Current Flow in Single Phase Neutral but Not Three Phase

03/16/2013 12:29 PM

I can't seem to find the answer to this question anywhere on the net.

I understand that there is no current flow in the neutral leg of a star configuration when the loads are balanced. I also understand that current does flow in the neutral in a single phase arrangement in a house per say. For example in a toaster the current will flow down the live through the element of the toaster and then back down the neutral so hence current flow in the neutral.

What I do not understand is that the house is part of the star arrangement with the first house having R the second having B and the third having Y and the pattern repeats across the estate with all houses having a connection to neutral. So.....the current flows in the single phase within the house, coming out of the toaster element, BUT when it meets the neutral outside the house it is said that any currents and voltages are cancelled out in the neutral in a balanced load. So why isn't the current coming out of the toaster cancelled out because it is part of the star configuration ?

I think I may be interpreting this wrong but I wandered if someone could clear this up. I have asked engineers and lecturers this but they can't see what I am getting at.

Register to Reply
Pathfinder Tags: Power Systems
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#1

Re: Current flow in single phase neutral but not three phase

03/16/2013 1:47 PM

The 3 phase distribution is high voltage, which goes through a low voltage isolation transformer. It's this low voltage that is connected to the house. The neutral is not connected back to the primary side, and the primary side does not have a neutral on the high volt distribution. So it's the center tap on the secondary that handles any neutral currents, and it's resolved there.

__________________
ignator -
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #1

Re: Current flow in single phase neutral but not three phase

03/17/2013 8:16 AM

You are assuming that its a 60 Hz home installation in say the USA or similar. Even some of the 60Hz installations around the world may not follow the system you mentioned in quite the same way....

The OP needs to confirm where he is an what system he is using, but it sounds like a European system at a guess, which of course may be completely wrong. He does appear to know its 3 phase......

The USA uses these single phase transformers and the neutral connection goes to the middle of the secondary for 2 x 110 volts output.

It is not 3 phase. Its single phase. There is technically no phase difference between the two outputs (except that as they are usually measured relative to neutral, there appears to be a 180 degrees phase difference.....)

Single phase step down transformers are occasionally used here (no central neutral) for outlying farms and the like, but usually even those are usually 3 phase nowadays...

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Active Contributor

Join Date: Jun 2012
Posts: 13
#8
In reply to #7

Re: Current flow in single phase neutral but not three phase

03/17/2013 8:24 AM

The system in question is just an average UK street which I believe is fed by 3 phases with individual streets getting a single phase each.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Current flow in single phase neutral but not three phase

03/16/2013 2:16 PM

...and assuming the phases are balanced which they never are, the load presented by the identical three houses' toasters in this hypothetical estate shares the neutral conductor between the houses and the neutral current flows between the houses. There is no net current in the neutral back to the star point of the distribution transformer LV side. As far as the distribution transformer is concerned, the loads are balanced and there is no current in the neutral between that place and the estate.

Once one of the toasters has ejected its toast, the loads are no longer balanced and the neutral cconductor from the estate back to the distribution transformer LV star point carries the vector sum of the phase currents to the other two toasters back to the star point of the distribution transformer. That is its job.

Simples.ζ

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/16/2013 6:00 PM

In a single phase installation the neutral current equals the phase current.

It's only when you get back to the tap off point of the three phase system do vectors come in to play. The three phase neutral current is then given by:

In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/16/2013 11:04 PM

In a center-tapped single-phase system, if the loads are balance on each side of the center, then the combined neutral carries zero current. It's just like a 2-point star vs. a 3-point star.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 3:02 AM

Dobidust,

It sounds like you are dealing with three dwelling units, each one supplied by two "hot" wires and the common neutral from a three-phase four-wire star system. Now, at each dwelling you are connecting a "toaster" that has two identical heating elements connected from the neutral to each of the two hot wires. For dwelling #1, the connected phases are A & B, with the unbalanced current on the neutral pointed as a vector in the direction of C. In dwelling #2, the connected phases are B & C, with the unbalanced current pointed in the direction of A. Similarly, in #3, the connected phases are C & A, with the unbalance in the direction of B.

At any point "upstream" of the three dwellings, the unbalanced current is pointing equally in the direction of A, B, and C. Since they are 120-degrees apart, the vector sum of the three is zero. Hence, you have no net neutral current drawn from the transformer, even though each dwelling has a net neutral current on its individual connection to the power line.

--JMM

Register to Reply
Active Contributor

Join Date: Jun 2012
Posts: 13
#6
In reply to #5

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 5:20 AM

I am guessing the the principle is the same for UK households which each receive a single phase and neutral, only that the net neutral current is cancelled out by vector sum back at the LV substation at the star point ? So would we would in deed be able to measure a current on the neutral coming out of the toaster and also at the consumer unit ? Is this correct thinking on my part ?

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13
In reply to #6

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 3:25 PM

Yes.

Each household neutral wire will have current flowing in them. But the vector angle of each one is different, (phase angle), and if balanced, 120 deg appart.

the resulting vector of the 3 neutral current will be zero if they are absolutely equal in amplitude, when they meet at the star point.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#9

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 8:40 AM

If you add three equal amplitude sine waves that are 120 degrees offset, they add to zero. Thus, the three neutral currents from the three phases can add to zero.

That having been said, the neutral currents will only cancel if the loads are equal and are linear resistive loads. A good example of a non-resistive load is fluorescent lighting. Because the conduction is higher at peak voltages, the current waveform has higher harmonic content, i.e., it is not sinusoidal. In this case you loads may be equal but you could have considerable third harmonic and higher currents flowing in the neutral.

Register to Reply
Active Contributor

Join Date: Jun 2012
Posts: 13
#10
In reply to #9

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 8:47 AM

My question is that in a UK house with a single phase supply the phase current matches the neutral current, when does it become a vector sum ? is it back at the substation or out on the street ?

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#12
In reply to #10

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 9:59 AM

I am assuming the you have a Y connected primary (three phases + neutral)

A three phase transformer can be thought of as 3 single phase transformers. The voltage on the primary windings is higher than the secondary and the current is lower on the primary side by whatever factor the step-down ratio is. The primary currents, proportional to the secondary currents (by 1/step-down-ratio) combine to cancel out on the neutral on the primary side of the transformer.

I hope this was helpful.

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#11

Re: Current Flow in Single Phase Neutral but Not Three Phase

03/17/2013 9:44 AM

In a balanced circuit, the current in your neutral will reach the star point (which is at zero volts) and split two ways to flow back via the other two phases. Because at that instant of time the voltage of the other two phases will be less than zero (negative) so no current will flow through the common neutral.

If the phase loads are unbalanced then the star point will not be at zero volts and some current will flow through the neutral.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2011
Posts: 13
#14

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/09/2013 8:42 AM

Hi there

Normally the Distribution transformers in the area got a vector group of Dy1 or Dy11...it all depends on the manufacturers...

If you are a 380V three phase power user....you are know the only one taking power from that transformer...all other equipment shut off.......only taking power for a 380V 3 phase motor being used..."NO" current flow in the neutral of the transformer

You also want to take power to boil a kettle in the kitchen...that is now 220V single phase power drawn from the transformer.....know there is current flow in the neutral of that transformer through the starpoint (380/sq rt3=220V)....for all 220V equipment being used there is current flow in the neutral of that transformer.......................

May be you understand it better know.........................

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#15
In reply to #14

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/09/2013 2:21 PM

This is not helpful at all.

You might have confused the issue, unless I did not understand your last paragraph on the "... kettle...".

If the Neutral is not available because it is cut off at the particular pole, then he will not have any current returning by the neutral point. All his loads will be between any 2 phases, via other possible loads, meaning that the voltage accross any switched load, will be anywhere between 0V (if no other load is switched on at another phase), and near 380V (possibly 300V + ) when some other load is switched on another phase).

Register to Reply
Anonymous Poster #1
#16
In reply to #15

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/11/2013 2:12 AM

Ok Vector group Dy11--for example only

lets try this....On the High voltage side 22kV(HV is Delta connected)

On the Low voltage side 380V (phase-phase) LV is star connected--the transformer connection "HV three windings" and "LV three windings"

On the LV side the starpoint is earthed(at the Customer house his neutral must also be earthed .....then for him to use the kettle(220v) single phase there is current flow in the neutral conductor and also in the live conductor...either R or W or B ...it all depends on which phase being used to supply the 220v for that house for then using a 220V kettle

Hope it makes sense know

greetings

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#17
In reply to #16

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/11/2013 4:26 AM

If you are #14 contributor, Thanks for the clarification.

Now you are saying that the earth return is used as Neutral return. This is not a safe and sound situation since the Voltage drop will depend on the earth resistance and the total current flowing down the earth return. Your 220V will be lower as more current is flowing: ex: if R=1 Ohm, and Current is 10A, you will drop 10 volts, to 210V. For 1 kettle, this is maybe OK, but imagine more single phase loads at the same time, and if R = 2 or 3 or 4 Ohms.

The described case (by OP) is a case where the Neutral to the house is cut, and the loads are now, mainly between phases (the earth return will be contributing in the faulty situation, but will be less influential if other loads are on different phases).

If the load is only on one of the phases, then the case is as you described, with the voltage drops due to earth resistance (the earth connection will exhibit some voltage).

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#18
In reply to #17

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/11/2013 6:20 AM

What you say is true and I agree, but if you look around the world, such methods as using the earth, also as a "return" is almost "standard"......but are intentional, not accidental. That is a two wire distribution. It saves a wire.

There are some CR4 members who know more about this than I do for example who could chime in if needed.

Some of the more remote parts of South Africa & Australia spring to mind for example.

Where I live in Germany we have the neutral & earth linked in the house distribution box because we have 3 phase and neutral coming into the house, but no earth.

The neutral & earth link is not made in the local substation.

In the UK for example, the link is in the substation I believe, but like the USA, no 3 phase into the houses, only a single phase, neutral and earth.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#19
In reply to #18

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/11/2013 7:12 AM

I agree that the earth could be used as a Neutral return for economy. This will be a single wire distribytion system, if for single phase, and not a 2 wire system.

But this method can only be used for small loads (Very small) and the earth rods need to be properly checked for near zero resistance.

Any 2 wire supply, for single phase system, will mean that a Neutral is there or if the main supply is 3 phase 115V and 2 phases are used to supply 220V for a house, then the one of the 2 phases is considered as a neutral while the Starpoint at the transformer is not grounded. This will make it possible to ground the 2nd phase (as Neutral), at the house, if that is necessary for protective devices to operate (?).

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20
In reply to #19

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/11/2013 1:24 PM

You have got it wrong on both 115vac US house systems and single wire earth return systems, sorry to be negative, but it is always best to get it right.

115vac US house systems.

Only one phase is supplied into a house but at 220vac. The supply is center tapped for 115vac neutral to phase and this is also grounded as safety ground, which is most likely also connected to an earth spike and any metal water pipes in the house.

I would guess that the transformer is a delta output at the substation. (citation needed)

You can see this well on a scope as the two "ends at 220vac" show as being 180° out of phase, whereas on a true 3 phase system, it will show any two phases as being 120° out of phase to each other, an obvious difference....

Single wire earth return systems.

The single wire earth returns systems use I believe a huge grounding plane buried in the ground, but to get the levels of power needed, they send a very high voltage, that is transformed down locally to the user to achieve normal mains voltage. (Citation required). What actual high voltage is sent I could not say.

This achieves useful amounts of power for the local home/farm user, not "very small" (Though no definition was supplied for very small, but I am talking about a house or farm supply) as you appear to believe......that would hardly make it worthwhile running wires for miles if you can only run a single light bulb at the end of it!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#21
In reply to #20

Re: Current Flow in Single Phase Neutral but Not Three Phase

04/11/2013 1:36 PM

Thanks for the US supply clarification.

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 23
Good Answers: 2
#22

Re: Current Flow in Single Phase Neutral but Not Three Phase

12/04/2013 12:15 AM

Hi Dobidust,

In a star you have a Neutral is the Key item---in typical European residential systems the different phases are phase to neutral not phase to phase 3ph, except in the water heater and sometimes the stove or oven, so most of your current will be from a phase through the neutral.

Expat 07

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #22

Re: Current Flow in Single Phase Neutral but Not Three Phase

12/04/2013 7:01 AM

I do not understand your thinking.

I am going to stick my neck out here as it is very many years since I studied this stuff, but here goes:-

In a European (not a UK or a US one as far as I am aware) home with 3 phases and a neutral coming into the house, all the single phase current will flow in the separate neutral used to supply sockets and other loads, via a 3 wire cable (Phase, Neutral and Earth), back to the switchboard/fuse box in that house.

At the SWB/FSBX, all the neutrals will be tied together and also tied to the neutral coming in from the street.

If all phases are only connected to single phase loads, just for an example, and if all the single phase loads are all the same, perfectly symmetrical and identical, there will be no current on the neutral going back to the local substation. It will only be seen on the individual neutrals leaving that point and going into the house...

At that time, measuring on the neutral point to ground will show 0 volts. A condition that in practice will probably never occur.....due to unbalanced loads, capacitive and and inductive and well as load currents. It is next to impossible to balance loads exactly in practice.

Neutral & Ground will be tied together at some point depending upon local Electrical laws, it could be in the house and it could be at the substation. I am personally not aware of any other possibilities for tying earth and neutral in Europe domestically, but I bet there are some!!

All the current/power will be now passing only via the 3 phase connections to the substation.

You need to draw it out and look at it carefully before it is clear. Using 3 wire and 5 wire cables in the correct places.....

I do expect the "electricians" among you all to tell me I am wrong (as usual!!), but I expect most of the good EEs to agree with me fully....

OK?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); Anonymous Poster (1); dobidust (3); EXPAT07 (1); horace40 (1); ignator (1); jmueller (1); LAA_Lucke (5); MJ Jordaan (1); PWSlack (1); Rixter (2); TonyS (1); Tornado (1)

Previous in Forum: Permanent Magnet Generators 65 RPM   Next in Forum: Calculate Transformer Power Rating

Advertisement