Anonymous Poster #1

Self Regulating Heat Tracing Cable

03/12/2013 7:35 PM

Hello All,

Can someone tell me if I need a thermostat to switch power off to a Self Regulating Heat Tracing circuit in case the cable overheats? I believed that self regulating heat trace cables need not have a thermostat in their circuit. The installation is in Hazardous Area (and the circuit will be RCD protected).

Your suggestions would be appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Self Regulating Heat Tracing Cable

03/12/2013 8:17 PM

Ask a supplier:Heat Tracing Products / Industrial Heating CablesHeat Tracing

"Self-regulating" might be a clue here.

Reply Score 1 for Good Answer
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Self Regulating Heat Tracing Cable

03/12/2013 8:34 PM

Ordinarily no. However, such cables come in various temperature cutoffs, so you need to check what the maximum cable temperature would be.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #2

Re: Self Regulating Heat Tracing Cable

02/06/2025 9:32 AM

...for the purposes of its being lower than the autoignition temperature of the flammable substance in the <...hazardous area...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#3

Re: Self Regulating Heat Tracing Cable

03/12/2013 8:44 PM

The heat tapes I have worked with that had temperature controls had the sensing device at one end. If part of the tape is under insulation and another part not, or the tape was allowed to touch itself or worse yet, cross over. It was sure to develop a hot spot and burn out.

This problem is made worse by the heat tracing expanding when energized so if it had been installed absolutely tight when cold, it will stretch out when warm and that slack can allow the tape to slide and touch or cross over if it is wound around the pipe or vessel.

By definition, heat tracing tape will cover at least some distance, often a considerable distance, since hot spots can develop anywhere along the trace, are you going to put in thermostats every few feet or few inches?

I suggest that you carefully describe your desired installation with your heat tracing materials vendor, listen closely to their suggestions and follow their guidelines for use of their products in your application.

TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #3

Re: Self Regulating Heat Tracing Cable

03/12/2013 9:56 PM

Self-regulating heat tape can parallel or cross over itself without developing hot spots.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Self Regulating Heat Tracing Cable

03/12/2013 9:44 PM

The installation is in Hazardous Area

Then it will almost certainly need to be hazardous area rated self-regulating heat trace cabling.

Standard industrial heat trace cabling will likely not be allowed, regardless of how it is protected against overheating (either by its own self-regulating design or with the use of an additional thermostat and/or RCD for circuit protection).

__________________
jack of all trades
Reply Good Answer (Score 2)
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#8
In reply to #4

Re: Self Regulating Heat Tracing Cable

03/13/2013 2:52 PM

My memory was of a heat tape back 15 to 20 years ago, that was self regulating. It was based on a positive temperature coefficient resistance of some sort of solid state material. You could cut it off of a roll (any length), and crimp on the power connection. The installer would also crimp on an insulating end. It had a real problem that the unsealed wires at either end, if it got wet, the cable started shorting and arching, and a fire of the plastic insulation occurred. As it consumed it self, it burned like fireworks fuses. It was used extensively in mobile homes here in the Midwest as the underside of these trailers was not heated. At any rate there were many unexplained fires, as these structures would normally 100% loss by un-determinable cause of ignition source.

__________________
ignator -
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Self Regulating Heat Tracing Cable

03/13/2013 4:33 AM

The person who can do this is the technical sales contact at the vendors of hazardous area self-limiting trace heating tape. Make the phone call.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7

Re: Self Regulating Heat Tracing Cable

03/13/2013 8:15 AM

After using such traces for a number of years and discovering some will get hot enough to burn polypropylene around them, although they claim to limit to 250 degrees, I finally found the temperature/wattage curves and even at 250 degrees F they have a significant wattage output. Apparently the "self limiting" is assuming an open air exposure on a roof at around 32 degrees ambient. Under those conditions, the wattage output would not be enough to heat any higher in temperature. We have driven a 250 degree "self limiting" to 305 degrees in tests in ambient temperatures of 75 degrees F, and poor air circulation.

If you need to limit to a lower temperature, yes, you need a thermostat. Why not just use the "non-limiting' type and a good temperature control unit? Precision Digital, Red Lion, and many others make very reliable relatively low cost temperature controllers that are quite programmable.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#9

Re: Self Regulating Heat Tracing Cable

03/13/2013 10:33 PM

Many self regulated heat lines will draw power even when there is no demand. These are honeycombed networks of conduction wires that will draw 1 watt per foot with no demand and 5 watts per foot when the demand is peaked. The advantage of these contracting networks is that they will create more connections (cold contracts the honeycomb) only in the area needed and not throughout the full length of cable. If you do not need the heat cable in summer time just shut it off. Otherwise it is self regulating along its entire length and no external thermostat is required.

__________________
If they want holy water, tell them to boil the hell out of it.
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#10

Re: Self Regulating Heat Tracing Cable

03/13/2013 11:55 PM

Electrical heat tracing cables are normally not allowed in hazardous locations. Unless there is something unique or special with the system you are asking about electrical wouldn't be allowed.

Steam tracing is normally used in hazardous locations. Copper or some other tubing is placed against the piping, vessel or other unit and steam fed through the tubing. Usually insulation is used to cover the unit and the steam tracing to make it more effective and efficient. Traps and thermal controls are also incorporated to regulate the temperature of the tracing.

I can't remember any installation in my numerous years (retired now) in a hazardous location where electric tracing was used (too risky and expensive)!

Also, heat tracing tapes can not be crossed over itself as others have stated. This is the first thing to fail if done so. Electric Heat tracing 101.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #10

Re: Self Regulating Heat Tracing Cable

03/13/2013 11:59 PM

Evidently you didn't take Electric Heat Tracing 201, which came along after self-regulating heat tapes were invented, and made part of 101 obsolete.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#13
In reply to #12

Re: Self Regulating Heat Tracing Cable

03/14/2013 12:23 AM

Following Electric Heat Tracing 101 kept us out of trouble if it was followed. Most electric heat tracing tapes including self-regulating explicitly state "do not cross". Also, I have seen numerous ones that were crossed and failed at the crossing point. Failures in a hazardous location tend to be extensive failures with collateral damages and frozen materials that must be thawed or cleaned up. Following the "do not cross" practice is much cheaper and safer than a hazardous area fix and clean up. It also does not expose personnel in the area to a potential accident.

Why take the risk?

Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#11

Re: Self Regulating Heat Tracing CableI

03/13/2013 11:59 PM

Have been installing heat trace in hazardous rated areas, both CL I & II, for 25+ yrs. Never had an installation that wouldn't require a thermostat or controller of some sort. Is this for freeze or process protection? What type piping? Regardless, contact your local Raychem/Chemelex or Thermon rep. Most hazardous rated, self-regulated, tracing, start at 65 C. Redundant and or some sort of indication of thermostat failure may also be needed. Ran across an installation where process heat tracing was used for freeze protection on an eye wash station. Thermostat failed, eye wash became a geyser, during a routine safety check of the station's operation. The self-regulating tracing, was rated at over 160 C. Be careful, if you don't know, contact those who specialize in these installations. They will be more than glad to assist you.

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Reply
4
Participant

Join Date: Mar 2013
Posts: 3
Good Answers: 1
#14

Re: Self Regulating Heat Tracing Cable

03/14/2013 2:16 AM

Raychem manufactures ATEX approved self regulating heat tracing for Hazardous areas. This is widely used in the Oil & Gas industry. The only use for thermostats in this application is for on/off function in accordance with the ambient temperature.

Reply Good Answer (Score 4)
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#15
In reply to #14

Re: Self Regulating Heat Tracing Cable

03/14/2013 4:36 AM

It is a bit more complex than the ambient temperature that drives the thermostat.

Self Regulating Heaters are safe for usage in hazardous areas: check the approval for the zone classification to know whether it would fit your zone. (contact the Authorothy having Jurisdiction to take decisions)

Cables exist with unconditional rating T2 till T6: just the cable will never go over the classification borders, overpowered, on a spool, nicely insulated.

So to answer the original question: NO

For energy consumption it is alway's wise to use line sensing: keep the pipe exactly at the temperature you require and not more.

A cut-off heater does not exist, they all have a negative temperature-power relation that will reduce the power as the heater gets hotter.

__________________
"Here we are now, entertain us"
Reply
Reply to Forum Thread 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bfmickl (1); Gwen.Stouthuysen (1); ignator (1); jack of all trades (1); kevinm (1); lyn (1); old salt (2); Phys (1); PWSlack (2); Thiele (1); Tornado (3); Turbotroll3 (1)

Previous in Forum: How to Tune a =% Valve with Linear Plug   Next in Forum: Class A & B in Temperature Sensor (PT 100 & PT 1000)

Advertisement