RTD & Thermocouple

08/21/2014 12:51 PM

Why triad cable is used in RTD & why only pair cable used in Thermocouple??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: RTD & Thermocouple

08/21/2014 1:23 PM

Doesn't have to be. One could use two, three or four wires for either thermal transducer. It is all a question of precision and reliability.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: RTD & Thermocouple

08/21/2014 1:57 PM

The third wire for an RTD allows easy compensation for lead length, simply by subtracting resistances.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: RTD & Thermocouple

08/21/2014 2:38 PM

...which is not an issue with a thermocouple, as it produces a milllivolt signal that only uses two wires.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#4

Re: RTD & Thermocouple

08/21/2014 2:45 PM

See this description of an RTD which includes the rationale for the third wire

http://www.omega.com/temperature/z/pdf/z033-035.pdf

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5

Re: RTD & Thermocouple

08/22/2014 4:22 PM

The thermocouple works on the principle of different metals in junction produce a voltage when one end is at a different temperature than the other. The "wiring" of the thermocouple is actually the 2 different metals. Hence the 2 wires.

The RTD's are a temperature driven variable resistance device that varies resistance with temperature. Two wires are all that is needed here, but we throw in a third or fourth as a way to allow compensation for the wires resistance.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#6

Re: RTD & Thermocouple

08/25/2014 9:03 AM

The RTD has an ambient temperature compensation circuit, and the thermocouple not.

Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#7
In reply to #6

Re: RTD & Thermocouple

08/25/2014 9:09 AM

Not good. I was still pondering the 6" vs 8" stove pipe problem.

The issue is the wheatstone bridge employed in the circuit, which is not the case with the t/couple, which has a known temp versus voltage value.

Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#8
In reply to #7

Re: RTD & Thermocouple

09/25/2014 10:14 PM

Actually, it is a thermocouple measurement that has the 'ambient compensation circuit', more commonly known as cold junction or ice point compensation.

The temp vs voltage table values are only valid for ice point compensated measurements.

Register to Reply
Register to Reply 8 comments