Air Volume Tank

09/17/2011 7:27 AM

WE ARE FACING A PROBLEM WITH ONE OF OUR CONTROL VALVE ITS OPENING TO SLOWLY AND WE INSTALLED VOLUME BOOSTER RELAY ON THIS VALVE STILL ITS TOO LATE TO OPEN, WE ARE HAVING A LOGIC SAYS THE VALVE SHOULD OPEN IN 2 SECS , SO PLEASE HELP ME OUT WITH THIS PROBLEM , WILL THE AIR VOLUME TANK WILL HELP TO OPEN THE VALVE FASTER, THE GAUGE ON THE VOLUME BOOSTER SHOW PRESSURE DROPS WHEN THE VALVE TEND TO OPEN

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#1

Re: aIR VOLUME TANK

09/17/2011 7:48 AM

Do this first:

1. Check to see that the ALL CAPS button on our keyboard is unlocked. If so, you should get lower case font instead of UPPER CASE font when you type.

2. Once you are sure that ALL CAPS is unlocked, pry off the Caps Lock button on your keyboard.

3. Throw away the Caps Lock button.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply Good Answer (Score 2)
Active Contributor
Engineering Fields - Instrumentation Engineering - Global Technical Village Engineering Fields - Control Engineering - Control Automation Engineering Fields - Biomedical Engineering - Engineering Philianthrophy Engineering Fields - Electromechanical Engineering - Electromechanical Tacho Engineering Fields - Engineering Physics - Physics change you life Engineering Fields - Energy Engineering - Save earth Engineering Fields - Environmental Engineering - Human Recycle Engineering Fields - Mechanical Engineering - We move earth Engineering Fields - Nanoengineering - Minute study Engineering Fields - Systems Engineering - Systems in Place

Join Date: Oct 2007
Location: HYDERABAD, INDIA
Posts: 21
Good Answers: 1
#2

Re: aIR VOLUME TANK

09/17/2011 8:30 AM

Plz do mention the type of valve:

Solenoid operated Ball Valve

Diaphragm Operated Ball Valve

Pneumatic Actuated Globe Valve etc.

Now check for the valve response time as the electronics response time will always be in milliseconds. It's only the electromechanical devices line valves which respond little slower for many reasons which include design consideration to avoid chatter.

If nothing helps you then pls contact valve supplier to suggest a better option. One thing you mentioned is that "OUR CONTROL VALVE", so can I presume it to be linearized valve with positioner????

__________________
One who is afraid to ask is ashamed to learn
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: aIR VOLUME TANK

09/17/2011 9:35 AM

In today's economy there are many pneumatic engineers and technicians looking for work. You or your boss should hire one of them to your company. This could just be a contracted repair job, consultancy or maybe even a new position in your firm. They should be able to identify all of the critical parts in your pneumatic system by inspection. They can then determine if your valve is getting the correct voltages and/or pneumatic pressure to operate in a timely manner. If these controlling energies are inadequate they can then trace back to identify why insufficient controlling signals are happening. If the controlling energies are adequate they will then investigate why the valve is operating too slowly.

This is how a qualified person solves any technical problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: aIR VOLUME TANK

09/17/2011 1:25 PM

Make sure that the pneumatic control tubing is no smaller than the port sizes. If there is a pressure regulator, you may be able to set it higher, so long as you don't exceed the actuator rating.

How large is the valve and what type? What type of actuator?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#5

Re: aIR VOLUME TANK

09/17/2011 1:55 PM

Imartin,

Is this control valve used by a anti-surge compressor system?

is there any positioner installed in the control valve?

Can you show us some drawing with the pneumatic scheme?

Regards

JP

__________________
Instruments-guy-SAV
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#6

Re: aIR VOLUME TANK

09/17/2011 5:24 PM

Assuming that the valve actuator is being controlled by the output of a PID loop, check the tuning parameters to ensure you have the fastest response to a change in the process variable.

There is also the issue of "stiction"; resistance of the valve's plunger through the valve packing. Did the volume booster relay help with the response time? If so, a stiction problem it may be. If such is the case, physically inspect the valve you should.

<(o.o)>

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#7

Re: aIR VOLUME TANK

09/18/2011 10:20 AM

If you could send a photograph of this valve with all the tubing shown, it might help us to diagnose your problem. A booster tank should help any air-to-open valve open faster, but all the air pathways (this includes boosters and other in-line devices as well as tubes) flow freely enough for your application.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Air Volume Tank

09/19/2011 4:19 AM

SHHHHHHHHHHHHHH! No-one wants to disturb Stinky Pete.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#9

Re: Air Volume Tank

09/19/2011 8:20 AM

It appears to be pneumatic control valve. Check whether you use dry air of at least -30 degC due point. Check air pressure, whether it can be improved by changing to higher size supply piping. Check for air leaks at all connections.

What type of actuator it is? Cylinder piston, diaphragm or rack & pinion? Check whether it is designed for available air pressure for the size of valve. Check whether differential pressure across the valve is higher than design.

Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Instruments-guy-SAV (1); Jaya Krishna (1); Mikerho (1); pritam (1); PWSlack (1); redfred (1); tonykuphaldt (1); Tornado (1); Usbport (1)

Previous in Forum: How to connect Delta DVP-12SC Type plc with Bar code scanner?   Next in Forum: Taping of Pressure Transmitter in Steam Line