impedance of traformer

07/08/2008 5:05 AM

In case of ONAN/ONAF (say 20/25 MVA) transformer, Its percentage impedance is based on which rating 20MVA or 25 MVA?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: May 2008
Posts: 13
#1

Re: impedance of traformer

07/08/2008 5:15 AM

20MVA which is the 100% rating of the tx....The ONAF rating is 125% of the normal tx rating.

__________________
Availalbe for short term contracts, by the hour, day or week to help you be successful.
Reply
Participant

Join Date: Jul 2008
Posts: 2
#2
In reply to #1

Re: impedance of traformer

07/08/2008 5:36 AM

But when you specify for ONAN/ ONAF transformer in your specification, Manufacturer will design transformer ( ie conductor size ,core size etc and hence resistance and reactance ) based on ONAF rating ,hence i think impedance is based on ONAF rating?

What do you say?

Reply
Anonymous Poster
#3

Re: impedance of traformer

07/08/2008 4:01 PM

Per IEEE red book and ANSI C57 you always use the self cooled rating for all calculations. 20 MVA

Reply
Participant

Join Date: Jul 2008
Posts: 2
#5
In reply to #3

Re: impedance of traformer

07/09/2008 2:00 AM

But Transformer design (that is determination of resistance and reactance and hence impedance ) will be on which rating ONAN or ONAF?. As higher MVA rating (ONAF) will cause more current. As current will decide decide conductor size hence resistance , and Higher MMF (Ampere turns ) will also affect the reactance (ie design of core, and clearances etc).

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: impedance of traformer

07/08/2008 6:53 PM

You use the self cooled rating 20 MVA. Do you know how the %Z is determined?

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: impedance of traformer

07/10/2008 3:59 AM

It is always the base rating ie 20MVA

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#7
In reply to #6

Re: impedance of traformer

12/16/2008 2:45 AM

The % impedence whether on 20 MVA or 25 MVA depends upon which standard (IEC or ANSI) is used by transformer manufacturer. % impedence is on the base rating (self cooled rating ) as per IEEE red book or C57.12.01. Even the rated KVA of transformer is output power at rated secondary voltage for transformer manufactured as per ANSI. For transformers manufactured as per IEC (almost entire world except USA) the rated KVA is the highest KVA rating (In our case 25 MVA) and it is the input KVA of the transformer. As per IEC manufacturer has to specify the impedence alongwith KVA (on which it is based). Normally it is based on rated KVA which is highest KVA rating of the transformer for IEC based transformers.

Reply