Testing a Potential Transformer

11/17/2013 10:50 AM

My boss gave me two numbers ptq and pt2 , 480/120 volts potential transformer of 150 VA , 60 Hertz to test because it was blowing fuses .

I used 50 HZ supply for all my testing as 60 HZ is not available in the workshop .

i did the following tests , i did the ratio test and it gave results very close to the ratio is is designed for i.e 4:1

Sr.No APPLIED PRIMARY (VOLTS ) SECONDARY VOLTAGE (VOLTS ) VOLTAGE RATIO
1 50 12.56 3.98:1
2 100 25.23 3.96:1
3 150 37.78 3.97:1
4 200 50.36 3.97:1
5 256 64.4 3.97:1

I tested the DC Resistance of the primary winding and the secondary windings and it came out to be

Primary winding resistance (H1, H2) - 16.2 Ω

Secondary winding Resistance (X1, X2) - 1.5 Ω

-------

Conducted Insulation test @ 1000 volts and obtained the below mentioned values:

a) Between primary and secondary : 2.2 GΩ

b) Between primary and ground : 2.2 G Ω

c) Between secondary and the ground : 2.2 G Ω

also i measured the inductance of the both primary and the secondary winding , the winding not being tested was shorted while measuring the inducatance

i have forgotten the exact value but there was a difference of 1.9 mHenry between the primary of pt 1 and pt2 . the inductance of the secondary windings is the same .

i have also measured the inrush current for the pt primary keeping the secondary open , it came out to be 1.28 A for pt1 and 1.31 A for pt2 , i beleive tha fuse being used is of .5 ampere

Please suggest me what other tests i can do .

are these pt good ?

and while doing the inrush current test i applied 380 volts @ 50 Hz , how do i determine the correct voltage while working on 50 Hz , because the transformer is designed for 60 HZ, what care should i take to avoide damage to the equipment

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Testing a potential transformer

11/17/2013 11:01 AM

all the tests you list are on the t-former itself. thats nice. they tell you that you have a good t-former to begin with. you didn't include information on the circuit and load of that circuit which is where your problem is coming from you can continue to replace good t-formers all day, they will continue to blow until you locate your real problem

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Apr 2012
Location: Sanskrit
Posts: 57
#2
In reply to #1

Re: Testing a potential transformer

11/17/2013 11:20 AM

Thank you Fredski !

I was only given the transformers to test , they were brought from the site after the complain .. I am not much aware of the rest of the circuit , i gave my boss all this data and he told me that though your report has lots of data but you haven't said anything about , the transformers are good or bad , i am begginer and i have not much experience in transformer testing so i wanted to collect more and more data before reaching any conclusion ...

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Testing a potential transformer

11/17/2013 1:32 PM

I suspect you just need higher rated primary fuses to accommodate the inrush current. Also measure both the primary and secondary amps when the transformer is loaded.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#4

Re: Testing a Potential Transformer

11/17/2013 8:56 PM

Past experience states; You need to test the transformer at its full load rated capacity and measure the temperature rise, say over a 24 hr. period to validate its functionality. You may use the following setup;

1) Using an incandescent lamp rated at 120V, 150 W, as your load, with an ammeter in series to measure the secondary current of the transformer.

2) You will also need a properly rated variac, (variable transformer) connected in the primary side. You need the ability to vary the input voltage to primary side of the transformer during this test.

3) using the variac slowly adjust the primary voltage until the secondary ammeter reading indicates the equivalent rated current capacity of the transformer.. at this point you may note that the primary input voltage will be lower than 480V rating of your device. This is normal since you are using a 50 Hertz supply!

4) At this point using the the ambient temp as reference you can start measuring the temperature rise of the transformer core. It is still normal if the transformer register a temperature rise of about 80 degrees centigrade over the duration of this test.. Note that operating at 50 Hertz will also contribute to additional heat rise!

Good luck!

__________________
vsar
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#5

Re: Testing a Potential Transformer

11/18/2013 2:01 AM

Mr. Tyagi, There is no problem with your transformer. Only use Delayed type HRC fuses or glass fuses. You find these in three ratings, slow or delayed, Fast and Ultrafast. I remember we used to get DZ type delayed fuses from Siemens. You can refer to catalogue of any fuse manufacturer and select the delayed type - hopefully your problem will be solved.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#6

Re: Testing a Potential Transformer

11/18/2013 2:31 AM

There will be a problem if you keep trying to run a 60Hz transformer on a 50Hz supply. Notice how much lighter the 60Hz transformer is. Wonder why? Consider what this might do to the transformer - in particular the current ...........

Register to Reply Score 1 for Good Answer
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#7

Re: Testing a Potential Transformer

11/18/2013 2:36 AM

Problem is with 0.5A fuse which may be a fast acting fuse and can blow off while in-rush current is applied in short period of 10ms-100ms. If slow blow fuse is used then this problem may not come. Perhaps load is a switching power supply with may be consuming much higher inrush current than what you have stated here. Ask the user to use PTC or resettable fuse of 500mA

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Testing a Potential Transformer

11/18/2013 4:15 AM

The purpose of the fuse is to protect the wiring. It is not there to protect the transformer!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#9
In reply to #8

Re: Testing a Potential Transformer

11/18/2013 9:59 AM

The purpose of the fuse depends on where it is located within the circuit.

If the fuse is on/in the primary side of a transformer it's protection function includes the transformer as well as the wire.

I often come across the same type of issue as listed in the OP.

I quite regularly get calls because a fault occurs, the equipment that caused the fault may or may not be removed and/or replaced, and then the technician either does not know the difference between fuse types or does not have the correct fuse on hand so they substitute a quick acting fuse where a delayed fuse is required or vice-versa and the mystery saga begins.

Many times the original technician is not sent back to the site and instead a second technician replaces the fuse with whatever was/is existing when they accessed the site so the problem takes a long time to actually get properly addressed.

Often I am called to try and put the smoke back into the transformer and/or other ambient equipment because at some point a technician in their frustration installed a fuse that is considerably too large and therfore does not protect anything in the downstream circuitry.

I am a firm believer that especially in today's workplace of hastily trained technicians that instead of depending on memory we need to start intensive labeling of all equipment so that these errors are minimized and hopefully eliminated.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Testing a Potential Transformer

11/18/2013 8:33 PM

Dear Mr.Mukultyagi,

Your Tst Results indicate - NOTHING WRONG IN THE TRANSFORMER.

Problem is on the Load side, and that circuit is to be checked. Perhaps it may be close to dead short - Circuit Continuity test may indicate the problem.

Pl. post the information, how the problem was solved.

DHAYANANDHAN.S

Register to Reply
Associate

Join Date: Feb 2009
Posts: 35
#11

Re: Testing a Potential Transformer

11/19/2013 1:34 AM

The primary winding fuse is mainly to isolate a faulty VT from the system.

From your data & tests this VT is a Single Phase line to line 480/120v 150VA Class 1(+/-1% ratio error permitted).

Using ohms law it can be determined from the above that a internal fault on the VT would probably be of the order of 700Amps IE:Z=VD^2/VA & If=V/Z.

The HV fuse should be about 20Amp rated to operate in +/- 10ms for 700Amps.

A far cry from the 0.5 amp presently rupturing.

The secondary fuse can be 10A to allow grading for sub secondary circuits..

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12

Re: Testing a Potential Transformer

11/19/2013 3:03 AM

For a 480/120 transformer of 150VA, the rated primary current is 0.3125A, and the rated secondary current is 1.25A.

Since the rated primary current <2A, the NEC (U.S. National Electrical Code) allows the primary fuses to be 300% or the next standard size up, which would be 1A.

The secondary fuse may be 125%, which would be 1.5625A. A 1.6A fuse would be a normal choice.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#13
In reply to #12

Re: Testing a Potential Transformer

11/19/2013 8:31 AM

I concur with Mr. Tornado's analysis..

Either that or the OP may use a "Slow Blow" or a "Time Delay" type fuse rated at 0.5A fuse at the primary.. whichever is available..

vsar

__________________
vsar
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); Fredski (1); Instruform (1); minggrabber (1); powersolutionsFBD (1); PWSlack (1); SHOCKHISCAN (1); Shyam (1); silverfox (1); Tornado (2); vsar (2)

Previous in Forum: Varistor Failure   Next in Forum: Pointers Towards NEMA Comparison Motor Studies

Advertisement