electrical installations..

03/09/2008 3:11 AM

can a industrial dryer(3phase 415v) burn if the neutral is loose?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: electrical installations..

03/09/2008 3:31 AM

Hello domanic

You ask <"...can the dryer burn...."> ?

To what actual "burn" are your referring ?

1. Do you meant to ask: Do the dryer motor or elements burn out ?

2. Or Do you mean: Does the Dryer catch Fire ?

3. Or do you mean: Does the dryer burn what it is drying ?

I do not see the circuit diagram shown.

You do not advise where exactly <"...the neutral is loose..."> It may be at the substation, the meter, the main switchboard, the distribution switchboard, the contactor, or at the elements, if all equal resistances and connected in star - we do not know, and that means nobody can say, with certainty.

Some 3 phase 415 Volt dryers require a neutral, some do not, and until your reply with further information, it is impossible to correctly advise you.

If you have a commercially made dryer in mind, advise Make + Model, along with the size in kW of the dryer, and we may be able to assist you.

Please reply here, with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Participant

Join Date: Mar 2008
Location: FIJI Islands.
Posts: 2
#2
In reply to #1

Re: electrical installations..

03/09/2008 7:31 PM

thanks for the reply..The circuit starts from the sub-board,then to the isolater and then to the contactor box in the dryer which have heating elements as well as motors connected in star...from my experience in a house single phase or 3phase..when neutral loose at the entry box or if its broken on the service mains then could lead to house shocking.but for 3phase(415v) equipements im not sure...esp dryers in hotels...i mean catch fire.....not burn....because i found that the neutral was loose at the contactor box...not from the subboard...i know that if neutral is missing then current diverts to earth...somtime if earth resistance isnt good equipements heat up...im not sure im just learning...let me know what you think...

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#3
In reply to #2

Re: electrical installations..

03/09/2008 11:39 PM

domanic,

Just tighten it.

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Participant

Join Date: Jan 2008
Location: Clinton Township, MI., USA
Posts: 1
#4

Re: electrical installations..

03/10/2008 12:21 AM

Let's assume the electrical service is a 415V line-to-line, 3 phase, Wye connected, with 240v present from each line to the neutral.

Now assume the 3 phase motor draws a perfectly-balanced 3 phase current and the current in the neutral lead is therefore "zero" amps. Then, since there is "no" neutral current, there are no watts dissipated in the high-resistance, loose, neutral.

If the dryer load was not balanced due to some single phase loading such as a control circuit, there could be some current flow in the neutral lead. Depending upon the resistance of the loose connection, some heat could be created in the connection. How much heat depends on the current flow in the neutral and the resistance of the loose connection. If the current and resistance are high enough, enough power can be present in the connection to melt the conductor materials in the connection. That could cause some problems. It is best to make sure neutral connections, like all electrical connections, are tight and do not form high-resistance. Be safe!

Some one else may address the safety issues that might arise if the motor winding fails to the enclosure.

Register to Reply
Member
India - Member - New Member

Join Date: Mar 2008
Location: Mumbai, India
Posts: 5
#5
In reply to #4

Re: electrical installations..

03/10/2008 1:53 AM

hi Jim,

All your statements are coinvincing. but,,

I am just curious to know if the neutral connection at contactor box is loose, how will it cause dryer to catch fire.?

Regards,

Vikas.

Register to Reply
2
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#8
In reply to #5

Re: electrical installations..

03/11/2008 2:09 AM

Hi Vikas,

In three phase heater connection the heaters may be star connected and it may not be necessary that the load is balanced. If the neutral is loose or disconnected there will be neutral shifting. This will cause higher voltage in a set of elements in one phase and this can cause elements to fuse. The fusing of some elements cause further un balance. The higher voltage can cause flash over or sparks resulting in triggering a fire. These are all assumptions and presumptions. The actual cause can be found out only after on site investigation.

Register to Reply Good Answer (Score 2)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#6

Re: electrical installations..

03/10/2008 5:42 AM

Electricians discuss problems Over SCHEMATICS/ MULTIPHASE DIAGRAMS.

three-phase motors do not have neutral connected to their windings, heaters could, controls with 240V yes.

To be sure all tips have value for your trouble-shooting the best way is to enclose diagram(s) in your request.

Register to Reply
Anonymous Poster
#7

Re: electrical installations..

03/10/2008 8:42 AM

If the heating elements are rated at 200 volts nominal and 4 wire Wye connected for parallel operation and control of the heating elements, the loss of the neutral will make the connection between the heating elements series connected. This shouldn't burn out the elements but will negate individual control of the elements. Check for high resistance connection which might burn out the connections to the elements.

Register to Reply
Register to Reply 8 comments