12/07/2013 10:01 PM

Dear all,

I am working in Hydro Power Station. Pressure at pen-stock Guard Valve (PGV) is approximately 10bars (At MIV 60 bars). I wanna change some of the gate valves associate with these PGVs. The power Station was commissioned 40 years ago.

However all gate valves has a number 300 on its body. I want to know that the number is mentioning its;

1. pressure rating in PSI or

2. its Class?

I am Confusing. Is it necessary to install Class 300 gate valves for this applications?

Please give a an answer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Gate valves

12/07/2013 10:32 PM

Why do you want to change some valves? Bored? Need work for the guys? Have extra money in the budget?

Some explanation of your intent is in order.

Lacking any further information, I would:

1. Ask the maintenance engineer.

2. Ask the facility engineer.

3. Ask your supervisor.

4. Using the same skills that got you here, contact the manufacturer of the gate valve and ask them what the mystery numbers mean, and what you should do. They will sell you the valves and make money, they should answer your questions.

Register to Reply
Active Contributor

Join Date: Oct 2011
Posts: 11
#2
In reply to #1

Re: Gate valves

12/07/2013 10:37 PM

Dear Lyn,

Those valves are leaking. I am confusing about this number, because Class 300 GV dose not need for this work. Thanks for the advice.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Gate valves

12/07/2013 10:46 PM

Contact the company who will sell you the new valves, or contact three, or more, companies who may sell you valves.

GlobalSpec.com

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Gate valves

12/07/2013 10:53 PM

I don't know what valve you have but it could well be a series 300 control valve....Here's a video demonstrating the proper valve for control operation....↓

http://www.youtube.com/watch?v=mqJ5ppRjmcY&feature=plcp

http://www.henrypratt.com/news/plunger.aspx

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Gate valves

12/07/2013 11:16 PM

What is "MIV"? How high is the dam? At what relative elevations are the various valves located? Are any of them fast-closing?

The "300" probably (but not certainly) means Class 300.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Gate Valves

12/08/2013 11:10 AM

I strongly suggest you call a valve supplier and have a sales engineer visit your site. consulting an internet forum is the wrong place to begin your project.

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7

Re: Gate Valves

12/08/2013 11:20 AM

I know nothing about the operation of such facilities... but... they are not to be trifled with. The power of water is staggering. Get an expert involved.

Why... Read this...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#8

Re: Gate Valves

12/08/2013 11:43 PM

Tilan-

You don't say what MIV means, nor the height of the water source so this is all based on what is normal for other types of piping. I have only toured Hydro Power Stations, not get into the "guts" other than a very intensive guided tour.

Check with the engineers who are responsible for the station.

If no engineers in house, get a consultant on Hydro Power Station piping. Have him look at it.

Check any prints of the plant. These should say on them. They should give some details.

Bring in a salesman or tech rep from a manufacturer or distributor who sells the appropriate size and type gate valves or just size of valve.

The money for outside consultants is well worth the investment!

DO NOT PURCHASE OR ATTEMPT TO DO ANYTHING WITH ANY VALVES UNTIL YOU DEFINITELY HAVE THE CORRECT INFORMATION.

In chemical processing and many other systems the 300 on the side, for the sizes of 1/4" to 12" and maybe above, means that the valve is rated for 300 psi. I include this only as information. As said before I'm not a Hydro Power Station Engineer and not very familiar with them just smaller valves. Get someone in there to help you. If you get the wrong one it will be a very costly mistake, $X,xxx,xxx.00

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Participant

Join Date: Nov 2013
Posts: 4
#9
In reply to #8

Re: Gate Valves

12/09/2013 12:35 AM

The questions you are asking, contain only little information, which can be a perfect recipe for disaster if you proceed as is.

A Gate valve is typically designated by size and rating / Class. To know the size, check the isometric drawings, it will have Bill of material which will give you some more additional information on the size and rating of the valve. This will also help you to discuss with supervisor as well as in contacting original valve manufacturer to go for an replacement or upgrade.

High possibility that a 40 year old isometric would have disappeared by now. Fancy your chances.

Post some pictures of installation with perspective.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Gate Valves

12/09/2013 1:48 AM

Dear Mr.Tilan,

In my opinion, it should be the CLASS of the valve, and the Pressure rating will be 150 psi.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#11

Re: Gate Valves

12/09/2013 6:45 AM

Don't forget that, on closing, there will be a velocity head resulting from inertia of the water.

Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#16
In reply to #11

Re: Gate Valves

12/09/2013 9:57 AM

A gate valve, used as a penstock (inlet for hydro turbine) will need to withstand a very high transient pressure - a shock - when shutting off the flow. That is what determines the class of the valve. An alternative would be to provide a surge relief column.

Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#18
In reply to #16

Re: Gate Valves

12/09/2013 1:57 PM

As I said, this is serious; there are so many things to consider eg. closing the penstock flow can cause cavitation; it happens all too often and is VERY expensive and potentially very dangerous.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#19
In reply to #18

Re: Gate Valves

12/09/2013 2:23 PM

What's to cavitate? Hydraulic hammer, maybe.

Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#12

Re: Gate Valves

12/09/2013 6:59 AM

Confirm that the 300 imprinted on the valves is the valve class; and that at normal room temperatures the pressure rating would be 720 psi.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#13

Re: Gate Valves

12/09/2013 8:56 AM

Your provided numbers for (measured ? ) pressure at the penstock (inlet ? ):

10 bars x 14.5 => 145PSI (This value is dependent on the reservoir height and can vary.)

Your stated MIV (Maximum Inlet Value ? ) at 60 bars yields:60 x 14.5 => 870PSI (If true this would be the maximum expected pressure generated when the reservoir height is at maximum value.)

By your own admission the valve must be capable of safely handling 870 PSI.

Are you sure that these valves are not plug valves? Normally gate valves are not used for throttle control and instead are used for isolation only.

I would strongly suggest you find out exactly what type of valve you are dealing with, contact a major valve manufacturer, provide them with all of the needed, correct information, and follow their recommendations very closely.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#14

Re: Gate Valves

12/09/2013 9:10 AM

More than likely you read 300 WOG?? valve rating is 300 psi and valve is suitable for water, oil or gas.

Simple enough??

__________________
Never stop learning
Register to Reply
Associate
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Mar 2013
Posts: 38
Good Answers: 2
#20
In reply to #14

Re: Gate Valves

12/09/2013 9:03 PM

Agree.

Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#15

Re: Gate Valves

12/09/2013 9:24 AM

Tilan,

I EPC hydopower systems. This is not a small question. Please get hydro engineering involved.

Gene

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Gate Valves

12/09/2013 1:27 PM

And the commissioning records? Where are they?

And the maintenance records? Where are they?

And the Process Description document? Where is it?

And the Control Philosophy document? Where is it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 20 comments

"Almost" Good Answers: