Calculating DC Withstand Voltage on a Power Connector

07/09/2008 12:54 PM

Hello Everyone.

This might be a simple question, but I'm not sure how to calculate the DC Withstand voltage from the AC Withstand voltage for a power connector. All I have to go with are the manufacturer's spec sheet. The power connector is a shielded metal can with + and GND pins inside the can.

The Spec sheets gives me the following numbers, AC withstand voltage 1800V AC for 1 minute, Current rating 5A, Insulation resistance is 1000M ohm.

Now, I want a working voltage of 18.5VDC and 3A so my guess is this connector looks to be able to handle my requirements fine.

But, how would I calculate the maximum DC withstand voltage for this connector? If at a later time the answer was not as clear, or if it was a requirement to state the maximum DC voltage for the connector/product?

Thanks all.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#1

Re: Calculating DC Withstand Voltage on a Power Connector

07/09/2008 1:36 PM

Assuming the spec is 1800 vrms , the DC withstand would be about 2500 vdc.

You have plenty of safety margin.

__________________
Charlie don't surf.
Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#2
In reply to #1

Re: Calculating DC Withstand Voltage on a Power Connector

07/09/2008 4:19 PM

That is the thing, it doesn't specify Vrms but AC which is a little different. Wouldn't the dielectric charactistics of the insulator come into play?

For example, another connector I found, had specifactions of 500VAC withstand voltage at 5amps and than states that the maximum DC contact voltage is 12Volts? So the solution can't be that simple. :)

Register to Reply
Anonymous Poster
#3

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 1:51 AM

please see IEC 60947-1 where u will get ur answer, normaly V ac = 1.41 V dc, so for 1 kv ac is equivalent to 1410 v dc,

please refere the standar, u will make it very clear for the same

regards

divyesh patel

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#10
In reply to #3

Re: Calculating DC Withstand Voltage on a Power Connector

07/11/2008 12:32 PM

IEC 60947-1 is $314 for a paper? To rich for my blood and I doubt my company would pay for that, just for interest's sake.

Register to Reply
2
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#4

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 7:21 AM

While, the 1.41X ACV is a good theoretical guess. Remember the old saying,"nothing is quite as simple as it seems"

Are you going to use this connector for switch duty?

If so the DC voltage limit is actually much lower than the AC voltage limit as well as the current rating. I have seen many connectors Rated say at 50A @ 600VAC yet 50A @ only 250VDC

It has to do with arcing at the contacts. If you try to disconnect under power the current will try to keep flowing. ie draw an arc when the circuit is broken. With DC this can be quite a large and destructive arc. The AC the wave form is passing through zero at regular intervals, so th arc problem is not as serious. Hence a higher voltage and current rating for AC than DC.

At the voltage and current levels you are talking about here, (18.5v 3A) there should be little problem. I just wanted to clarify for any one reading, that simply using a blanket 1.414 times the AC rating can be dangerous.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2008
Posts: 10
#5
In reply to #4

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 9:40 AM

Ok, the arching makes sense why the VDC withstand voltage is less than the VAC and the current would play a big part of this. The application is a power plug being inserted into a socket, so arching would need to taken into consideration, but there is no actual switching done in the connector.

I'll have to grab a book on quantum physics to read this summer, seems that's the way electronics is heading...lol.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#6
In reply to #5

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 9:54 AM

DC voltage is much harder to handle than AC because of the lack of zero crossing that extinguishes the coronas just before an arc is ignited. This becomes even more important in applications where the connector is exposed to dearth and humidity. Over time, the DC will ionises a track of dearth between the contacts and arc over. AC does this much less.

Below about 100VDC, the equivalent AC rating is often used but above this one must be very careful. The dc rating is quickly limited while the AC rating can increase.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#7
In reply to #5

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 10:43 AM

" but there is no actual switching done in the connector."

Maybe I should have clarified that a little. When I referred to using the connector for switch duty, I merely meant connecting and disconnnecting under power. Not an actual switch in the connector.

Although, the Brits and Australians do have a good system of switches in their sockets. So you don't (thoeretically, at least) plug and unplug under power.

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#11
In reply to #7

Re: Calculating DC Withstand Voltage on a Power Connector

07/11/2008 12:35 PM

ok, thanks for clarifying because there are power connectors which have a mechanical switch inside. :)

We have to expect the customer will plug in wall outlet before the device so yes the connector will have switch duty, but in most cases the product would not be moved so the switch duty should be fairly light.

Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#12
In reply to #11

Re: Calculating DC Withstand Voltage on a Power Connector

07/11/2008 1:19 PM

No problem.

Like I said earlier, 18.5V@3A? You could probably plug and unplug that connector (under power) all day long with no problems. My comment on switch duty really only applies at higher voltage and/or current levels. (ie tens to hundreds of amps and/or around a hundred volts and higher.)

Cheers

Register to Reply
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#8

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 2:19 PM

ianr is correct, 1.41xAC is a maximum. further derating must be done especially with an inductive load.

__________________
Charlie don't surf.
Register to Reply
Anonymous Poster
#9

Re: Calculating DC Withstand Voltage on a Power Connector

07/10/2008 11:15 PM

hi to all

i have gone through the answeres received from all, but connectors are only associated with continuous carring capacith, they are never been associated with its making and breaking capacity, yes but maximum carring capacity can be assigned to them, so with irrespective of rated operational voltage, connectors are more importantly rated by their rated insulation voltage perticularly at DC when AC rating is defined.

and if AC swtiching devices are intended to use at DC supply, they required to change its design because in DC breaking is more painfull for device, which depends on time constant of load, speed of opening of contact, contact tip and its material, distance between contact and laste but not least on arc chutes used.

so kindly refere IEC 60947-1, EN 60947-1 or CSA,IS or japaness standard specifies that DC = 1.41 * AC

regards

divyesh patel

X employee of ERDA (Switchgear), currently working in Bombardier Transportation India Ltd. (Test lab)

Register to Reply
Register to Reply 12 comments