Pure SINEWAVE Output from D/G !!

02/08/2013 4:20 AM

I Have a 500VA Honda DG . In runing condition my light load is flickering. it is very irritating. i thing it is due to engine ,that not a constant moment of inertia. is it possible to get an output with pure SINE wave as like our distributions line .
Thank you.

__________________
"Keep work and family separate. "
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2012
Posts: 115
#1

Re: Pure SINEWAVE Output from D/G !!

02/08/2013 5:25 AM

Check the AVR of generator,Problem will be generated If the AVR is not working

properly.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2009
Location: INDIA.
Posts: 39
#9
In reply to #1

Re: Pure SINEWAVE Output from D/G !!

02/20/2013 8:57 AM

there is no AVR section !!

__________________
"Keep work and family separate. "
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #9

Re: Pure SINEWAVE Output from D/G !!

02/20/2013 8:28 PM

What do you mean by "No AVR section" ?

AVR = Automatic Voltage Regulator. It can be an electronic module or an electromagnetic device of some kind like a compound transformer + rectifier etc. You need it to keep the voltage constant when loading.

If it is a small electronic module, then it might have some knobs for adjusting ...

Your 500VA unit is small. If the AVR is not with any adjusting pots, then maybe you can reduce the flickering by speed increasing.(?)

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Pure SINEWAVE Output from D/G !!

02/08/2013 6:15 AM

The Thimble Drome of gensets!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#3

Re: Pure SINEWAVE Output from D/G !!

02/08/2013 6:42 AM

What is your load?

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Associate

Join Date: Dec 2009
Location: INDIA.
Posts: 39
#10
In reply to #3

Re: Pure SINEWAVE Output from D/G !!

02/20/2013 8:59 AM

load maximum 250 to 300 Watt. there is no inductive load.

__________________
"Keep work and family separate. "
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Pure SINEWAVE Output from D/G !!

02/08/2013 8:14 AM

Dear Mr.RAMAKANTHA,

You have not mentioned the Number of Cylnders in the system. Any Diesel Generator set while running at Rated Speed will generate only SINE WAVE and NO DOUBT ABOUT the Generation of Sine Wave. FLICKERING of Light will be due to the following Reasons.

1. On Electrical Front: a) EARTHING in the POWER DISTRIBUTION may not be proper. b) The Neutral may be loose or connection may nay not be perfect. c) The Fuse/Links in the system may have problem. d) Defective AVR of the Generator - or too SLUGGISH RESPONSE by the AVR, for varying Voltage.

2. On the Engine Side: a) Fuel Injection may not be proper. b) Governor will be TOO SENSITIVE. c) Power developed in each cylinder may vary - due to defective/leaky Piston Rings.

Pl. check and inform what was the problem.

Thanks,

DHAYANANDHAN.S

Register to Reply
Associate

Join Date: Dec 2009
Location: INDIA.
Posts: 39
#8
In reply to #4

Re: Pure SINEWAVE Output from D/G !!

02/20/2013 8:56 AM

this problem occurs from New, when i was in primary school nearly 1994

DG - Only one cylinder

and this DG is single phase .

__________________
"Keep work and family separate. "
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#5

Re: Pure SINEWAVE Output from D/G !!

02/08/2013 10:56 AM

that not a constant moment of inertia


Unless the parts in the engine are changing shape, their moments of inertia will be constant.


For incandescent (and most other) lighting purposes, the output of small, standard generators is close enough to pure sine wave. Inverter generators synthesize a sine wave, so the quality of the electronics affects the shape of the wave. Your best bet might be to look at the output on an oscilloscope. You might find that a vibrating loose connection (such as the connection at the plug) is causing your flicker.

It is possible, but unlikely, that your light power supply (if an LED or CFL) is unusually sensitive to frequency. Some versions of this generator have a frequency meter, and you could experiment with lower or higher frequency to see if that helps. Also try the same bulb on mains power to make sure that it is not just the bulb.

__________________
Think big. Drive small.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Pure SINEWAVE Output from D/G !!

02/09/2013 2:21 PM

Check the AVR:

If there is a setting potentiometer labelled 'GAIN' or 'Sensitivity', reduce it a little by rotating rhe knob until the flickering stops. (if it increases, go the other way).

Register to Reply
Member

Join Date: Jan 2013
Posts: 8
#7

Re: Pure SINEWAVE Output from D/G !!

02/10/2013 8:28 AM

If you connect a multimeter to the output terminals when the generator is running it will show you the frequency and voltage before loading and after loading.

that will also give you an idea of voltage regulation.

if frequency is low adjust governor.

if you get a big voltage drop between open voltage and reading you get when you load the generator, replace AVR.

Check for loose wire connections and cable runs from DG and load

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); electrobrains (1); Hendrik (1); K_Fry (1); LAA_Lucke (2); Muthuvel (1); RAMAKANTA (3); Tornado (1)

Previous in Forum: Why Electrical Motor Using Terminal Block?   Next in Forum: What is Diversity Factor in Electrical Loads

Advertisement