Boiler Drum Water pH and Boiler Feed Water pH

10/17/2014 12:54 PM

Dear CR4 Members,

To-day I have come across a situation in a Boiler Plant of 80 Tonnes/Hr, 64 bar, 495 Deg.C. There is a Water Treatment/RO plant, De-Aerator, H.P Heater, and it is well designed system, with LP Dosing and H.P Dosing system

It is universally followed that the Boiler Drum Water pH will be always higher than Feed Water and it will be in the range of 10.5 to 11 for Drum Water, and 8.2 to 8.5 for Feed Water. The Boiler Manufacturer has prescribed the Water Quality as follows in the Instruction Manual. TDS of Feed Water is 2 ppm, and for and Drum Water is 100 ppm. Drum Water pH in the range of 10.5 to 11 for Drum Water, and 8.4 to 8.6 for Feed Water.

But one Chemical Water Treatment Company has approached us and suggested to use their chemical in which the following conditions are prescribed for operation.

1. Stop H.P. Dosing Pump, as no chemical to be used by H.P Dosing Pump.

2. Drum Water pH 8.8.

3.Feed Water pH 9.5.

4.Boiler Drum Water TDS - Less than 30 PPM.

Personally I am against these parameters, and I did not accept/approve it.

Now I want to know the views of CR4 MEMBERS in the Boiler Field, in Terms of Design and Operation and Water Treatment Field - whether I can insist my view.

Thanks,

DHAYANANDHAN.S

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#1

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/17/2014 1:44 PM

Approach the manufacturer of your equipment and ask if would be harmful or helpful to change to that chemical; consider costs and water quality.

Chances are that a savings project, becomes a nightmare in the end.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 3)
2
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#2

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/17/2014 1:47 PM

It not only the boiler requirements, the pH can also effect items with in the line such as steam traps.

I wrote a white paper on this, I'll PM you the link.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Aug 2014
Posts: 66
Good Answers: 2
#3
In reply to #2

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/18/2014 12:38 AM

Post the link.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#7
In reply to #3

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 10:41 AM
__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #7

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 11:50 AM

So basically what you are telling us in the link is that the customer's process cooker was either a direct-steam injection, or had a major leak in the cooking jacket? No challenge to dump any condensate from this out of the boiler loop, as you stated. Not only that, there is the USDA requirements for direct contact steam with food products, that clearly states how much neutralizing amine is permitted in such cases.

On a small boiler, the concentrations of neutralizing amine might be really hard to control, especially when said boiler operates in a surge/halt mode of steam delivery.

Perhaps I missed something in your white paper: is most of the steam actually being added to the cheese?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#9
In reply to #8

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 12:30 PM

Excellent reply, and you are correct, Steam is being added directly to the cheese.

There were filters on the inject side to supply culinary steam for a direct inject to the product. It has been a while, but I believe it's 2 microns filter for culinary steam. And that would be USDA-3A requirement, (there is a difference between USDA and USDA-3A)..... for some time they were thinking of combining the two, but I believe they are still separate entities.... so to speak.

It was direct steam inject, and the product was contaminating the condensate return with proteins through the steam injectors. The thought was with a higher pressure deferential on the injector side that wouldn't happen, but it does.

And with the boiler sized just enough to do the job in the best of conditions on the heavy loads. I myself believe they were lucky because the actually needs of the steam is not steady, as shown by my graph. I see you came to the same conclusions also.

There really was no reserve. Which was another reason why it would trip. But a larger boiler was out of the question, so we had to address and correct other inefficiencies

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #9

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 1:38 PM

Yep. That one is a no-brainer, as to condensate return.

To help with the steam surge, could they make use of a steam buffer vessel? I don't know, and of course it would have to be quite robust as to pressure/temperature stamp. Another small consideration - maybe use something like a clean water supply and a steam eductor operating at higher pressure to arrive at the right steam flow/ heat input to the cheese. That would cut down on interrmittant flow steam requirement.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#11
In reply to #10

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 3:16 PM

Yes, the one that design the system should have known better.

The rule of thumb I recall using was was 5 lbs of steam required for every 100 pounds of cheese. to bring the cheese up for 65 degrees F to 150 Degrees F.

And that rule of them was out dated. They are now bring the temps high to the critical point just short of Maillard reaction taking place. And also reducing the amount of moisture. Which increases shelf life by reducing the change of taste of the cheese (sharper)

Just letting it drain by the injectors steam trap was enough. The other steam traps they could return the condensate, but the amount of return was nothing. One thing that was critical, was that the delivery of steam was to be as dry as possible for reasons stated above.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#12
In reply to #11

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 3:27 PM

I suppose the direct steam contact method is more efficient in rapid heating. IF the initial steam is present with enough super-heat, the attemperated steam flow (after the water injection) will still be super-heated, and dry.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#13
In reply to #12

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 3:37 PM

This is where I meet a lot of impractical engineers.

A large cheese manufacture, I designed and fabricated (2) 750 pound batch cookers.

Operating at 70 lbs of steam (about 315 Degrees F) , with a batch time every 7 minutes approx.?

He wanted to use 150 lbs of steam (about 365 degrees F) thinking the temp/cook time was invertly linear. cutting the batch time down by about a minute. (I'm not going to get into pasteurization)

I told him to try cooking a pizza, or anything that way, then give me a status report of your results.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#14
In reply to #13

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 6:01 PM

that is a sound answer, given what you were presented with.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/18/2014 10:22 AM

This 64 bar boiler, (~930 psig, 176,370 lb steam/hr, 923 °F), is in range where either all-volatile treatment, or the more protective controlled Na:PO4 ratio (addition of DSP, NaOH (small amount) treatment are both acceptable. I prefer phosphate treatment, (1) additional protection against condenser leaks should they occur, and higher pH, although the free OH- ion concentration must be kept below 10 mg/L (Pand M alkalinity test), and (2) the quality of the water from the RO plant might not be sufficient to remove all hardness ions, and (3) there is a limit to silica that should enter such boilers, and while a bit higher for your boiler, still best to have higher pH than 8 something to limit silica vaporization into the steam, as the turbine will suffer.

It seems a bit odd that the feedwater pH could be maintained higher than the drum pH, since the make-up water specification is not that great, (in other words, there is still some alkalinity residual in make-up water, along with sodium, etc.)

I think it really remains to be seen how such boilers hold up under such an AVT scheme, but there is long-standing proof of boilers lasting at least 50 years with the alkaline phosphate scheme.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2014
Posts: 1
#5

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/18/2014 10:31 PM

1. HP dosing pump will be used in cases of abnormally high conductivity level

2. Drum water should be more than 9 for safety consideraion , but I stongly recommend you to monitor the OH instead , since this is more reliable reference of alkalinity .

3. Feedwater PH of 9.5 is okey ,to protect pump from abrasion or acidic attack

4. Boiler water TDS pf 30 ppm may not be attainable even with very good boiler water treatment . Two things that may cause lower TDS of your boiler water , it is either you have a very very clean feedwater or the boiler water chemicals are not reacting or functioning .

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#6
In reply to #5

Re: BOILER DRUM WATER pH and BOILER FEED WATER pH

10/20/2014 10:37 AM

Sure the operators could achieve 30 ppm TDS in Boiler drum water, even with the make-up to the system being as high as 2 ppm TDS, as long as sufficient continuous blow-down is maintained to control the cycles of concentration (ratio of makeup to blow-down flow) at 15:1 or less. The issue will then be de-aeration of the make-up to a sufficient extent to prevent oxygen attack of economizer tubes, etc.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

badbob (1); James Stewart (6); n_bacudo (1); phoenix911 (5); Yahlasit (1)

Previous in Forum: Hydraulics   Next in Forum: Lubricant

Advertisement