Pressure Reducing Valves (PRV) locations?

07/04/2009 8:52 AM

Need help! I have 6"dia. riser for 1Basement to 12flr(for sprinklers ground-12th flr) & another 6"dia. riser that will run from basement to 25 flr (for sprinklers 13-25th flr) from a common header (typ. flr. elev-3.6m).On original design there are no PRV installed on system, which is not advisable, then i am planning to install PRV to control the required pressure for each flrs. At where should i placed the PRV, on the riser?, or on each floor control zone valve?, how should i tell exactly the location of PRV?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#1

Re: Pressure Reducing Valves (PRV) locations?

07/04/2009 11:50 AM

You cannot install the PRV in the main riser. That leaves you with PRV's at the start of each lateral or smaller ones at each section or individual emitter.

I don't see any mention of pumps and emergency generators.

Our fire brigade can only service 19 floors. that will leave us with at least 6 floors with a higher requirement.

The best would be to contact your local fire chief and have him recommend the best or prescribed option for you.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#2

Re: Pressure Reducing Valves (PRV) locations?

07/04/2009 2:42 PM

i think you don't need PRV for your system , that because

1)fire piping are designed to overcome the applied water pressure

2) for fire fighting system , almost no water flow all the time, then no need to control pressure for no flow pipes.

3) in case of actual fire, you need full pressure to allow the biggest coverage area for all sprinklers

4) other way to control sprinklers pressure without using PRV is to use different pipe diameters for each floor ( it may be considered in your building design )

5) As other member said, it's better to consult chief fire man before taking your decision

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Commentator

Join Date: Sep 2008
Posts: 70
#3

Re: Pressure Reducing Valves (PRV) locations?

07/05/2009 8:51 PM

You need to place one PRV to serve your low zone (Basement to 12th floor). It can be placed before the low zone riser. PRV on each floor will be expensive..

Register to Reply
Commentator

Join Date: Jun 2009
Location: Between India & Australia
Posts: 71
Good Answers: 3
#4

Re: Pressure Reducing Valves (PRV) locations?

07/06/2009 8:05 PM

Have you considered pressure regulating hydrant valves.

Given your piping system is designed to handle the pressure, one of the solution to overcome the high pressure in the lower zones would be to use pressure-regulated hydrant valves. These deliver a constant pressure downstream of the hydrant (typically 3.5 barg) irrespective of the higher pressure on upstream side. These are available commercially.

Good luck!

__________________
Continuous Learning
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#5

Re: Pressure Reducing Valves (PRV) locations?

07/08/2009 12:31 AM

PRV on each floor control zone valve to control each floor.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply