Instrument Cable for Digital Signal

05/03/2010 12:54 AM

What type of cable should I use to transmit 24 V dc signal from field instruments to PLC, Field instruments are level switch, pressure switch.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Instrument cable for digital signal

05/03/2010 2:13 AM

Twisted-pair shielded (foil or braid, possibly multiple pairs) seems to be a commonly specified choice. A prominent manufacturer of such cables is Belden, and I think they have lots of good information, as well as a wide selection. The switch signals you describe are discrete on/off, so you might not need the shielding that would pertain to analog data such as 4-20ma or 1-5 VDC or mv thermocouple signals. The manufacturers of the devices you mention will also have good recommendations.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#2

Re: Instrument cable for digital signal

05/03/2010 2:19 AM

Any cable can work at 24 volts, but only thing that need to be seen is what is the status of cable when 24 Volts is not there, Does it come down at ground level or is it just floating as an open circuit,

You need to ground this cable with a reasonable size of resistance if the pressure switch is just like an on off switch,

Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#3
In reply to #2

Re: Instrument cable for digital signal

05/03/2010 2:42 AM

Good point. If the PLC input is high impedance even with the switch open the input could float up to 24v, especially if there are other 24v lines in a cable bundle. I've seen this happen before and it's difficult to troubleshoot. The solution was a 10k resistor across the PLC inputs. If the input is optically isolated there should be no problem.

__________________
Charlie don't surf.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4
In reply to #2

Re: Instrument cable for digital signal

05/03/2010 3:34 AM

GA.
The important thing is to ensure there is some protection on the input to the instrument to stop any nasty pick up or vampires. A couple of back to back zenners, a varistor, a load resistor, 0.1uF capacitor, clove of garlic ...the usual.
It's cheaper than using expensive screened cable.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Instrument Cable for Digital Signal

05/04/2010 3:33 AM

Follow the Cabling Standards in use at the installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#6

Re: Instrument Cable for Digital Signal

05/04/2010 9:01 AM

Is there a length of run limitation with 24V? question address openingly

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#7
In reply to #6

Re: Instrument Cable for Digital Signal

05/04/2010 9:35 AM

Not really if the supply and termination circuit are suitable.
You only need to drive say 10mA through it to give plenty of noise immunity, and if you don't mind dropping the odd volt or so, which is no prob if you are interfacing to 5v logic you have tons of spare thrunge to mess about with.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#9
In reply to #7

Re: Instrument Cable for Digital Signal

05/04/2010 3:17 PM

Thanks

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#10
In reply to #9

Re: Instrument Cable for Digital Signal

05/04/2010 4:23 PM

Hmm, I spose you've gotta factor in my idea of scale. Being a cat I'm somewhat smaller, and usually work in an environment where 75feet would be considered quite a long way. Some of you big guys work in terms of maybe quarter of a mile I guess...
So take my opinion with some caution.
Del (I only an ikkle wikkle cat)

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#11
In reply to #10

Re: Instrument Cable for Digital Signal

05/04/2010 4:56 PM

ha, I was thinking about that, some of the process machines I design, the EE suggest we use 110V signals, due to possible signal degradation.

He was the EE, and I went along with it.

ikkle wikkle huh?....ya me too

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 5)
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#8

Re: Instrument Cable for Digital Signal

05/04/2010 11:59 AM

I routinely use 24 AWG Cat. 3 twisted pair telephone wire for this type of discrete signal from remote sites; it works well up to ~10 miles (16 km). We've been doing this since the late 1970's to provide alarm & indication from remote electrical substations. The only problems encountered have been due to lightning strikes on the aerial cable. At generation facilities, where the distance is relatively short (<500m), I use 16 AWG twisted shielded pair due to the higher electromagnetic fields around operating machinery.

As others have indicated, one side of the 24V should be solidly grounded at the source; the optical isolation and dropping resistor options mentioned by Stevem also work well.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

phoenix911 (3); pwr2thepeople (1); PWSlack (1); rakesh_semwal (1); stevem (1); Tornado (1); user-deleted-1105 (3)