Pebbles in switchyard

11/17/2008 10:27 AM

why we use pebbles /stones of 100mm mesh size in 220KV switchyards??i want to know the technical reason.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Pebbles in switchyard

11/17/2008 10:46 AM

The technique offers a good ratio of appearance quality divided by cost-per-unit-area of all the combinations of providing ground cover where the under-surface is of poor aesthetics. It will be found that vegetation has difficulty in establishing itself through this particular covering and, should it appear, it is readily and quickly removable. Drainage of surface water run-off is excellent.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#2

Re: Pebbles in switchyard

11/17/2008 5:32 PM

Way back 1980 in Saudi Arabia... This inquiry was asked during that time "Why gravel mulching (pebbles as you call it) used to cover the entire 230kV and 380kV main substation/switchyard?"

Well, they have told us (Consultants) that gravel mulch can:

* minimizes step ground potential

* easy to clean once there is spill of oil and any chemicals

* uniformity of design criteria based on international requirements.

You see those replies? There is no technical matters, except for step ground potential. I have made some inquiry and research also on this. Through my engineering experience... It really for grounding system only.

Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#5
In reply to #2

Re: Pebbles in switchyard

11/18/2008 8:41 AM

Dear Sir,

Apart from increasing surface resistivity , preventing flow of trafo( split oils),preventing growth of weeds ,yetanother reason is that reptiles will not move fast if Switchyard surface is covered by pebbles

V.Ambarani

__________________
Best Regards
Register to Reply
4
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#3

Re: Pebbles in switchyard

11/17/2008 6:33 PM

From IEEE 80

7.4 Effect of a thin layer of surface material

A 0.08–0.15 m (3–6 in) layer of high resistivity material, such as gravel, is often spread on the earth's surface above the ground grid to increase the contact resistance between the soil and the feet of persons in the substation. The relatively shallow depth of the surface material, as compared to the equivalent radius of the foot, precludes the assumption of uniform resistivity in the vertical direction when computing the ground resistance of the feet. However, for a person in the substation area, the surface material can be assumed to be of infinite extent in the lateral direction. If the underlying soil has a lower resistivity than the surface material, only some grid current will go upward into the thin layer of the surface material, and the surface voltage will be very nearly the same as that without the surface material. The current through the body will be lowered considerably with the addition of the surface material because of the greater contact resistance between the earth and the feet. However, this resistance may be considerably less than that of a surface layer thick enough to assume uniform resistivity in all directions. The reduction depends on the relative values of the soil and the surface material resistivities, and on the thickness of the surface material. Covering the surface with a material of high resistivity is very valuable in reducing shock currents. The value of this layer in reducing shock currents is not always fully realized. Tests by Bodier at a substation in France showed that the river gravel used as yard surfacing when moistened had a resistivity of 5000 Ω·m. A layer 0.1–0.15 m (4–6 in) thick decreased the danger factor (ratio of body to short-circuit current) by a ratio of 10:1, as compared to the natural moist ground. Tests by Langer in Germany compared body currents when touching a hydrant while standing on wet coarse gravel of 6000 Ω·m resistivity with body currents while standing on dry sod. The current in the case of dry sod was of the order of 20 times the value for wet coarse gravel. Tests reported by others provide further confirmation of these benefits .

In basing calculations on the use of a layer of clean surface material or gravel, consideration should be given to the possibility that insulation may become impaired in part through filling of voids by compression of the lowest ballast layers into the soil beneath by material from subsequent excavations, if not carefully removed, and in some areas by settlement of airborne dust. The range of resistivity values for the surface material layer depends on many factors, some of which are kinds of stone, size, condition of stone (that is, clean or with fines), amount and type of moisture content, atmospheric contamination, etc.

If you need the equations and details, I suggest you read IEEE 80. When I did substation design I would spec granite fractured on three sides, at what ever size the client preferred. Some liked large some small. There are limits in size though. It is where the points of the rocks touched other rocks in the layer that caused the high resistance areas. This is definitely not considered to be decorative rock. I always looked at railroad track ballast rock as something that would have been good substation cover, probably because it is fractured on all sides. Be careful to inspect what you get sometimes it will be different from what you ordered. Remember each time it goes through the crusher it costs the vendor more. If you are not paying attention then it is more profit for him

Register to Reply Good Answer (Score 4)
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#4
In reply to #3

Re: Pebbles in switchyard

11/18/2008 4:09 AM

It is where the points of the rocks touched other rocks in the layer that caused the high resistance areas.

That's interesting: if you're trying to make a low impedance contact in a connector that's exactly what you try to do. I guess that the higher resistance of the section near the point becomes the overriding factor in this case?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#8
In reply to #4

Re: Pebbles in switchyard

11/18/2008 11:14 AM

I think it kind of makes sense when you think you resistivity from the physics point of view. The divisor is the area. If smaller, the resistance goes up and larger, the reisistance goes down. Per IEEE 80 the rock makes it about 20 times less likely you will be electrocuted. That is under worst case conditions. Who ever called for a switching order on a beautiful evening, or because things were just working too well?

Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#9
In reply to #3

Re: Pebbles in switchyard

11/18/2008 11:49 AM

I voted you a "good answer" only because there's no "great answer" option! But whomever mentioned easier cleanup of spilled transformer oil was right about that, too. The oil will adsorb to the surface of the rock and less soil contamination underneath will occur.

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply
Guru

Join Date: Mar 2008
Location: Sebring, Florida
Posts: 923
Good Answers: 25
#10
In reply to #9

Re: Pebbles in switchyard

11/18/2008 12:36 PM

I just think that we see things a little differently. I always prefer the simple answer over the lengthy complex ones. Seems I never could get away from having to add B---S--- to my term papers just to make them long enough to get a passing grade.

TMF

__________________
The only problem with common sense, is that not very many people have it, or know how or when to use it.
Register to Reply
Anonymous Poster
#6

Re: Pebbles in switchyard

11/18/2008 8:58 AM

It makes it easier to find your nads if you get them blown off...

Register to Reply
Guru

Join Date: Mar 2008
Location: Sebring, Florida
Posts: 923
Good Answers: 25
#7

Re: Pebbles in switchyard

11/18/2008 9:19 AM

Smaller sized materials will compress and pack tighter thus producing greater resistance to movement. Rail road switch yards under go stresses when the cars are being moved from one line to another, even though it is done slowly. By using the smaller gravel the track and ties remain in place much better. Just imagine the ramifications of having the frogs moving all over the place in a switch yard with several hundred switch tracks.

TMF

__________________
The only problem with common sense, is that not very many people have it, or know how or when to use it.
Register to Reply
Register to Reply 10 comments