At the Clarion Mansion Inn in Sacramento, we fired the previous stationary engineers.

Before they left however, they removed ALL of the Barber colman actuators and chopped up the wiring, so now the building's heating/cooling must be controlled by gate valves (meant for bi pass, not permanent control).

I am not a registered engineer in California, and need assistance and ADVICE in returning this system to an operable condition. Any and all comments are welcome and a bid or two for estimates might even fly.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: barber colman hvac valve nightmare! help!

11/03/2009 9:12 AM

What is a "stationary engineer"????

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: barber colman hvac valve nightmare! help!

11/03/2009 10:28 AM

One that looks good on paper?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3
In reply to #2

Re: barber colman hvac valve nightmare! help!

11/03/2009 11:14 AM

I'll bet bgillming thinks they would look good behind bars!

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#21
In reply to #1

Re: barber colman hvac valve nightmare! help!

11/08/2009 10:24 AM

certified Boiler Operator

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Commentator

Join Date: Nov 2008
Location: Houston, Texas
Posts: 70
#4

Re: Barber Colman HVAC Valve Nightmare

11/03/2009 11:27 AM

My guess is the stationary engineers probably shouldn't have been allowed access after being fired

__________________
God Bless everyone!
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#5

Re: Barber Colman HVAC Valve Nightmare

11/03/2009 12:41 PM

Presumably stationary engineers are those retained on site?
Maybe the guy who fired them can fix it, or maybe an accountant could do it?
The 'manager' who allowed this situation to occur should certainly be fired.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #5

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 8:15 AM

I agree with you completely.

You would think that a manager entrusted with employee termination, in the world's biggest "Hire 'n Fire" Nation (the USA) would know how to go about this correctly........

I would assume that legal action is being taken and the people responsible must pay, so why worry, get a firm in to "repair" the situation fully.....or tell the perpetrators to do it at their own cost!!!! And in a set time scale......with a guarantee......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#6

Re: Barber Colman HVAC Valve Nightmare

11/03/2009 8:04 PM

Regardless of labor issues, I'd be worried about fire.

My ADVICE is you get your Commercial Insurance Agent there to shut the building down till it is safe.

I do not know enough to give you a bid for command of the situation.

For a scout and plan from where I am in NC, 20 grand would get me out of the house and back.

Otherwise figure 4 million 2 hundred and 87 dollars and 57 cents as my initial bid, knowing nothing.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Commentator

Join Date: May 2009
Posts: 64
Good Answers: 6
#7

Re: Barber Colman HVAC Valve Nightmare

11/03/2009 11:02 PM

Found this online, a comment made back in 2007...

"This "hotel" is a complete disgrace. The thermostate is an illusion. The only thing you really have control over is the fan. They control the AC and Heat from the desk. I went to bed running the AC and woke up at 2:30am in a pool of my own sweat, had to be something like 95 degees in the room. I guess the night staff was a little chilly down stairs. They claim there is just one pipe of either hot or cold air. Aside from that, some other posts claim there is a lot of history at this hotel..... I agree, the furnishings should have been in a landfill 30 years ago."

Will fixing the actuators fix your problems? Judging by this and other comments made online about this hotel, not likely. Why did the "stationary engineers" quit? Likely because of impossible conditions in a hotel in sad shape, desparately requiring major HVAC, plumbing, fire and other upgrades. How old are the systems? Probably over 30 years and more likely 40 to 50 years old, right? Likely the building is rife with code violations, and any work will trigger a whole slew of required life-safety upgrades, not to mention proper guest comfort.

That comment about only one "pipe" for either heating or cooling really concerns me. Such a system could not function properly, nor meet the expectations of the modern traveller/guest. Also, likely very energy inefficient.

My bid for a complete HVAC retro-fit would be in the neighbourhood of $15,000 per room for 106 rooms, not including facilities and amenities such as restaurants, pool rooms, mechanical rooms, etc. Using a dull pencil, I would say you are looking at about $2 to 3 million for a total mechanical renovation.

Register to Reply Score 1 for Off Topic
Anonymous Poster
#9
In reply to #7

Re: Barber Colman HVAC Valve Nightmare

11/03/2009 11:50 PM

tell the owners of the hotel to sell and solve their problem of yours

crm

Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#10
In reply to #7

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 2:40 AM

Dear Duane,

You are undercutting me!

(Though I feel it would be good to add another 5 grand to not stay at the place for a scout.)

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#8

Re: Barber Colman HVAC Valve Nightmare

11/03/2009 11:31 PM

How about some more info Like model numbers, voltage, feedback type...

What temperature controller are being used, brand, model#, voltage, feedback...

The barber coleman actuators I'm familiar with are fairly straightforward, the operation has much more to do with the controller than the actuator.

Register to Reply
Power-User
United States - Member - US Citizen - Born & Raised Engineering Fields - Control Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Instrumentation Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Energy Engineering - HVAC/R Simplified Using PLC Controls

Join Date: Mar 2007
Location: Brick, NJ (USA)
Posts: 110
Good Answers: 5
#11

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 5:59 AM

With all due respect to the "on-line" bidders, you need to have a mechanical contractor perform a walk through of the building and submit a "real numbers" quote. In the mean time, your catastrophe can be temporarily mitigated by re-installing a new actuator on each valve with a local controller & temperature sensor to modulate your heating water in each room. I also can show you a way ro re-set your central plant heating water to control the water temperature based on the calculated heat loss of your building.

Without performing an equipment audit, true costs cannot be determined. Here are my material costs for your consideration:

Each Room with one valve, one fan coil, one sensor and local controller:

Valve actuator: 3/4-inch = $250 - $500

Local Controller: PLC w/HMI & relays, sensors = $1000

Central Plant Control: PLC w/HMI will control Boilers, Pumps, Mixing Valves with boiler optimization stratedgies = $20,000

All labor is additional. Wiring may be able to be installed using "surface mounted" wiring if acceptable to your local jurisdiction. This would reduce your install costs.

Please contact me for any additional questions or help with consultation.

John Castoro

Innovative Logical Controls, LLC

www.innovativelogicalcontrols.com

800-208-5461

__________________
"Memorize the calculations, you look like a fool searching your notes while teaching class"
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#13
In reply to #11

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 10:21 AM

The unspoken issue is that management has probably tossed out a union.

The original poster [OP] is just trying to figure out how to keep from having to dash from room to room...

OP knows he's working for the devil, which isn't the end of the world, just part of the overall package.

jcchiefeng Has a good plan, if mgt. is willing to actually spend real money, which is doubtful.

Register to Reply
Anonymous Poster
#14

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 11:51 AM

Advertise the Hotel as "adventure for back-packers", release some rats and make the guests sign a disclaimer when registering.

No, seriously, get the manual for that controller and for that actuator, read and understand the "basic configuration" or "basic application" example, including schematics.

Hopefully all rooms are controlled in the same fashion, so it will be a repetitive task after fixing the first one. It will take a bunch of courage and no fear of getting dirty though.

Good luck to you and your crew.

Yahlasit

Register to Reply
Associate

Join Date: Sep 2009
Posts: 32
Good Answers: 1
#15

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 12:36 PM

Tell me more about your central plant. Boilers chillers and all?

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#16

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 6:00 PM

The OP came here for some help, not to be the brunt some of your jokes. I've had to clean up after vandalism, it's not at all fun nor funny. Seems like some of you guys have nothing better to do than sit in front of your computers and try to think...., instead of trying to a guy out. If I can help the OP, he/she can contact at dj95401@gmail.com

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#17
In reply to #16

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 7:22 PM

I think I did say that it sounded like a dangerous situation.

Us veterans use humor when horrified.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#18
In reply to #16

Re: Barber Colman HVAC Valve Nightmare

11/04/2009 7:54 PM

If the OP would have included more details, the chance of meaningful advice would increase greatly.

The circumstances are bound to generate lots of speculation & some digging into the back story...

The OP has all of 1 post & will probably never be heard from again

DJ you really shouldn't post your email unless you like spam

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#19
In reply to #18

Re: Barber Colman HVAC Valve Nightmare

11/05/2009 9:10 AM

"The OP has all of 1 post & will probably never be heard from again"

I see by the profile that this problem only held his interest for about 14 hours. Has not returned to the forum since 7:38 PM on 3 November.

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#20
In reply to #19

Re: Barber Colman HVAC Valve Nightmare

11/05/2009 9:15 AM