Changing Boiler Fuel Type

03/17/2013 5:06 PM

I have 2 boilers each 3035 kW with efficiency 85% and I am planning to change the burners to dual type one because the cost of 1 cubic meter of natural gas is almost 1/3 the cost of the 1 liter of oil.

how to calculate the energy saved and payback period taking into consideration the initial cost is 215000 US$; and the average daily operating hours for the 2 boilers is 8 hours per day and the calorific value of oil is 11.22 kw/liter and 10.73 kw/m3 of natural gas.

__________________
Mohamed A ESMAT; Director Of Engineering; LMH
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Changing Boiler Fuel Type

03/17/2013 7:31 PM

It sounds like you have all the data you need to produce a fairly accurate estimate except for the price of oil and gas.

If you want to go a step further you could also take into account the cost of changing over the transporting, handling, storage and maintenance from oil to gas.

Do you get any additional government (environmental charges or rebates) or maintenance benefits from switching to a cleaner fuel? Don't forget to check as you may find this reduces the overall payback period.

__________________
jack of all trades
Register to Reply
Member

Join Date: Jun 2011
Location: Le Meridien Heliopolis Hotel - CAIRO
Posts: 7
#3
In reply to #1

Re: Changing Boiler Fuel Type

03/18/2013 1:50 AM

the unit cost of light oil in my country is 0.164 US$/liter and for natural gas is US$ 0.0522US$/m3

do not amaze I believe these prices will increase soon; however let us work on the existing.

thanks

__________________
Mohamed A ESMAT; Director Of Engineering; LMH
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #3

Re: Changing Boiler Fuel Type

03/18/2013 5:29 AM

Then all the information needed to effect the calculation is already to hand, assuming that by <...kW...> in the calorific values what was meant is actually kWh.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jun 2011
Location: Le Meridien Heliopolis Hotel - CAIRO
Posts: 7
#6
In reply to #5

Re: Changing Boiler Fuel Type

03/18/2013 5:49 AM

yes you are true the calorific value in KWh

__________________
Mohamed A ESMAT; Director Of Engineering; LMH
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Changing Boiler Fuel Type

03/18/2013 6:09 AM

Go on, then. Get the pocket calculator out...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #6

Re: Changing Boiler Fuel Type

03/18/2013 12:01 PM

Dear Mr. esmat,

The Calorific Value will be in BTU/Lb. (or) CHU/LB. (or) K.CAL/Kg. (or) KJoules/Kg. (or) W/gm. (or) KW/Kg. but not KWH.

DHAYANANDHAN.S

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Changing Boiler Fuel Type

03/18/2013 12:34 PM

W/g and kW/kg would not qualify as comprehensible units of calorific value as they both have the dimension [time]-1.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jun 2011
Location: Le Meridien Heliopolis Hotel - CAIRO
Posts: 7
#10
In reply to #8

Re: Changing Boiler Fuel Type

03/18/2013 2:40 PM

please check this site to see the relationship between the KWHR as energy unit and the KJ also

http://www.efunda.com/units/convert_units.cfm?From=203

__________________
Mohamed A ESMAT; Director Of Engineering; LMH
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Changing Boiler Fuel Type

03/17/2013 11:50 PM

dear esmat,

It is very simple. You have to ESTIMATE THE ALTERNATE FUEL REQUIRED - UNDER IDENTICAL OPERATING CONDITIONS, and once QUANTIFIED, MULTIPLY BY UNIT COST OF THE FUEL, this one You yourself can calculate.

While deriving the QUANTITY OF ALTERNATE FUEL, the COMBUSTION EFFICIENCY, Perhaps AIR-FUEL RATIO, NON-COMBUSTIBLES will come in to Picture.

The NEED is that "EQUIVALENT AMOUNT OFHEAT IS TO BE RELEASED, BY THE ALTERNATIVE FUEL, IN THE FURNACE - FOR IDENTICAL LOAD/OPERATING CONDITIONS" of the Boiler, then only we can estimate the fuel cost.

As other CR4 MEMBER has pointed out the Impact on the Investment of Equipment is also to be accounted, for arriving the OVER-ALL BENIFIT.

If you want, I will work out and post the message, for which you have to furnish the following, to derive the SAME HEAT RELEASE IN THE FURNACE, for both fuels.

1. FUEL ANALYSIS. 2. MOISTURE CONTENT if any in the FUEL. 3.ASH CONTENT and NON-COMBUSTIBLES. 4. EXCESS AIR USED or PERMISSIBLE.

DHAYANANDHAN.S

Register to Reply
Member

Join Date: Jun 2011
Location: Le Meridien Heliopolis Hotel - CAIRO
Posts: 7
#4
In reply to #2

Re: Changing Boiler Fuel Type

03/18/2013 1:59 AM

I do not have the fuel analysis however I am sure of the following info:-

light oil used has a calorific value of 11.22 KWh/liter and the natural gas calorific value is 10.73 kwhr/m3. and my boilers gross efficiency as per last audi was 85%.

my question is how to calculate the energy saved due to replacing my old burner by the new one working mainly with natural gas.

finally the government will not pay my property any debat all what I make use is the cost reduction of the each unit of fuel type as indicated previously

__________________
Mohamed A ESMAT; Director Of Engineering; LMH
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #4

Re: Changing Boiler Fuel Type

03/19/2013 8:00 AM

As pointed out by several others already, you are not comparing correctly the two fuels.

Where is it given that a cubic meter of gas produces the same amount of heat as a liter of oil? It could be more or even less.....

You need to work out the amount of heat (BTUs?) per Dollar of gas and the per Dollar of oil type you are using!!!!

Then you can properly compare one with the other.....till then, you are only guessing!!!

Though gas usually brings lower maintenance costs which may affect the comparison, as it brings less deposit with it and a simpler burner that does not need a pump. Not to forget that correctly formulated gas will still flow freely in even very cold weather!!!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#15
In reply to #12

Re: Changing Boiler Fuel Type

03/19/2013 10:14 AM

Given the location in Cairo, I doubt cold weather operation will be an issue!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#17
In reply to #12

Re: Changing Boiler Fuel Type

03/19/2013 11:14 AM

Dear Mr. Andy,

Your views concur with my views (Refer Post No.2), I have referred ""EQUIVALENT AMOUNT OF HEAT IS TO BE RELEASED, BY THE ALTERNATIVE FUEL, IN THE FURNACE - FOR IDENTICAL LOAD/OPERATING CONDITIONS."

This means EQUAL AMOUNT OF HEAT is to be RELEASED in the Furnace, for IDENTICAL LOAD CONDITIONS,for which, the quantity of the 2nd Fuel will vary and cost is known and can be compared.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#14
In reply to #4

Re: Changing Boiler Fuel Type

03/19/2013 10:10 AM

"my question is how to calculate the energy saved due to replacing my old burner by the new one working mainly with natural gas."

That is a good question!

To answer this you need to separate boiler efficiency and combustion efficiency, and review the numbers separately. You or your boiler tech needs to perform a combustion analysis to determine how effectively the existing burner is extracting energy from the fuel. Determine what repairs, cleaning or adjustments are needed to optimize the performance. Review the proposed new burners to determine their effectiveness in extracting energy from the fuel.

Generally, natural gas is easier to burn than fuel oil, and might be slightly better performance.

Good luck with your project.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Member

Join Date: Jun 2011
Location: Le Meridien Heliopolis Hotel - CAIRO
Posts: 7
#16
In reply to #14

Re: Changing Boiler Fuel Type

03/19/2013 10:32 AM

your comment is excellent.

please send me your e-mail and I can send my last boiler analysis to calculate the efficiency of the old burner and then we can work on the new burner analysis.

if possible we can calculate the combustion efficiency based on the report I will send you

__________________
Mohamed A ESMAT; Director Of Engineering; LMH
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#18
In reply to #16

Re: Changing Boiler Fuel Type

03/19/2013 1:26 PM

I apologize, but I must decline your offer of employment!

I would expect a city like Cairo would have consultants more readily available for a short assignment like this. Or check post 11, he seems close to your answer.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#11

Re: Changing Boiler Fuel Type

03/19/2013 6:53 AM

Doing a quick calculation

2 boiler on oil x 3035kW/boiler x 8/24 hr /day x 0.164 $/litre x 100/85 efficiency / 11.22kWhr/litre = $34.79/day on oil

2 boiler on gas x 3035kW/boiler x 8/24 hr /day x 0.0522 $/m³ x100/85 efficiency / 10.73kWhr/m³ = $11.58/day on gas

Savings $23.21/day.

Capital cost $215,000.

Bank interest at 4% on $215,000 = $23.56/day

Payback NEVER

(but if you can get 4% on this deal I want to be with your bank)

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#13
In reply to #11

Re: Changing Boiler Fuel Type

03/19/2013 9:14 AM

That also assumes that the capital costs include changes needed to storage facilities, safety and maintenance equipment, as well as retraining of personnel.

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #11

Re: Changing Boiler Fuel Type

03/19/2013 2:53 PM

Can you point me to a link which says that a cubic meter of gas supplies the same energy as a liter of oil. It appears to be missing from this blog as far as I can tell....

I did find these websites which understand the problems of calculation, it could possibly help the OP to get it right. (The second two links have built in calculators for which fuel is best for you)

One thing that is needed that has not been supplied, is the exact types of oil and gas, or even better, the calorific value of each in a specified amount.....

http://askville.amazon.com/BTUs-gallon-oil/AnswerViewer.do?requestId=5286513

http://www.fpl.fs.fed.us/documnts/techline/fuel-value-calculator.pdf

http://nepacrossroads.com/fuel-comparison-calculator.php

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#20
In reply to #19

Re: Changing Boiler Fuel Type

03/19/2013 6:19 PM

I took the values given in the original post, made the same assumption as post 5 that kW should read kWh and did a simplified calculation to show that with the figures as stated this project is a non starter. I did not question or verify the stated figures.

I also did not question that these boilers are running 8 hours per day which is very odd if you have to run 2 industrial sized boilers in tandem. I did not include a correction for the fact that any boilers only running 8 hours/day probably also only run 5 days/week and 45 weeks/year. If I asked my bank manager only to charge interest on capital only while a plant was running rather than 24-7-52, I suspect that his response might be unprintable in a child friendly forum like CR4.

I did not factor in a possible grant/investment tax windfall or that governments normally take 6-12 months to pay out such bounty. Nor did I factor in maintenance costs, training, lost of utility while the plant is modified and many other variables.

I suspect that this is a homework exercise. If it is, the teacher/lecturer/professor who set it should be castigated for including a totally unrealistic capital spend. The capital spend:returns ratio is so low that this would never have passed the first hurdle in a real commercial/industrial environment.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#21
In reply to #20

Re: Changing Boiler Fuel Type

03/20/2013 6:06 AM

You could be right about the Homework, let us wait and observe!

Certainly there is a lot of VERY important infos missing that need to be known and factored in before anyone can make a stab at finding out which fuel would be best!!!

I certainly have the feeling that the difference is a LOT smaller than the OP imagines!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); dhayanandhan (3); esmat (5); jack of all trades (1); jhhassociates (2); PWSlack (3); Ried (3); Tom_Consulting (1)

Previous in Forum: Gas Handling License   Next in Forum: Double Block and Bleed Valves

Advertisement