Level Calibration Range

02/22/2008 5:04 PM

Hi,

I'm confused with a range calculation for a level transmitter in a DEA Contactor Vessel.

We have two products in the vessel, DEA and HC. The DEA Specific gravity is 1.05.

My reference Level is 105". How I can calculate the instrument calibration range for the level interface?.

The transmitter pressure type level transmitter with two legs.

I appreciate your help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: Level Calibration Range

02/23/2008 7:46 AM

I posted this before in another thread so here it is again.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Member

Join Date: Jan 2008
Location: Tanzania
Posts: 7
#2
In reply to #1

Re: Level Calibration Range

02/23/2008 7:34 PM

If that vessel is non pressurised,then no need to go for 2 legs..

Just multiply the specific gravity(g) of medium with maximum height of the medium(h), that is the range for ur transmitter....

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#3
In reply to #2

Re: Level Calibration Range

02/23/2008 8:37 PM

The original question involved two legs. Why provide an answer to a question that wasn't asked?

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: Level Calibration Range

02/26/2008 9:27 AM

That's OK provided one can neglect the changes in barometric pressure caused by local weather variations. In a small vessel, it can introduce a large error.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Feb 2008
Location: Mexico
Posts: 10
#4

Re: Level Calibration Range

02/24/2008 1:09 AM

Hi, Romer. hope this helps you:

As I understand the calibration problem, you have a vessel with the measuring leg always full of liquid: 100% DEA, 100% HC or something in between.

Also, from your drawing, the physical distance between high pressure and low pressure instrument taps is 105". For ease of calculation, I'm gonna use 100".

In order to obtain calibration range, we need the HC specific gravity. You don't give it, so let's say it's 0.75 (some sort of light gas oil?).

O.K., here goes:

0% (zero) of transmitter is 100" X 0.75 = 75 inches equivalent water column.

This happens when the distance between taps is full of the lighter liquid: HC.

100% (URV) of transmitter is 100" X 1.05 = 105" WC. }

This results when the measuring leg is full of the heavier liquid: DEA.

Transmitter span is 30" WC.

With this calibration, 0 to 100% of transmitter gives interface level from lower (hi pressure) tap to higher (low pressure) tap.

For an interface height of H", transmitter % lecture will be:

% = (Hx1.05 + (100 - H)x0.75 -75) x 100 / 30

You can check it out with several examples of interface height.

-------------------------------------------------------------------------------

Things to watch out for: 1-) Emulsification of the two liquids in the interface region = imprecision 2-) very similar specific gravities in the upper and lower liquids = very small calibration range.

__________________
Nestor, a.k.a. Agridulce
Register to Reply
Member

Join Date: Feb 2008
Posts: 8
#7
In reply to #4

Re: Level Calibration Range

02/26/2008 3:19 PM

Nestor,

Thank you by your help. We calibrated the trasnmitter with your calculation and is working well.

Regards,

Romer.

Register to Reply
Participant

Join Date: Feb 2008
Posts: 4
#5

Re: Level Calibration Range

02/24/2008 4:59 PM

Hi,

Just remember that if the 105" is the range, the differential pressure corresponding to that is multiplied by the density, with consistent units. The density of the DEA is Density of water x the Sp. Gr. Therefore expect the 105" to be:

Diff. Pressure = H, in Ft * D #/Ft^3 * S.G. = press diff , in psf or divide by 144 to get psi.

Diff. Pressure = (105"/12")ft*(62.4 #/ft^3)* 1.05 = 573.3 psfd, = 3.98 psid

Here' some shortcuts

1. Convert Differential Head of Fluid to equivalent Head of Water by multiplying w/ S.G.

Ex. Diff Head = 105" DEA = 105" * 1.05 = 110.25" water = 9.19 Ft Water

2. Divide Diff Head in ft of water by 2.31 to get psid. ( 2.31 =144/62.4)

Ex. Diff Pressure = 9.19/2.31 = 3.98 psid

The reasons I gave all the above workout is that you might be looking for answers in different units.

Summary:

Given: 105 " DEA fluid, S.G. = 1.05

Diffential Head in INCHES Water = 110.25 Inches of Water

Diffential Head in Ft Water = 9.19 Ft

Differential Pressure, psi =3.98 psi

Good Luck

Register to Reply