Federal Pacific Electric Co. Circuit Breakers

01/06/2013 1:39 PM

Breaker panel in my 1982 house has these breakers, 4 with GFI feature. One of the latter no longer functions as GFI, needs to be replaced, but are no longer available. I understand company went out of business because of some shaky issues with their UL rating. Does anyone know of a replacement brand? Are there any other safety issues with them other than the GFI aspect? Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Federal Pacific Electric Co. circuit breakers

01/06/2013 1:59 PM

Blurb...

"

Federal Pacific Electric PanelsPotentially Could Fail to Provide Proper Safety and Protection for Homes

Federal Pacific Electric Company (FPE) was one of the most common manufacturers of circuit breaker panels in North America from the 1950s to the 1980s. Millions of their panels were installed in homes across the country. Yet, as the years passed, electricians and home inspectors often found Federal Pacific Electric panels failed to provide proper protection to homeowners and their families. Experts now say that FPE panels can appear to work fine for years, but after one overcurrent or short circuit, they can overheat and become fire hazards.

In a class action lawsuit, a New Jersey State Court ruled that the Federal Pacific Electric (FPE) Company "violated the Consumer Fraud Act because FPE knowingly and purposefully distributed circuit breakers which were not tested to meet UL standards…" (To see the Class Action Settlement Notice issued for New Jersey Residents, click here.) An expert who investigated the potential hazards of Federal Pacific Electric panels stated under UL 489 test conditions, that FPE panels fail to trip at a much higher rate than standard panels.

When a breaker fails to trip, an extreme amount of power from the outside electrical supply surges into a home's panel and circuits. Once that happens, it cannot be stopped or shut off manually. Electricity will burn until it runs out of fuel or the wires melt. The panel could overheat and catch fire, causing serious harm to a home and its occupants. Many Federal Pacific Electric panels and breakers can operate properly for years. But if and when they do malfunction, a disaster could occur."

http://www.ismypanelsafe.com/fpe.aspx

Source for refurbished FPE breakers...

http://www.baybreakers.com/catalog/Federal-Pacific-FPE.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Federal Pacific Electric Co. circuit breakers

01/06/2013 2:09 PM

Be careful that any other brand of breaker is made to the same dimensional standards and is approved for interchangeabillity.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Federal Pacific Electric Co. circuit breakers

01/06/2013 3:50 PM

One can purchase a 17th-Edition-compliant split-load distribution box for less than £100GBP these days. Replacing the distribution box potentially falls under Part-P of the Building Regulations, so, get it tested and certified post-installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#4

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 6:14 PM

East coast of central Florida has lots of FPE breakers. My local ACE has breakers that are 100% compatible (except for the dangerous part). I don't recall who makes them but if I recall correctly the company bought the FPE rights and can be traced. The next time I am in ACE I'll try to remember to look. If I remember then I'll add a post to this thread. But, with a little more searching you will probably find them first.

I think SolarEagle indicated that yes, there are safety issues beyond GFI. My research indicated that when exposed to a small overcurrent they can weld shut and become a significant fire hazard.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #4

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 6:26 PM

The problem here is that it's not just the breakers that are defective but the panels themselves....I recommend total panel changeout asap.....

Here's a link to more info....

http://www.prestigeelectric.net/downloads/hazardous-fpe-circuit-breakers-and-panels.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 7:04 PM

Very sensible, understandable, and well written article.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#5

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 6:23 PM

Home Depot's web site lists FPE breakers but since they haven't been in business for many years I'm sure someone else is making them.

The link http://wiki.answers.com/Q/What_circuit_breaker_will_interchange_with_federal_pacific is a little bit helpful.

I don't recall for sure but I think that Ace sells Connecticut Electric breakers that work well in the FPE Stab Lok panels.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#8

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 9:36 PM

Hire someone to come and up-grade to new style UL approved box. I would not take the chance, too many good people and homes have been lost to these units.

I changed one last year that had let the smoke out of one breaker and as luck would have did not start a fire. But it sure toasted the box. Hence they called me to look at it. House also had good old aluminum wire from the 70's. I found several areas of concern here as well. Pulled all new number 12 copper circuits as well. Now meets current code and is safe.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#9

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 11:24 PM

25 years ago I was doing a lot of electrical work and needed a FPE circuit breaker to help a friend out who had a bad one. At that time a replacement one, one that had sat on a shelf at an electrical supplier's warehouse, was going for $40. Google "Federal Pacific circuit breakers supplier" and there are still some outfits which have them, but of questionable quality. The cost of a GFI, if you could find one, will be much higher

My solution at the time and several times after that was that it was about the same cost to buy a "breaker box kit" which includes the panel and several breakers. This cost plus the cost of any future additional breakers makes this the cheaper solution.

I was once involved with the sale of a house with a FPE panel in it. The buyer made its replacement with a GE or Sq. D a contingency of the sale. I used the old box minus the "guts" with a piece of steel for a cover as a junction box and mounted a Sq D panel next to it with nipples between the two boxes. Was done in 2 hours for box with 12 breakers.

Replace the whole setup and get rid of potential headaches now and in the future. Its also cheaper in the long run.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Power-User

Join Date: Jul 2010
Location: Virginia, USA
Posts: 227
Good Answers: 4
#10

Re: Federal Pacific Electric Co. Circuit Breakers

01/06/2013 11:52 PM

There were at one time, companies that would rebuild FPE breakers, but I didn't recommend it then and now that the system is even older, I dedfinitely don't recommend it. I've seen and replace FPE equipment where a 15 Amp breaker was carrying loads of 25 amps or more without dropping out. THEY'RE DANGEROUS!! Change it out ASAP.

__________________
Robert A. Heinlein (1907-1988) "There is no worse tyranny than to force a man to pay for what he does not want merely because you think it would be good for him."
Register to Reply
4
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#11

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 12:40 AM

FPE - Fire Preceding Explosion. Failure Prone Electrical.

Step 1) Fix, Step 2) Pray, Step 3) Extinguisher

You can get replacements for these at www.breakerbroker.com
But... please don't.

My unpleasant experiences:

1) My mom is a real estate broker in the Houston area. From 1982 to 2012 she brokered one or both sides of over 1800 home sales. Of those, approximately 15% (270 homes) had FPE panels. The last time one of the panels passed inspection by a licensed home inspector or licensed electrician was in 1987. So, for the last 24 years not one FPE panel has passed = 100% failed and 100% had visible defects - melted plastic, damaged buss bars, breakers that would not hold onto the buss bar because of weak tension, breakers that would not trip when tested, and many more.

2) I have watched a licensed electrician replace a sizzling, sparking FPE breaker, and gone back to the same house the SAME DAY to replace the entire panel. The new breaker worked fine, but jiggling the new one into place caused the adjacent breaker to fry and ruin the buss bars.

3) The subdivision section next to mine is 627 homes. About half were built with Zinsco or ITE and about half with FPE. We are down to 8 and counting. There were 9 until last summer when the smoke was released at #9 - electrical fire in the kitchen. Was it the FPE panel? Was it the wiring? Was it the oven? The FPE breaker had been replaced, twice. That's not conclusive, but the insurance report stated the (proper size 40 amp) breaker failed to protect the (proper size #8) wiring and the wiring overheated and started the fire.

4) In short (pun intended) there's no saving grace to these panels. Even if a homeowner can find the ACE hardware replacements, the panel will fail inspection at time to sell. It's too risky, and simply by noting the presence of the aftermarket breakers, a home inspector may and should cite the panel for "obvious modifications not approved by the manufacturer".

5) The individual replacement FPE breakers can cost more than a new panel. When an entire panel, with a good assortment of breakers included, can be purchased for less than $200... it's not worth the risk or the trouble to keep the FPE panel.

__________________
txmedic3338
Register to Reply Good Answer (Score 4)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 9:37 AM

The old FPE went belly up after losing its UL listing because investigations into fires uncovered the fact that FPE was falsifying their test reports. The RIGHTS to the brand name were bought and sold by several companies after that because of the potential for retrofit of the large installed base; FPE was the low bid brand on a LOT of public housing projects in the 60s and 70s. Most of the buyers of the name rights were reputable but the name bounced around for years because most people who used it discovered that the stink would not go away with time. The rights to use the name now belong to some obscure guy in the east coast, who just takes a licensing fee from several other mfrs to produce retrofit breakers, mostly in China, Connecticut Electric being one of those. So the relationship is in name only and the market is strictly for retrofit to people who can't afford to do it right and junk the old panels. But think about it; questionable original product design, questionable quality of the panel it goes into, now made in China by people with no skin in the game and immunity from prosecution. No thank you.

Side issue: someone mentioned "rebuilding" FPE breakers. FPE made all sorts of electrical equipment, not just residential panels. The breakers that can be rebuilt are the industrial molded case breakers, NOT the residential ones, called "Stablok". If anyone sells a residential breaker, any brand, that says it is "rebuilt", you should run away, fast. Residential circuit breakers are NOT designed to be rebuilt in any way shape or form. All these people do is clean them and run a rudimentary test (sometimes).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Member

Join Date: Sep 2008
Posts: 7
#13

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 10:19 AM

If you look in a Grainger catalog under Electrical Distribution there is a page for Replacement Circuit Breakers for Obsolete Load Centers. About half the listings are for FPE replacements. They will sell you a new breaker, UL standard (made in China by Connecticut Electric, labeled as American FPE). With that said, I have to agree with some of the other comments about safety issues. If it was my home, I would replace the entire load center with a Square D QO load center.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 11:23 AM

That is one one of the great points of living in Germany, all these bits have to follow DIN standards, which means all companies must make to a standard, so replacing a breaker (or switch or socket or whatever) with one from another company is really easy....they simply just fit......

Deutches Institut für Normung = German Institute for Standards....

(Marking as off topic)

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Participant

Join Date: Jan 2013
Posts: 3
#15

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 11:25 AM

Replacement Breakers are avaiable at Home Depot I have bought them

Register to Reply
Associate

Join Date: Aug 2007
Location: Cincinnati, Ohio
Posts: 36
Good Answers: 1
#16

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 3:13 PM

As stated before, I wouldn't walk but RUN from a 30 year old Federal Pacific box. My parents had one and after the lights went out and the breaker failed to trip I was on the phone with my electrician to go change out the service drop, meter base, and panel.

It was scary to tap on the breaker and see the lights flicker and hear the buzz of a thousand angry hornets coming from a 60 amp breaker.

The cost of a new panel is far cheaper than the cost to rebuild the home if it catches fire and burns down! Not to mention the safety of the family.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#17

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 4:57 PM

Friends,

I learned something here that I didn't know. The documentation has sufficient references to be something I would trust. However one portion is not explored: FPE stab-lok breakers were off the market for many months when they lost their U/L listing, but they eventually got it back and attempted to regain their lost market share. Their new breakers had a different colored (red or pink, if I recall correctly) U/L label to give easy comparison to the old ones. In the independent tests was there any distinguishment made between the "new" and the "old" breakers? That little piece of information may be good to have.

--John M.

Register to Reply
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#19
In reply to #17

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 5:51 PM

There were several different color schemes and labels.

Follow this link to learn a lot more

__________________
txmedic3338
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#18

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 4:59 PM

While you are replacing the panel it is a good idea to put a thin coating of "Nolox" or other brand aluminum anti-oxidizing compound on the buss bars before installing the breakers. Most of the buss bars in panels are made of aluminum and will oxidize after time goes by. No-lox is the same compound that is required if splicing aluminum to copper wire. The aluminum forms an aluminum oxide coating which is less conductive. As the coating forms the resistance increases. With resistance comes heat.

When I moved into my last house I noticed that the lights and TV would flicker sometimes when the A/C or other heavy load would come on. Several weeks later I was installing a 240v 2 pole outlet below my panel in my garage for using a welder. As I was working with the panel cover off I noticed an intermittent humming from the panel. Further investigation revealed a strange orange color behind the main breaker which would appear when it hummed. Investigation with a dentists mirror (a non-conductive plastic one) showed that it was one contact on the main breaker arcing to the buss bar. Since this was a Sunday and I had no source for a replacement breaker I took all the necessary circuits and put them on the non-arcing buss bar. All unnecessary circuits were turned off and put on the arcing buss bar. Since there was no current on the bad bar the arcing stopped.

On the next day, a week day, I spent half the day searching for a Cutler-Hammer 200 amp 2 pole main breaker. Not a easy thing to find. When I found one I pulled the meter and pulled all the breakers to examine the entire length of each bar. There had been serious arcing at one clip on the main breaker. At the direction of my guru electrician I cleaned the arcing residue off with a file and put "No-lox" on the entire length of each bar. Problem solved. Hardest part of the job was finding the breaker in stock and shelling out $90 for it (in 1984!)

Since it is often a hardship or quite disruptive to do much work on a panel it is worth it to do the best you can do when installing it. Preventive Installation and Maintenance. This condition I had could have progressed to a fire, a lost house and possibly lives if not taken care of.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#20
In reply to #18

Re: Federal Pacific Electric Co. Circuit Breakers

01/07/2013 6:27 PM

Here is one called NoALox from Ideal Industries

There's also a general purpose grease called No-Ox-Id from Sanchem.

My high school shop teacher has us put grease on practically everything electrical that was not a soldered connection, even on lightbulb bases and sockets. He said it was how they did it on the Navy Subs. That part I don't know about, but on land it really works, and while I can't prove it, it sure seems like the bulbs last longer.

Either product will make a better connection, for a longer time, on just about any copper-copper or copper-aluminum connection.

__________________
txmedic3338
Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (1); bluebelly (1); BruceFlorida (2); Dlingo (1); fixitorelse (1); frederick10 (1); jmueller (1); JRaef (1); old salt (2); PWSlack (1); SolarEagle (2); Tornado (2); TRANSFORMER (1); txmedic3338 (3)

Previous in Forum: Solar Panel Question   Next in Forum: Single Set of CT to 2 Power Meters? 3 Phase Meter to Measure 2 Phase?

Advertisement