Cantilever Beam is So Thick - Looking For Counter Proposal

12/27/2007 8:33 PM

Hi

There is this design from my consultant that proposes cantilever beam . Thickness is as 450 mm for a house. It looks odd . My friend suggested a prestressed beam but I have no idea on the design and methodology. Can anyone help me?

Regards Dave, Malaysia

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member Safety - Hazmat - New Member

Join Date: Dec 2007
Posts: 125
Good Answers: 1
#1

Re: Cantilever beam is so thick - looking for counter proposal

12/27/2007 9:19 PM

Must be one helluva cantilever, assuming it's an "H" beam. What is the application in more detail.. A balcony of what dimensions with what load... for example.

that's about 18 inches or so, right? By thickness you mean from the outside plates?

=============

If I'm "getting your drift" corectly, I am of the opinion that anyhthing else you put in there will be more bulky than the steel.

Register to Reply
Member

Join Date: Oct 2007
Posts: 7
#2
In reply to #1

Re: Cantilever beam is so thick - looking for counter proposal

12/27/2007 10:46 PM

The beam is of reinforced concrete and for a balcony of a villa. The span/ depth is to the limit of 7. Prestressed beams could be the answer .. for which I am looking for the detail design and method.

Regards

Register to Reply
Guru

Join Date: Feb 2006
Posts: 757
Good Answers: 12
#11
In reply to #1

Re: Cantilever beam is so thick - looking for counter proposal

12/30/2007 7:58 AM

Re: "Counter Proposal"

one helluva kitchen as well....for a counter to need such strength!

Register to Reply Off Topic (Score 5)
2
Power-User

Join Date: Apr 2007
Posts: 270
Good Answers: 19
#3

Re: Cantilever beam is so thick - looking for counter proposal

12/28/2007 4:48 AM

Some assumtions based on what you have already said:

  • house internal slab is 450mm thick
  • length of cantilever is 7 x 450 = 3150mm
  • the balcony is a continuation of the house slab

Now some observations in no particular order of merit:

  • you will probably need to stop rainwater by raising the threshold 100mm. make sure you don't lose 100mm of structural depth when this happens
  • 3150mm long balcony seems very long. can it be reduced and still meet your requirement?
  • the 1:7 ratio is based on keeping deflections down to a minimum (see also comment on crackwidth below) and, by implication, the dynamic response of your balcony: footfalls (for comfort criteria) and strong rythmic dancing e.g. party (for structural criteria)
  • if you have a span/depth ratio less than 7, you can reinforce the top of the slab quite alot to make it work in stress but the crackwidth may be too great and so the reinforcement will need upping again (crackwidth check can be found in BS8007 Aqueous media retention). this can lead to a great deal of additional reinforcement
  • note that, under the imposed load codes, the balconies are subject to the same loading as the room that they adjoin. this generally means that the human loading onto a balcony is the defining loadcase and not the self weight. we can try to make the cantilever look better by tapering it (it's not that much more expensive to do this although some contractors inititally baulk at the idea) but this does not solve the main thrust of the problem.
  • in terms of the rainwater flowing off the balcony, the deflection under self weight can be significant enough to alter the flow path that you inititally created i.e. the water doesn't drain from the balcony leading to algae and possible attacks on the reinforcement.

Finally a word on prestressing, for a small balcony of 3m it would be, my first thought, an expensive solution and would be quite difficult to put into place.

On the other hand, it could be made as a precast piece with the rods pretightened prior to the pour and then released after 14 days. This is how they make beams for the beam and block industry which give them a precamber of about 1/500 (?). However, this leaves you with a large piece of concrete to put in place and some long bits of rebar poking out.

At least in Malaysia you shouldn't have too much of a problem with thermal bridging.

Sorry this was a bit long winded.

__________________
omw7
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#4
In reply to #3

Re: Cantilever beam is so thick - looking for counter proposal

12/28/2007 12:10 PM

Have you looked at steel and stucco?

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member Safety - Hazmat - New Member

Join Date: Dec 2007
Posts: 125
Good Answers: 1
#5
In reply to #3

Re: Cantilever beam is so thick - looking for counter proposal

12/28/2007 1:57 PM

Awesome answer. Including the "water damage potential" was added value.

I presumed it was steel to begin with: but since it was not, perhaps it is an option..

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#6

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

12/28/2007 2:37 PM

I assume this is a concrete beam and not a slab that is 450 mm thick. Prestressing the beam is a process of tensioning cables that reinforce the beam inside, placing a compressive force across the entire concrete beam length (since concrete is much stronger under compression, this allows the cables to offset some of the tension on the concrete and increases the compression). This could improve the strength of the structural support from the beams, but 18" is not a particularly thick concrete beam, and you'll need a certain cross-sectional thickness of the beam to add support against the applied bending forces. so, you may not save much thickness by prestressing (maybe a few inches). A good alternative to reduce the beam thickness is to use a Steel beam instead of concrete. You can then cover the beam in stucco or grout just for the aesthetic appearance. Use of a Steel I Beam will require changes to the connections to the supporting structural bearing wall. You can reduce the thickness of a beam a lot by using steel instead of concrete, but you'd still probably need a beam at least 6" thick, and then add any aesthetic covering.

Register to Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#7

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

12/28/2007 11:04 PM

I don't think that a prestressed beam is the most economical, at least not in my neck of the woods. But if you do want a prestressed concrete beam, the methodology is well known.

What is the length of cantilever? What is the tieback span? How much roof, floor or combination of roof and floors does the beam carry, that is, what is the tributary width?

A timber beam or steel beam may be a more economical alternative. Hard to say without seeing your drawings.

__________________
Bruce
Register to Reply
Anonymous Poster
#8

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

12/29/2007 12:43 AM

Hi everyone ,

Thanks for all the feedbacks. I am yet to receive my consultant's alternative design. Will keep you posted on the final decision.

Thanks again

Regards

Dave

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#9

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

12/29/2007 5:39 AM

Can anyone help me:

Lot many can:--if only you send drawing of the design you referred to:

Cross section of slab through this 450 thick cantilever beam>the both end supported beam/s,columns, other end cantilever beams.All dimensions,rebars,bend reversals.

If you begin with solid thick heavy concrete slab/s, and long free-hanging ends you may indeed need heavy/deep highly reinforced beams.

If you had opted for hollow precast light-concrete slabs and short freehangs--your home building could have cost 1/4>1/6th.And a lot safer on earthquakes. Lot better insulated too. Like mine-which I designed/built in 1985.AND you would have not bothered to eventhink of prestressing--because NET saving would have been small.

Register to Reply
Anonymous Poster
#10

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

12/29/2007 6:13 AM

I think he's asking for someone to describe the process of pre-stressing. Too busy right now so I'll leave it to someone else. It's surprising that a consultant who would recommend so involved and capital intensive a process would not be able to describe the process for the client. Maybe a second-consultant opinion is advisable. Better Malay house description would be helpful too. Including whether the beam is new construction or retrofit for some purpose.

Register to Reply
Anonymous Poster
#12

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

12/30/2007 8:41 AM

It is hard to know just what kind of answer you are seeking. You mention a consultant but also speak of a friend. Are these one and the same person? If not, is your friend's advise based on some notion that (provided the required tools can be gotten) you, yourself, or some small house construction company--or buddies/relatives--will attempt the pre-stress prep and pour? If so, I see that as strongly ill advised, especially where you are located--where, in some provinces, shoddy construction techniques are as much the rule as the exception. Your quest for answers, including answers about preliminary engineering analysis, should--no, must--begin with a respected, commercial construction firm with well-established engineering reputation and previous experience with this construction method.

As I understand, pre stressing of concrete is based on the principles, that concrete reaches greatest strength with increasing cure time and increasing compression loading. The idea behind compressing (pre stressing) during initial cure is that less concrete, and less weight of concrete, can do the same job as a greater amount without pre stressing. For one, a pre-stressed concrete beam might serve where space does not otherwise permit for a non-pre-stressed beam. The trade, as I see it, would also involve the cost of one versus the other method of pour; but pre stressing is normally done, even though more costly, because the extra cost is justified by technical/design/architectural factors. For all but very few residences, the additional cost (engineering studies and implementation) is probably not justified. Again, the best way to find out is to go ahead and solicit a proposal and bid...for both methods.

Cal

Register to Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member Safety - Hazmat - New Member

Join Date: Dec 2007
Posts: 125
Good Answers: 1
#13

Re: Cantilever Beam is So Thick - Looking For Counter Proposal

01/02/2008 1:56 PM

The principal role of prestressing ( as i recall..) is to assure that the entirity of the width of the beam remains in compression when bending loads are placed on it.

Register to Reply
Register to Reply 13 comments