Temperature Indicator -urgent

09/11/2010 4:08 AM

We received a temperature indicator(TI) with thermowell. Where inserton length is u-260mm and thermometer stem(dia-8mm) length is 350mm.Total thermowell length from the connection to bottom tip( extention+flange+insertion length) is -325mm

thermometer is bimetallic type. process fluid is -HC gas

Problem: 25 mm of the thermometer stem is exposed to the atmosphere.(means-20mm cannot go inside of the thermowell as stem length is 25mm more).Is it acceptable? I think- atmospheric temperature will interfere with process temperaure and ultimately temperature measured by TI will be process temp+ atmospheric temp

Pls tell me am i right?

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Temperature Indicator -urgent

09/11/2010 6:39 AM

What does the procurement specification say?

Or, what does TI say?

I say you are not right. Does the probe take two readings and add them together?

Reply
Anonymous Poster
#2
In reply to #1

Re: Temperature Indicator -urgent

09/11/2010 9:07 AM

Procurement spec says that TI is measuring process temperature ..not atmospheric temperature. My question is If some portion of the stem(20mm) exposed to the atmosphere ..does this portion effect the temperature value?

tell me how can i add picture here? i would like 2 attach photo for clear view.

Reply
Anonymous Poster
#3
In reply to #2

Re: Temperature Indicator -urgent

09/11/2010 10:26 AM

Hi, Guest

Send your instrument to the machinish to add socket to cover the 20mm exposed to atmospher.

Regard's

newbie

Reply
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Temperature Indicator -urgent

09/11/2010 12:25 PM

The sensing portion of the probe is near the tip, so the exposed portions outside the pipe/tank will have very little if any effect on the reading. There should be no problem.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 3)
Power-User

Join Date: Aug 2010
Posts: 108
#10
In reply to #4

Re: Temperature Indicator -urgent

09/12/2010 2:37 AM

GA for pointing out that the sensinsg element is at the tip.

The TI will not be mechanically coupled to the thermowell (as was pointed out by a Irs)and therefore it is likely (depending on the application) that the TI will become loose and measurements will be compromised. There is only so much heat transfer paste that can go into a thermowell and this alone may not be sufficient to maintain the mechanical stability.

I saw your suggestion about the compression fitting and this is not a bad idea but perhaps for the the long term succes of this application the Op should just simply purchase the correct TI.

__________________
"New and stirring things are belittled because if they are not belittled, the humiliating question arises, 'Why then are you not taking part in them?' " - H. G. Wells
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Temperature Indicator -urgent

09/11/2010 1:42 PM

While the air space will permit heat to be transferred by convection a little easier, the temperature reading will always be of the bi-metallic sensor. The small amount of heat lost to heating the air that is permitted to leave the cavity will likely not be a significant loss. Now if there is no seal at all you might lose a considerable amount of you HC gas.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: Temperature Indicator -urgent

09/11/2010 3:35 PM

I agree with those who explain that the measurement is made in the 50mm near the tip of the bimet, so that the influence of 25mm exposed stem is not signficant.

But as I understand it, it seems that there is no means of securing the bimet in the thermowell, because the threaded process connection does not screw into the internal threads on the thermowell:

How is the bimet secured from falling out of the thermowell?

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Temperature Indicator -urgent

09/11/2010 6:16 PM

You might be able to screw a compression fitting into the female thermowell threads.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#8
In reply to #7

Re: Temperature Indicator -urgent

09/11/2010 11:19 PM

sir kindly give me a clear picture ...what should i do.....

should i fix a compression fittings to cover the expose part or else?

or any other method is there

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: Temperature Indicator -urgent

09/12/2010 12:23 AM

A compression fitting would cover almost all of the exposed 20mm of the probe stem, which already doesn't really matter.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#11
In reply to #9

Re: Temperature Indicator -urgent

09/12/2010 3:45 AM

is it really true that of 50mm from bimet probe tip contains the sensing part?

upper portion of the probe doesnt contain sensing part.

i didnt find this in the vendor catalog

model :Baumer TBI130/264.160 RANGE : (-) 50 TO 400 DEG F

Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#15
In reply to #11

Re: Temperature Indicator -urgent

09/12/2010 2:27 PM

All bimets have similar construction. The helical or spiral bimetallic element is anchored at the tip. The length of the bimetallic element depends on range and model.

The article's author at the link provided below cites a study that shows that a bimet's element averages the temperature gradient across the element.

http://www.hi-tm.com/Documents2001/hamburger-temp.pdf

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Temperature Indicator -urgent

09/12/2010 7:21 AM

OK, so put lagging round it, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#13

Re: Temperature Indicator -urgent

09/12/2010 8:08 AM

Conventional wisdom is that thermowell length should be at least 10 times the sensor diameter. Your system exceeds this criteria which means you should be okay. If you want to test this conclusion, measure the temperature at different insertion depths and plot the data. If the measured temperature doesn't change over the last 10 mm of insertion, the length is okay.

Reply
Anonymous Poster
#14
In reply to #13

Re: Temperature Indicator -urgent

09/12/2010 11:14 AM

thanks to all those who spent time for me and replyed .

i will verify it by measuring temp.

I am in the process industry for last 10 years and we are purchasing usually from WIKA INSTRUMENTS.i never found such cases.thats why i asked to alll.

thanks to all again

Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#16

Re: Temperature Indicator -urgent

09/13/2010 8:14 AM

Happens all the time. We manage to get at least two sensors too long for the thermowell that was installed in a new tank every year. Then one has the following choices

1. if the well and the sensor are NPT a nipple or a coupling can be added - whatever works.

2. if not, perhaps an extension can be welded to the thermowell

3. none of the above work - order a proper length sensor

And, always point fingers at someone as the culprit for not correlating the two dimensions correctly, unless it was you, then have a good excuse ready.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#17

Re: Temperature Indicator -urgent

09/14/2010 9:00 AM

Most processes use one thermocouple for process control and one for over temperature alarms. If your system is set up this way simply compare the two readings. If the readings are both the same or close you should be OK.

As was mentioned earlier in this post the sensing is done at the tip of the thermocouple and if the installation is vertical the sensing tip will be in physical contact with the bottom of the thermowell if it is unsupported. This may cause process overshoot if the system is tuned with the thermocouple not in contact with the thermowell. If the installation is horizontal or the gland nut can secure the thermocouple off of the bottom you should be OK.

The only other thing to consider is mechanical damage. If the thermocouple sticks out of the thermowell too far it may get damaged by objects or persons moving around in the area.

It's best to use the proper length thermocouple if possible. We have in the past been able to shorten ours but they may not be the same design as yours.

Good Luck

__________________
Knowledge makes what was impossible, seem easy.
Reply
Reply to Forum Thread 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AGuest (1); Anonymous Poster (5); Elroy (1); Iris (2); lyn (1); Phys (1); PWSlack (1); redfred (1); Tornado (3); welderman (1)