Comparing Work Required At Compressing Gas & Pumping Liquid

03/25/2015 11:33 AM

In one of online lectures comparing Vapour compression cycles (conventional refrigerators) with Thermal compression cycles (absorption chillers) it was said that former required more 'high quality' work input (mechanical compressor) than the latter (which requires low quality but greater quantity thermal energy)...

While comparing the two cycles it was said that between same pressure change work required to compress gas is very very high when compared with work required in pumping liquid through the same pressure change. This was said because the former refrigeration cycle required compressor but the latter only a solution (LiBr 50wt%) pump...or some times a refrigerant pump (demi water)

Is there any mathematical correlation that I can look at to understand this.

__________________
Chemical Engineers are like high Temperatures & high Pressures
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Comparing Work Required At Compressing Gas & Pumping Liquid

03/25/2015 1:30 PM

The work neded from any fluid mover is the difference between the finish conditions and the start conditions, multiplied by the flowrate.

  • In the case of a gas, the conditions can be evaluated by comparing the change in enthalpy. The pressure and temperature of the gas before and after the compressor can be compared on a suitable chart, or looked up in tables. Multiply by the mass flowrate.
  • In the case of a liquid, the work required is the change in pressure multiplied by the volumetric flowrate.

In either case, the electrical input is the calculated figure divided by the efficiency of the equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#2

Re: Comparing Work Required At Compressing Gas & Pumping Liquid

03/26/2015 12:05 AM

The electrical load for an absorption chiller is VERY low- the big energy "hog" is the thermal input required to re-generate the liquid desiccant.

Absorption chillers "cool" the water much like cooling towers- evaporating water sprayed on the "chilled water" coils which extracts heat from the chilled water to vaporize the water which is under a very high vacuum (so the water will "boil"- evaporate) and the gaseous water vapor is absorbed by the concentrated desiccant being sprayed in a coarse mist near the water spray on the tubes. The "cool" concentrated desiccant becomes slightly warmer saturated desiccant, which is then heated enough so that the water in it "boils" again, and then is condensed by some of the cooling water. The cooling water also cools the heated desiccant (now concentrated again) so it can do its thing all over again.

Using "English" terms- a high efficiency electric chiller can provide cooling at about 0.6 kW per ton- meaning that the cooling water needs to remove about 0.6 x 3412 PLUS 12,000 BTU's (or 14,500 BTUs) every hour per ton provided. A high-efficiency absorber uses about 9,400 BTUs of thermal input (and about 0.05 kW of power) for every ton, so the cooling water needs to remove 9,400 + 1,700 +12,000 BTUs (or 23,100 BTUs for every ton. That also means that the cooling pump will work about twice as hard, and the tower will have about twice the load (tower fan) to operate- which will use more electricity. NET power for an electric machine is about 0.75 kW per ton and for an absorption chiller is about 0.30 kW per ton- plus the thermal input.

Obviously, IF the thermal input energy (high grade waste heat) is FREE, the absorber is definitely the way to go- AND its "refrigerant"- water- has a zero GHG impact- always better than ANY refrigerant.

IF the thermal is coming from a "purchased" source, it is worth about 2.75 kW per ton so- the overall energy load is about 3.05 kW per ton- about 4 times more than an electric machine.

Hope this helps your decision process.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3

Re: Comparing Work Required At Compressing Gas & Pumping Liquid

03/26/2015 12:59 PM

This is an interesting question!

Leaving aside the details of refrigeration, and looking at compression of gases and liquids, for one-off compression in a closed cylinder, gas compression (isothermal, adiabatic or somewhere in between) needs more work, obvious because as liquid is practically non-compressible the piston movement → 0. But in continuous compression the liquid case uses more power.

For one-off compression it is non-flow work and

W = 1/(k - 1)*P1*V1*((P2/P1)(k-1)/k - 1) It's convenient to define n = (k - 1)/k.

Isothermal compression k = 1, n = 0. Can show that W = (P1*V1)*ln(P2/P1)

Polytropic compression (somewhere between isothermal and adiabatic) usual figures are k = 1.3, n = 0.23.

Liquid compression k → ∞, n → 1 and W → 0 as 1/(k -1) → 0.

For continuous compression, flow work = k*non-flow work.

W = k/(k - 1)*P1*V1*((P2/P1)(k-1)/k - 1) = (P1*V1)/n*((P2/P1)n - 1)

Isothermal W = (P1*V1)*ln(P2/P1) as for non-flow (as k = 1)

Liquid, k/(k - 1) → 1 as k → ∞, so W = P1*V1*(P2/P1 - 1) = V1*(P2 - P1) = V1*ΔP as expected for liquid flow. You can check power is greater than for gas compression.

This was discussed a while back under thread below.

http://cr4.globalspec.com/thread/99106/Compressor-Work-in-Brayton-Cycle

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (1); energygod (1); PWSlack (1)