Loss Due to Low Grid Frequency

12/08/2012 12:27 PM

How to calculate the losses occurred in 250 kw floor mill due to low grid frequency?

Its motor rated voltage is 415 V, frequency - 50 Hz, kw - 250.

We noticed slight reduction in power consumption at lower frequency say at 49.5 hz. What is the benefit in terms of electrical energy saved?

If the rated output of mill is 2 tons/hr, how to calculate the losses per hr (in terms of tons/hr)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Loss due to low grid frequency

12/08/2012 12:32 PM

We've already flogged this horse once, why go into it again.

There are 10,000 web site that will tell you how to do this and EVEN DO IT FOR YOU.

Go find one and use it.

Run the motor at any speed you like. You seem bound to do this anyway, so go ahead.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Loss due to low grid frequency

12/08/2012 12:41 PM

You've noticed a slight reduction in power consumption. Did you compare this to the amount of work performed or any other plausible mitigating factor?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Loss due to low grid frequency

12/08/2012 12:49 PM

2 - 2(49.5/50)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Loss due to low grid frequency

12/08/2012 12:51 PM

If your company has reached the point it has to start turning down the electrical systems operating frequency to try and save money the odds are its too late anyway.

So is this experiment an effort to save money or for other things?

Register to Reply
4
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Loss due to low grid frequency

12/08/2012 12:55 PM

What we have here, is failure to communicate.

Logic won't work.

Reason won't work.

Careful explanation of the problems to be encountered won't work.

My dear departed mother had a saying that I think fits here. "Just let 'em stew in their own juices".

Someday OP may be back with the question, "my motor insulation is failing, causing us to spend money that we don't want to spend to replace this motor. What could be the cause?"

Register to Reply Good Answer (Score 4)
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#6

Re: Loss due to low grid frequency

12/08/2012 3:17 PM

do power plants save money by running at a lower ower frequency? it seems to be a trend. is there any affect to the consumer?

Register to Reply
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#7
In reply to #6

Re: Loss due to low grid frequency

12/08/2012 3:25 PM

sorry tcmtech for repeating your post.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8

Re: Loss Due to Low Grid Frequency

12/09/2012 6:58 AM

What is the drawback in cashflow and operating profit in terms of running the motor at 1% lower speed, Bro?

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15
In reply to #8

Re: Loss Due to Low Grid Frequency

12/10/2012 7:06 AM

You clock runs slower so you spend more time at work that you need to.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#9

Re: Loss Due to Low Grid Frequency

12/09/2012 9:16 AM

In theory if you drop the frequency by 1%, you drop the motor speed by 1%, and the output by 1%, but only in a mill that operates at 100% efficiency. As no mill can operate at 100% the calculations become a little more complicated. The mill stones will be optimised for grinding most efficiently at a certain speed. If your existing motor speed matches this optimum then you will experience a reduction in quality not throughput. You have not changed the in-feed rate to the stones so the same quantity will be milled, it just won't be milled as finely. If the 50Hz motor speed and stone efficiency are not a prefect match then you stand an equal chance of improving the flour quality as you do of reducing the flour quality.

I am amazed that any multi generator grid system could vary in frequency for any length of time by as much as 0.5Hz. All the generators a synchronised and any generator that comes onto line slightly out of sync will be motored into the common frequency. It is the easiest part of bulk generating AC electricity to get right. Voltage is allowed to fluctuate by up to 10% but frequency is normally held to +/-0.2Hz short term. It will also spend as much time over frequency as under frequency so it balances out over a longer period. All clocks and a big chink of industry depend on this.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Loss Due to Low Grid Frequency

12/09/2012 12:42 PM

Dear Mr.satendrakumart

It is true in the case of centrifugal pumps, centrifugal fans for industrial applications like application in boilers. The out put speed will be 49.5/50 = 0.99 i.e., 99% and speed reduction is 1%.

For the Pump or Fans, the capacity will vary the as the speed, Pressure or head will vary as the square of the speed and the power demand will vary as the cube of the speed.

Accordingly for a Frequency of 49.5 c/s, the capacity will be (0.99)C, the Head or Pressure will vary as (0.99)x(0.99) P or H = 0.9801 or 98.01% and the Power drawn will be (0.99)x(0.99)x(0.99) P = 0.9702 or 97.02% thus a fall in power demand by 2.9701%. Here the synchronous speed is considered.

For 2 tons/hr rated output, the fall will be 0.596 Tonne/Hr., if the Frequency falls to 49.5 from 50.

Thanks,

DHAYANANDHAN.S

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11
In reply to #10

Re: Loss Due to Low Grid Frequency

12/09/2012 9:37 PM

It seems odd that a 1% speed reduction would cause a nearly 25% throughput drop. Perhaps you meant 0.0596.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#12

Re: Loss Due to Low Grid Frequency

12/09/2012 11:28 PM

If I repeat the working of Dhayanandhan sir, for 1% reduction in frequency

Fall in speed =1-0.99 = 1%

Fall in head (through put) = 1-0.98=2% ?

Fall in power consumption = 1-0.97=3% ?

so the production loss is 2% ie fall in mill out put is 0.04 ton?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: Loss Due to Low Grid Frequency

12/10/2012 12:46 AM

Those figures are for a centrifugal pump, rather than for a flour mill.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#14
In reply to #13

Re: Loss Due to Low Grid Frequency

12/10/2012 6:47 AM

Is it a flour or a floor mill? I still would like to know how the slight reduction in power consumption was measured in comparing one power grid frequency to another.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: Loss Due to Low Grid Frequency

12/10/2012 10:21 AM

It sounds like good news. Why stop there, though? Why not drop the frequency to, oh, say 20Hz?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#17
In reply to #16

Re: Loss Due to Low Grid Frequency

12/10/2012 10:29 AM

Do I here 15Hz, 15,15,15. Now I'm at 15. Do I hear 10,10,10,10 and I have a 10! Now I'm at 5. Can I get 0,0,0,0,0. Sold to the lowest bidder at 0 Hz. The expected power savings will be 100% since no work will get done using induction motors.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#18

Re: Loss Due to Low Grid Frequency

12/11/2012 4:32 AM

How to calculate the energy lost in the form of heat, due to low frequency in inductive loads?

And what about V/F ratio and its effect?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#19
In reply to #18

Re: Loss Due to Low Grid Frequency

12/11/2012 10:07 AM

You calculate the loss the same way one calculates any real energy loss. Energy into the system minus energy applied to the load. The difference is frequently mislabeled as the energy lost. Energy is never lost, it can be unusable, the price for doing a task, delivered to the intended load but it is never lost.

All of that energy difference will not be realized in the form of heat depending on the type of inductive load you are driving. For an electric motor some of the non-thermal diversions will be moving coolant, the rotor assembly and free space radiation. The root of the thermal dissipations will be resistive losses in stator and rotor windings, bearing friction, magnetic core losses of eddy current and hysteresis.

To accurately discuss these effects requires more education than you've demonstrated here so far. Can you tell me how many watts a solenoid with 100 mH of inductance and 4 Ω of winding resistance produce if driven by a 120 VAC (RMS) 60 Hz source? Ignore hookup wire resistance. If you can, then repeat this exercise for 59.4 Hz.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Crabtree (1); dhayanandhan (1); durtieduck (2); jhhassociates (1); lyn (2); PWSlack (1); RAMConsult (1); redfred (4); satendrakumart (2); tcmtech (1); TonyS (1); Tornado (2)

Previous in Forum: Slow Powder Conveying   Next in Forum: Grading Ring for Insulators

Advertisement