Grounding of 1C Unarmored Cable

04/20/2013 11:41 AM

Please some one clear my dought.....

How can single core un-armoured cable can be grounded.....??

Since single core cable should be grounded at one end to avoid circulating current......??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Grounding of 1C unarmoured cable

04/20/2013 12:11 PM

Attach one end of it to ground (earth).

I suspect more context is needed for this question.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2
In reply to #1

Re: Grounding of 1C unarmoured cable

04/20/2013 12:35 PM

Nah, we'll just get a wide variety of WAG, as we normally do. We'll probably collect a few that will deliberately misapply the tiny amount of information we do have. (Just use a pneumatic circular grinder. The burrs on the conductors will be ground off easily.) Then somebody will make a timely joke on a reply and the fun will begin.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3
In reply to #2

Re: Grounding of 1C unarmoured cable

04/20/2013 12:41 PM

I almost forgot, somebody will cite along the way some Engineering reference that the OP should already have to be doing their work. This may or may not generate a brief firestorm of safety concerns. As usual safety issues will lead to complaints of the "nanny state". A pedantic flurry will ensue until this vacuous thread dies.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Grounding of 1C Unarmored Cable

04/20/2013 5:43 PM

Using the correctly-sized cable lug, correctly-fitted onto a correctly-sized terminal. If in doubt, consult a qualified Electrician locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Grounding of 1C Unarmored Cable

04/20/2013 11:40 PM

It seems to be:

SHIELD [if it is a shielded cable] should be grounded at one end to avoid circulating current..

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Grounding of 1C Unarmored Cable

04/22/2013 5:43 AM

Oh! How naive you are!

When anyone talks about (intentional) grounding of a cable, it generally is understood that the cable's shield or armour is grounded intentionally, for reasons of safety, et al. It could be at one end or both ends, each method having their own merits & demerits. But, this applies to "armoured cables" only.

And, your bold lettered quote is wrong. It should read" "Since single core cable's SHIELD OR ARMOUR should be grounded at one end....."

So, unarmoured cables need not be grounded.

One exception could be that if the single core unarmoured cable itself is used as a grounding conductor or protective conductor, in which case, obviously the conductor core of the cable should be grounded at BOTH ENDS.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7
In reply to #6

Re: Grounding of 1C Unarmored Cable

04/22/2013 8:28 AM

Sorry electricalexpert65."But, this applies to "armored cables" only." Medium Voltage cable-from 5 kV-is always shielded and- usually- non-armored.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: Grounding of 1C Unarmored Cable

04/22/2013 8:42 AM

In your country you call it shield; here, in India, we call it Aromour.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#9
In reply to #8

Re: Grounding of 1C Unarmored Cable

04/22/2013 10:43 AM

So how do you know that the nomenclature of your country applies here?

Yet another WAG here.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#10
In reply to #8

Re: Grounding of 1C Unarmored Cable

04/22/2013 10:55 PM

Shielding is to prevent interference, Armour is physical protection...

All that aside, the OP Specifically says that the Cable is un-armoured Single core and does not mention a shield...

So the Cable is either earthed at both ends (DB & Earth Conductor) as it is a Protective Earthing Cable or the original question is a "Nothing" question.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); electricalexpert65 (2); PWSlack (1); redfred (3); Sapper (1); Tornado (1)

Previous in Forum: One Single Phase kWh Meter to Measure 3 Phase Power   Next in Forum: DC Motors

Advertisement