My boss gave me two numbers ptq and pt2 , 480/120 volts potential transformer of 150 VA , 60 Hertz to test because it was blowing fuses .
I used 50 HZ supply for all my testing as 60 HZ is not available in the workshop .
i did the following tests , i did the ratio test and it gave results very close to the ratio is is designed for i.e 4:1
|
Sr.No |
APPLIED
PRIMARY (VOLTS ) |
SECONDARY
VOLTAGE (VOLTS ) |
VOLTAGE
RATIO |
|
1 |
50 |
12.56 |
3.98:1 |
|
2 |
100 |
25.23 |
3.96:1 |
|
3 |
150 |
37.78 |
3.97:1 |
|
4 |
200 |
50.36 |
3.97:1 |
|
5 |
256 |
64.4 |
3.97:1 |
I tested the DC Resistance of the primary winding and the secondary windings and it came out to be
Primary
winding resistance (H1, H2) - 16.2 Ω
Secondary
winding Resistance (X1, X2) - 1.5 Ω
-------
Conducted Insulation
test @ 1000 volts and obtained the
below mentioned values:
a) Between primary and secondary : 2.2 GΩ
b) Between primary and ground : 2.2 G Ω
c) Between secondary and the ground : 2.2 G Ω
also i measured the inductance of the both primary and the secondary winding , the winding not being tested was shorted while measuring the inducatance
i have forgotten the exact value but there was a difference of 1.9 mHenry between the primary of pt 1 and pt2 . the inductance of the secondary windings is the same .
i have also measured the inrush current for the pt primary keeping the secondary open , it came out to be 1.28 A for pt1 and 1.31 A for pt2 , i beleive tha fuse being used is of .5 ampere
Please suggest me what other tests i can do .
are these pt good ?
and while doing the inrush current test i applied 380 volts @ 50 Hz , how do i determine the correct voltage while working on 50 Hz , because the transformer is designed for 60 HZ, what care should i take to avoide damage to the equipment