Antipumping Contactor use

11/05/2007 2:18 AM

Breakers generally have a contactor or relay called antipumping relay....whats is its use...can anyone tell me point wise

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Oct 2006
Location: Hyderabad,India
Posts: 49
#1

Re: Antipumping Contactor use

11/05/2007 7:37 AM

Dear Sir

The use of anti pumping relay / contactor is to ensure that the breaker closing coil receives only one closing impulse.It does not allow continuous closing command to the breaker in case the TNC switch is held in the position of "close" continously.

For further details studying the manufacturer's closing circuit scheme of a breaker will be very helpful.

Hope the same is clarified.

regards

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#2

Re: Antipumping Contactor use

11/05/2007 9:35 AM

If you give the breaker a close command and the breaker fails to latch in the closed position , it will drop back to the open position.

Another reason why a breaker will do this is if there is a trip command present to the breaker.

The purpose of the anti-pimping relay or contactor is to prevent the breaker from trying to reclose every time it drops back to the open position even though you hold the close switch in the close command position.

This prevents severe wear to the breaker mechanism and contacts.

To give a second close command , you need to release the first command and make another atempt to close the breaker.

__________________
Learn more, Do more , Be more
Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Antipumping Contactor use

04/27/2008 6:53 AM

On a persisting fault , if a continuous closing command is maintined on an electrical circuit breaker , the breaker will first trip and then reclose due to the continous closing command . This is termed as " pumping of breaker .

This will result in considerable damage to system ( due to continous O-C-O-C operation)

To prevernt such pumping operation an antipumping device is used . This ensures

that breaker with continous closing commannd , once tripped , wlill not againg closed again unless closing command is withdrawn and deliberate closing commnad is given subsequently .

Antipumping is geneally provided by electrical interlocks..It involves an ausillary contactor or a relay .

Vikash Agrawal

Crompton greaves

Nasik

Register to Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Antipumping Contactor use

12/22/2008 5:35 AM

Sir,

NC contact of the Anti Pumping relay(K2) is back feeded

to the Closing coil so that when K2 is Picked

NC becomes NO and Closing Coil of The breaker is isolated

and O-c-O-C opeartion of the Breaker is prevented in the process .even when the

closing switch pressed continuously, for a period of time.

regards

Brijesh Ojha

Reliance Ind Ltd.

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); djacob (1); ravipra01 (1)

Previous in Forum: Load Flow   Next in Forum: L297 Stepper Dirver

Advertisement