Using AC Circuit Breaker in DC Circuit

02/22/2013 5:41 AM

If one wish to use AC Circuit Breaker in DC circuit, how much it will be feasible. and why/or why not.

__________________
BNDas
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
7
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Using AC Circuit Breaker in DC Circuit

02/22/2013 9:00 AM

It is more difficult for a set of contacts to interrupt the flow of DC current than AC current because the voltage is not crossing zero 120 (or 100) times per second. Therefore the DC voltage that a set of contacts can reliably switch is severely curtailed. Most circuit breakers rated for AC will be able to handle very low voltage DC, but then because the DC current interrupting will heat up the contacts more, it can also drastically change the current rating, so the trip values can become useless. The only circuit breakers you should use on DC are those that SPECIFICALLY state a DC rating on them.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 7)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8
In reply to #1

Re: Using AC Circuit Breaker in DC Circuit

02/24/2013 7:32 PM

You are correct.

Reliance Electric used to use MCB's with the three poles in series for DC armature protection under inverting fault conditions. The breakers where nominally 600VAC mag only with a very low trip setting (about 200% of motor NP). The breakers used had a DC rating along with the AC rating. The number of interuptions under fault conditions was very limitted, but tended to be less expensive than fuses rated for DC interruption. (Not all fuses will adeqautely clear DC inductive loads). The irony is the Fuses can be more expensive than the SCR's, but under inverting fault conditions the motor is more expensive than the entire DC bridge. Breaking the AC power delivery versus protecting the motor can be difficult, especially with high inertia loads that can drive the current for a long time across a "flashed" commutator.

Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Using AC Circuit Breaker in DC Circuit

02/22/2013 9:18 AM

This question is a fire waiting to happen!

Never make assumptions when dealing with electrical power, if you have no clue what the answer might be.

Get a copy of Indian electrical code. and read it.

Register to Reply Good Answer (Score 2)
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#3

Re: Using AC Circuit Breaker in DC Circuit

02/22/2013 3:35 PM

The manufacturer's datasheets are the best place to find your answer.

If you are using IEC-type MCBs, these typically have a DC rating of 48V per pole, but it does vary from manufacturer to manufacturer so it is vital to check. To further complicte things, the larger manufacturers also manufacture ranges of MCBs that are either AC with a greater DC rating (~125V) or are designed for DC only, also with the higher voltage rating.

Without wishing to plug any one brand, if you were to do a search for "GE Redline Technical Catalogue" you will be able to find and download a book that I have found particularly helpful for questions such as this.

__________________
paulusgnome
Register to Reply
Guru

Join Date: Dec 2005
Location: Etats Unis
Posts: 1871
Good Answers: 45
#4

Re: Using AC Circuit Breaker in DC Circuit

02/22/2013 10:31 PM

With DC if there is a resultant arc that bridges the gap across the open contacts there is no zero crossing that would normally exist with AC that would act to extinguish the arc.

__________________
The hardest thing to overcome, is not knowing that you don't know.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Using AC Circuit Breaker in DC Circuit

02/23/2013 12:32 AM

There are switches, contactors and relay contacts clearly rated for AC and DC. But be ready for a rude surprise, for how much derating is there.

Register to Reply
Power-User

Join Date: Apr 2010
Location: Dominican Republic
Posts: 189
Good Answers: 6
#6

Re: Using AC Circuit Breaker in DC Circuit

02/23/2013 8:45 AM

I have worked a lot with DC doing solar system installations. The OutBack systems provide DC breakers with thier equipment. On one installation we used 60Amp breakers and the breakers say CARLINGSWITCH, INC. on the body. One breaker failed. It did not trip it simply failed and when we removed it I could see signs of overheating. Out of curiosity I disassembled it and did a physical comparison to an AC breaker and must admit that in my opinion there wasn´t much difference on the insides. For safety reasons we use fuses up on the roof in the combiner panels. A fuse will melt under overload conditions not trip so the question of zero crossing current points for AC versus steady flow DC does not arise.

Try contacting the above INC or use fuses.

Regards

John

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#7

Re: Using AC Circuit Breaker in DC Circuit

02/23/2013 2:56 PM

This has been well answered already. Some manufacturers do show some DC characteristics. Look to the automobile industry - they use fuses to protect and semiconductors to switch.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Using AC Circuit Breaker in DC Circuit

02/25/2013 5:13 AM

Further to #2↑, having read it, then apply it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments