fuel rack is at max when on load it indicates the governing system is trying to compensate.and power is falling off to such an extent as you indicate then pumps injectors and fuel would seem to be the culprit.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#11

Re: Generator Frequency Dips

05/15/2008 3:13 AM

Normally drop in frequency is indicative of excess load.Secondly the frequency variation limit is too close for a diesel engine set .Normally +- 5% and for such close frequency a MG is set is preffered.Were the set builders/suppliers were aware of this requirement?One what I can think is check the governing of the engine.Check the load (A thorough load study may be required)and if governing is ok then u may need a higher sized set may 630KVA.Pl. also check with the set supplier.In case u have already done that what do they say?

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#12

Re: Generator Frequency Dips

05/15/2008 7:10 AM

Check the fuel flow to the injector pump. There are a few things which could give you the problem you're experiencing, however as you are already part way through the test procedure, check to see if either or both the fuel filters are waxed up and not passing enough fuel to sustain the load. This often happens in stand-by machinery. Could also be bacterial contamination of the filters, or indeed the fuel lines, or the tank outlet, also reducing the fuel flow.

Bad mix of fuel, water contamination (internal rusting of the injector pump and governor can be a by-product of this too) will also bring the machine to it's knees. Can't give accurate diagnosis 'over the phone' as don't know the maker of the motor or the fuel system, but this is a place to start. Let's know the results.

My money is on the fuel system. The electrical stuff is very reliable, as is the mechanical section.

Cheers,

Stu

__________________
"Nothing, is as it seems." Dr Wally.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#15

Re: Generator Frequency Dips

05/15/2008 10:20 AM

Have you checked for DC current from the load? Dc current produces dynamic breaking in rotating machinery. Use a clamp on meter that has a DC range to measure each phase. If you cannot find a DC clamp, use an AC clamp. You won't read anything but if it sticks, or you cannot open it while the load is on, you have many amps of DC current.

If you find DC current, check the different load branches. It is possible that an AC drive or a UPS has lost a diode and draw DC current.

Good luck

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#16

Re: Generator Frequency Dips

05/15/2008 11:25 AM

jjbadski,

What type of fuel does the generator use? Many on this thread are making the assumption that your system is diesel. In Southern California, because the Air Quality Management District (AQMD) does not allow diesel, other fuels such as compressed natural gas are often used.

Is the engine set up for the type of fuel it is being supplied?

Has this system ever operated?

Have any changes been made recently?

Register to Reply
Anonymous Poster
#25
In reply to #16

Re: Generator Frequency Dips

05/23/2008 11:45 PM

Read the org. post.

Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#17

Re: Generator Frequency Dips

05/15/2008 5:34 PM

Prist is the brand name of the microbial inhibitor we put in Learjet tanks for avjet fuel.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#18
In reply to #17

Re: Generator Frequency Dips

05/15/2008 11:59 PM

Check the fuel filter and passage to governor. Reposnse of Governor is the prolem with increase in load. Also check Droop settings if ok for the givenm load. Also does it happen at a particular time whne load suddenly increases.

Check governor opeation and fuel pump and its circuit for choking of pies and filters.

__________________
Best Regards, Shivaram
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #18

Re: Generator Frequency Dips

05/16/2008 9:37 AM

Well you really caught me out there, what did you mean by:-

and its circuit for choking of pies and filters.

??????

"and its circuit for checking(?) of pies(??) and filters."

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Anonymous Poster
#20

Re: Generator Frequency Dips

05/16/2008 1:28 PM

Most replies are addressing the engine side except a few.Is it possible to have such close level of frequency variation with a dg unless the set is over sized.Request forum to clarify this point

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#21
In reply to #20

Re: Generator Frequency Dips

05/16/2008 1:53 PM

Yes I have commissioned ( 20 months back) 3 nos 2000 kVA ,caterpillar sets in chennai India, with woodward controller, we are getting frequency tolerance between 50.15 and 49.85 hz.It is possible to achieve.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#22
In reply to #21

Re: Generator Frequency Dips

05/16/2008 11:09 PM

Ues. It is possible with Kohler make DG sets.

__________________
Best Regards, Shivaram
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #21

Re: Generator Frequency Dips

05/17/2008 6:40 AM

I agree completely. We had big emergency Diesel generators in the RN in the 60's with similar tolerances. If it was possible then, it must be possible today.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Anonymous Poster
#26
In reply to #21

Re: Generator Frequency Dips

05/23/2008 11:47 PM

I love Ramvoid!

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#24
In reply to #20

Re: Generator Frequency Dips

05/18/2008 5:33 PM

Absolutely...Essential Services site (eg Data Centres, Call Centres etc) all rely on these sorts of tolerances.

Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#27

Re: Generator Frequency Dips

06/01/2008 12:03 AM

Hello jJbadski,

A lot of posts have been made but no feedback.....

Few inputs....

a) The full load current.

b) Generator rated current

c) Total VSD application load

Check your grounding, and also bond neutral to ground.

Can you check the droop setting in the speed controller ? It might be set too high...

Hopefully you have checked the filter/fuel-fungus by now.

Any discussion can go ahead only if there is feedback...

Please keep us posted....

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#28
In reply to #27

Re: Generator Frequency Dips

06/01/2008 2:20 AM

Dear sir

I do agree with you, most of the Guests do not report back , after their problems/issues are sorted out.

Their feed back will immensely help us for future reference.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 23
#29

Re: Generator Frequency Dips

06/01/2008 11:03 AM

TO ALL....

Thank you for all your valuable suggestions and insight. As it stands right now, the governor settings were adjusted during the recent testing and everthing seemed to work properly. However, a new issue arose and that being one of the VFD's controlling an air handling unit started to "fault out" during the testing.

This is currently being investigated and I will report back as soon as I get the results. The mfg of he VFD indicated it might be a simple solution of placing the required size line reactors at the VFD to stop the transients being caused by the testing/switchover procedures.

As always, any suggestion or insight is greatly appreciated.

Agian, I thank you all for you patience and help with this issue.

badski

Register to Reply
Register to Reply 29 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: