Close Accuracy Batch Fill Method

06/13/2010 9:56 PM

What is the best way to batch fill a tank, when the customer insists we use a flow meter and a control valve (open/close - not modulated) to do the task? All sanitary, 20 Ra finish, stainless steel, etc., which limits the flow meter manufacturers immediately. The desired fill point is under 100L (volume desired depends on the batch components) and the accuracy is expected to be to +/- 0.01L. I have already said this isn't going to happen, but we need to get as close to this as possible. Oh, and the fluid is DI water, so magnetic based flow meters are definitely out.

I have some ideas - I assume a good coriolis flow meter to begin with. I have looked at some various totalizers, and expect to open/close the valve with a good solenoid from a discrete output from the totalizer. This will create over fills due to the time for the valve to close, but with a constant flow, I think I should be able to tweak this to correct for the finite closing time. Any better ideas?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Close Accuracy Batch Fill Method

06/13/2010 10:39 PM

I think coriolis and ultrasonic flowmeters will be unable by far to attain this accuracy, and I even wonder about various positive displacement types. Instead, I would look at a positive displacement pump driven by a stepper motor. Once this is calibrated, accurate volumes can be achieved by operating the motor a specific number of steps.

A paint mixing station might almost be an off-the-shelf way to do this.

And, no, the customer is not always right.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2

Re: Close Accuracy Batch Fill Method

06/13/2010 10:55 PM

Have you considered weighing the vessel with load cells, rather than flow metering?

If you have to CIP the process piping, the metering part doesn't get heat/acid/caustic treated.

Weighing has the resolution to provide you those accuracies. Typically you need a main flow to some high percentage (like 97% of batch size) and a 'dribble' line at a fraction of the main flow that runs until the batch size is reached. And weighing can confirm solids batching (salts, powders) at low levels, too.

I've used Sartorius industrial load cells because of their incredibly fast response and their ability to hold up to wash down. Due to some unique property, they don't need or use the signal filtering that other load cells do. Filtering stretches out or averages out the response from the load cells, which is not what you want when you're approaching the batch limit value. Fast response is needed for batching control.

On a coriolis meter batchers, we've had to experiment with shut off values to get the right one for any given flow rate. It isn't adjusting the value that's time consuming, it's running the batch and then checking it, then running it again, until we hit the right value.

I know Hoffer has a sanitary turbine meter. I'm not sure whether vortex meters meter sanitary requirements or whether they're just available with triclamp fittings. You might get by with vortex meter because of the requirement for flow/no flow, where your system would never modulate down into the the low flow cutoff level inherent to vortex.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#4
In reply to #2

Re: Close Accuracy Batch Fill Method

06/14/2010 7:56 AM

Yeah - load cells or a scale, as the tank is on casters - that was my first choice - the customer does not want them.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: Close Accuracy Batch Fill Method

06/15/2010 3:50 AM

Sooner or later the customer is going to have to accept something!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#11
In reply to #7

Re: Close Accuracy Batch Fill Method

06/15/2010 8:09 AM

Yes, and on the last project we had a simple turbine flow meter and a ball valve on top of the tank for flow start/stop. Accuracy was at best ±1L. Price drove us to this simple arrangement, as they kept asking for lower costs each bid we submitted. They are using this system now, but the complaints over filling repeatibility rang out for 3 months. This time, they have asked for the flow meter and valve again, but have included the ±0.01L specification. As I said, I immediately asked about load cells and got an emphatic "NO". This is what they want - flow meter and valve. I am trying to optimize this combination as best as possible. Cost seems to have become a non-issue.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Anonymous Poster
#3

Re: Close Accuracy Batch Fill Method

06/14/2010 7:08 AM

Put the flowmeter & valve at the discharge point use quick close valve, say irish valve or batterfly valve or better.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#5

Re: Close Accuracy Batch Fill Method

06/14/2010 2:58 PM

No load cells? I don't blame them. I was "no load cells", too, until I discovered Sartorius.

It isn't clear how they do it, but they do not drift, period. No drift.

No summing box.

There is no iterative tweaking for calibration, whether at startup or over time. The load cells come precalibrated, each and every one at exactly the same output 2.000mV/V and they stay that way, no drift.

Startup takes about 10 minutes to get the tagged data from each cell entered. Done.

The response time is phenomenal. Lay a clip board on top of the vessel and the response is an instantaneous step change. Or a pencil.

You almost have to see it to believe it, if you've lived in the world of drifting, averaged-over-time, need-to-be tweaked-and-tweaked-and-tweaked bonded load cells. German know how, I guess.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#6
In reply to #5

Re: Close Accuracy Batch Fill Method

06/14/2010 3:28 PM

I'll keep that in mind - I often wondered how the load cell systems were ever used in the "real world" (I design/build controls for process skids - not use them) when the darn things drift so much. We have customers get concerned about the readout on a temperature transmitter being 0.1 off from the PLC at times, as they drift around a point a couple hundredth above the reading. But, they have no problem accepting the drifty load cell readout. (????)

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Close Accuracy Batch Fill Method

06/15/2010 3:51 AM

1 part in 104. OK. At what temperature?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10
In reply to #8

Re: Close Accuracy Batch Fill Method

06/15/2010 8:02 AM

60°C

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Anonymous Poster
#9

Re: Close Accuracy Batch Fill Method

06/15/2010 6:56 AM

Use a positive displacement pump and limit no of strokes etc v acurrate

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#12

Re: Close Accuracy Batch Fill Method

06/15/2010 4:32 PM

Alfa Laval (formily Triclover before that G&H) has a sanitary flow meter a PD340 Very expensive. Need a PLV. Shut-off calve would be fine. Would need a PLC, oops, I see no mag meter

I see its a low volume what is the flow rate, did you have you considered load cells

p911

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#13
In reply to #12

Re: Close Accuracy Batch Fill Method

06/15/2010 5:07 PM

Flow rate will be as low as I can convince them to keep it in 1/2" 0.040" wall tubing. Slower is better for control. I hope they can allow a 1/2 hour to fill, but suspect we will get full flow from a 1/2" tube at 60 psi. (haven't calculated that yet) I doubt they will consider any pressure dropping or flow restricting devices before the tank. More later after a phone meeting tomorrow.

See my reply #11 for the load cells.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Carl_E (2); phoenix911 (1); Phys (5); PWSlack (2); Tornado (1)

Previous in Forum: Reverse Flow in Control Valves   Next in Forum: Process control

Advertisement