VFD Drive Parameter

02/22/2014 4:31 AM

Hello,

Recently in our plant ,VFD installed for 315 Kw motor ( parameter are preset) brought from china, i would like to know

1) how to calculate minimum and maximum frequency for motor .

vendor is not so helpful.

Register to Reply
Pathfinder Tags: VFD drive selection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#1

Re: VFD Drive Parameter

02/22/2014 7:25 AM

Dear Mr.sriram1988,

Normally the Speed of the Motor to be specified by the Buyer. The range will be 10% as Min. and 90% of the specified speed by the Buyer of the Motor will be the Range.

DHAYANANDHAN.S

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#2
In reply to #1

Re: VFD Drive Parameter

02/22/2014 8:54 AM

Thanks for your valuable comment Sir dhayanandhan

Motor speed is 1485 rpm used as primary air fan for small boiler.

Is there is any rule that motor more than 20kw should not be run less than 20Hz (just to avoid lesser audible frequency) or any specific reasons.

Regards sriram.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: VFD Drive Parameter

02/22/2014 9:02 AM

If the motor is self-fan-cooled, too low of a speed may result in insufficient cooling. Each installation needs to be considered separately.

There may also need to be one or more skipped-over frequency ranges, to avoid resonances of the driven equipment.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#5
In reply to #3

Re: VFD Drive Parameter

02/22/2014 10:15 AM

Thanks for your reply Tornado

1) Motor has got separate cooling fan

2) Motor spec:

Power : 315 Kw ; V: 380 V ; A: 596 A

P.F: 0.85 ; Eff: 0.90 ; speed: 1485 rpm

Delta connection

class : F insulation

3) VFD now we are planning to connect was manufactured by ABB stromberg Oy (Finish). ABB announced this product as oboslete.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #5

Re: VFD Drive Parameter

02/22/2014 10:24 AM

Sorry to hear about the inconvenience of an obsoleted product.

Another item you should check is that the motor is rated for VFD operation, which affects the insulation of the windings.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #2

Re: VFD Drive Parameter

02/22/2014 10:49 AM

Dear sriram1988

You have referred that the Motor Speed is 1485 RPM. You can run 150 RPM approx. and above (10% of 1485 is 148.5) provided

1.The Motor is SUITABLE for VFD OPERATION, which should have external Fan, Insulated Bearing, or Bearing Insulation.

2. Earhting provided is minimum 2.5 times more than the Normal/Conventional size as that of the Conventional Motor,

3.The Cable to the Motor from VFD is less than 15 Metres.

4. Earthing of Cable Armor should be ON ONE END ONLY.

Pl. check up why the VFD purchased from China has failed and verify whether the above details are satisfied with the actual Installation.

Pl. check up the Effectiveness of HARMONIC FILTER and its level.

Pl. post the information - what was the problem,observed and reason for the failure.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#14
In reply to #8

Re: VFD Drive Parameter

02/23/2014 6:15 AM

Thanks for the detailed explanation sir. dhayanandhan

Soon i will post the problem observed in the VFD.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#4

Re: VFD Drive Parameter

02/22/2014 9:44 AM

Sriram1988

Have your company purchased motor or VFD or both together from China. You have given the kW capacity of the motor but what is the other details of the name plate like voltage , phase, frequency ,RPM etc. VFD has to be purchased to suit the motor . So your question is not clear please explain clearly so that a proper reply can be given.

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#6
In reply to #4

Re: VFD Drive Parameter

02/22/2014 10:23 AM

Thank for your interest V.I.Abraham

1) Motor spec:

Power : 315 Kw ; V: 380 V ; A: 596 A

P.F: 0.85 ; Eff: 0.90 ; speed: 1485 rpm

Delta connection

class : F insulation

2) Motor & VFD are manufactured in china. due to heat sink problem in VFD ( trips often), we decided to replace the VFD with avaliable VFD in plant .

3) VFD we are planning to install is ABB ACS 503 model.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#9
In reply to #6

Re: VFD Drive Parameter

02/22/2014 11:00 AM

Dear sriram1988,

You have referred "due to heat sink problem in VFD ( trips often),..."

The above point posted by you, makes to me to conclude

1. That the Heat Generated, due to Harmonic Effect is more than the Permissible Limit or the Ventilation in the VFD.

2. The Cooling Effect for the Heat Sink is NOT SUFFICIENT.

3. Harmonic Filter is NOT properly sized.

In my earlier reply, to you, I have raised these point.

To avoid this, HARMONIC FILTER is to be properly sized. Ventilation/air circulation to cool the Heat sink should be taken CARE. If AC is provided for the VFD Panel Room, pl. ensure the Temp.is just 24 deg.C and below.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#10
In reply to #9

Re: VFD Drive Parameter

02/22/2014 12:09 PM

1) yes i agree with you dhayanandhan We talked to the supplier , they informed us there is no problem with VFD . Real problem is ambient temperature ( 35 c) , suggested us to install chiller unit for the MCC room to bring down the temp to 25 C.This seem to be an expensive option for management on long run.

chiller unit installation+ running cost >= VFD energy saving

2) So we decided to replace VFD unit with ABB ACS -503. ABB unit works very well under harsh conidition.

3) We couldnt able to get any data from the VFD ,since parameter settings are locked (Password protected). Supplier are not helpful.

4) now we are using soft starter for motor.

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: VFD Drive Parameter

02/22/2014 8:53 PM

So many questions... it seems that a VFD was too complex of a choice for you, given that you are exhibiting inexperience that I would deem to make that the case. No offense, everyone must start somewhere. But with an obsolete (for 20+ years) 315kW drive, you have jumped into the deep end of the swimming pool before ever having learned to swim.

As to minimum speed, on a boiler ID or FD fan I would imagine that at some low speed, the fan ceases to move enough air for it to be effective, so THAT becomes your de-facto lower speed limit anyway. As a gross general rule, that tends to be in the 25-30% speed range. The VFD can make the motor go 1RPM, the motor might not like it, but the VFD can do it. The motor may be able, with that separate fan, to go 15 or maybe even 10 RPM. But at any speed even approaching that low, that fan will have ceased to move air long befor it got to that point, making the exercise futile and pointless.

I am often surprised by the general lack of search engine skills I seem to observe. Maybe it's because I live in California, near the Silicon Valley where Google dominates our very existence? But I had no problem at all finding a manual on line for an ASC503 ABB drive.

Try this (meaning Click Here):

Parameter Lock is Parameter #23, the Lock / Unlock code is 358

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#12
In reply to #11

Re: VFD Drive Parameter

02/23/2014 5:16 AM

1) Thanks for your reply.JRaef

2) Yes i am inexperienced in VFD or Field of engineering . i am not the one who is going to install that VFD .

3) I posting here ,because others (experts) can give some ideas , so that i can gain knowledge .vendors and plant engineers not so helpful..

4) sorry for my poor presentation (english skill).VFD i am talking was made in china, plant engineers are planning to replace the chinese VFD with ABB (ACS 503).

chinese VFD are vendor locked /password protected .

5) I already have the ACS 503 manual .we also had a chat with ABB .

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#13
In reply to #11

Re: VFD Drive Parameter

02/23/2014 5:22 AM

My primary question

how to calculate minimum and maximum frequency for motor to operate safely.

Regard,

Sriram

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #13

Re: VFD Drive Parameter

02/24/2014 3:43 AM

The minimum speed for a motor to operate safely is 0Hz.

The maximum speed depends upon the load. In the case of a fan, the power varies with something like the cube of the speed, so increasing the speed by 10% over its nameplate figure will lead to an increase in current of aroound 33%. Now, if the motor is oversized for the job, it may cope. If it is correctly sized for the job then increasing its speed may result in trips on overcurrent, indicating that if more forced ventilation is required, additional equpiment would be needed.

Without visibility of the installation it is difficult to comment further.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#15

Re: VFD Drive Parameter

02/23/2014 10:40 AM

The Maximm Frequency for the Fan Motor will be the Nameplate value, which is 50 Hz as long as this is the original manufaturer equipment and it was not modified.

if you increase the frequency above that value, you will be overloading the motor since the Power requirement for the fan is proportional to the cube of the rpm( if from 50 to 55 Hz, 55/50=1.1 => (1.1)³=1.331 ==> 1.331 * 315 = 419 kW). Therefore, the maximum limit will depend on the motor, the Fan+Ducting etc Curve Chart, and the VFD size. Most VFD can handle frequencies above the normal 50 , 60 Hz up to 100 Hz or up to 400 Hz.

As the Lower limit, below the Motor rated 50Hz (your motor), the limit will be dependent on the Boiler minimum requirement at the minimum firing load, and on the overall design.Also, on the cooling method of the Motor. Preferably, not less than 40% of the rated motor rpm, if there is no independent cooling fan(20 Hz).

You can run the Fan Motor at higher than 20Hz and close the inlet damper more to control the air volume while keeping the rpm high enough to keep cooling the motor at the low firing positions.

I hope that I understood your installation ...

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#16
In reply to #15

Re: VFD Drive Parameter

02/23/2014 11:00 AM

Thanks for the wonderful explanation . LAA_Lucke

1) Motor has got independent cooling fan.

2) Can you explain a bit more for " if there is no independent cooling fan(20 Hz)" .why 20 Hz why not 15 Hz or other frequencies. ( any association with audible frequency range.)

Regards,

Sriram.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#17
In reply to #16

Re: VFD Drive Parameter

02/23/2014 12:11 PM

If the motor is cooled by an external fan, fixed on its own shaft, the cooling air volume will be reduced as the motor speed is reduced. The motor windings will not be cooled properly as designed by the manufacturer if this self cooling fan speed is reduced too much. Usually, the heating will start to increase the internal temperature if run too long at very low speed. How long and at what speed this will happen is dependent on ambient temperature and designs ...

An independent cooling Fan is driven by an independent electric motor, at a constant speed not dependent on the speed of the Motor it is cooling. This will allow lower speeds if necessary, but try not to go too low for long periods unless the motor maker is consulted.

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#19
In reply to #17

Re: VFD Drive Parameter

02/25/2014 12:56 AM

Thanks for detailed information. LAA_Lucke

regards

Sriram.

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

dhayanandhan (3); JRaef (1); LAA_Lucke (2); PWSlack (1); sriram1988 (9); Tornado (2); V.I.Abraham (1)

Previous in Forum: Electrical Question   Next in Forum: Capacitor Value

Advertisement