Anonymous Poster

Carrier Chillers (5H120) Comp.

04/29/2008 8:51 PM

Looking for information on how to adjust the capacity control on a 5H120 comp. It has 12 unloaders and is an R-22 unit, it was a custom built system in probaly 1955 so the actual tonnage I can't be sure about but I'm guessing about 75 tons. It has a water cooled condensor and chiller barrel. Any help would be greatly appriciated.

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Commentator

Join Date: Dec 2005
Posts: 92
Good Answers: 5
#1

Re: Carrier Chillers (5H120) Comp.

04/30/2008 2:13 AM

The actual tonnage is 120. It has six heads so starting from the seal end the head in the middle is the first to unload both pistons, then the head on the left, both pistons then the head on the right both pistons, finally one pistin in the front on the left head and one piston on the right front head togather, that is the 4 steps. The capacity control in in the front covered with a hex nut that is removed to exposed a square 1/4" stem that you turnclockwise to load. Use an amp probe on one leg the see it load and unload as you adjust the capacity control. If it hasn't been serviced for over a couple of years and has had a lot of service you may have to replace all the "O" rings in the unloaders. they have a tendency to wear and get flat where they will not load anymore also be aware that the unloaders get worn and get groved and have to be replaced.

Reply Good Answer (Score 2)
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#2
In reply to #1

Re: Carrier Chillers (5H120) Comp.

05/01/2008 3:34 PM

Shogun good job.

Yes the nominal tonnage is 120 usually with a 125 hp open drive running the tonnage to 123 fully loaded. Uloaded 60 tons.

The 120 is the short stroke comp usually installed in multi evaps DX systems with small RA shafts. The 126 is long stroke and it nominal tonnage 132 tons used in class a1 style of buildings, that have large RA plenums and usually one large DX coil with multiple passes.

The capicity controller is located in the front of the compressor by the oil pump housing. If you have oil problems be sure to check the oil regulator, they always seem to get plugged up reducing the pressure to unloaders and increasing it to the journals and running higher amps from the journal load.

When you set the unloaders do not just use an amp meter use your gauges as well. The compressor should begin to unload at 58 pounds. If you run it lower you will loose efficencicy in the evaporators and tend to slug or ice. 58 pounds should also bring on HG if it is present.

General rule of thumb for unloaders is 58 to 75-78. After that you will need to begin to load again so that you do not loose effiencify at the high end.

__________________
To be or not to be........ok that's a trick question.
Reply Score 1 for Good Answer
Participant

Join Date: Apr 2008
Posts: 3
#3
In reply to #1

Re: Carrier Chillers (5H120) Comp.

05/08/2008 10:34 PM

I took over the service work 2 years ago and accorrding to the service records the annual service has been kept up and they are used regulaly during cooling season. What are some symptoms I can look for that will tell me that it might be time for an O-ring and/or unloader replacement. By the way thanks for both answers, they will deffinately help me with PM and CM.

Reply
Commentator

Join Date: Dec 2005
Posts: 92
Good Answers: 5
#4
In reply to #3

Re: Carrier Chillers (5H120) Comp.

05/09/2008 1:09 AM

edit

Reply
Commentator

Join Date: Dec 2005
Posts: 92
Good Answers: 5
#5
In reply to #4

Re: Carrier Chillers (5H120) Comp.

05/09/2008 1:41 AM

Please excuse me as I made a major mistake with regards to "O" rimgs on the Carrier 5H120. It doesn't have "O" rings ...I was thinking of the Trane "B" compressor so no need to worry about it. The Charier 5H 120 has unloader power elements with unloader forks that lift an unloader sleeve which lift the pins to lift the suction valves off the seat. I have never had to repair one. Again Please accept my apologies. If I were you I would try to get ahold of a Manual on the 5 H series.

Roger

Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#6
In reply to #5

Re: Carrier Chillers (5H120) Comp.

05/09/2008 11:41 AM

The next time you go into an EBward, Valair, United tech, Store go to the literature rack and get the free manual for the 5H120 Comps. They used to give them away when I was wrenching back in the late 80's. The manual is just the Service manual, but it has all the specs you require.

__________________
To be or not to be........ok that's a trick question.
Reply Score 1 for Good Answer
Participant

Join Date: Apr 2008
Posts: 3
#8
In reply to #6

Re: Carrier Chillers (5H120) Comp.

05/10/2008 2:36 AM

Thanks for the information, do they have a web site?

Reply
Participant

Join Date: Apr 2008
Posts: 3
#7
In reply to #5

Re: Carrier Chillers (5H120) Comp.

05/10/2008 2:35 AM

No problem, I got alot out of your answer. it sounds like you know your chillers. Thanks again.

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

FMT (3); shogun7 (3); Stedou73ish (2)

Previous in Forum: piezoelectric pump   Next in Forum: LiquidAir Energy Group (LAEG)

Advertisement