Allen-Bradley 480VAC Motor Drives Conking Out

12/11/2008 3:58 PM

A strange thing has been happening at our plant the past 6 months . A little background . The drive panels I'm talking about are all designed the same and were installed in 3 different areas of the building . All 3 panels operate motors on the same type of machinery . The panels contain an AB SLC-500 processor/ I/O modules and 2 - 1 hp. 480VAC drives (Cat.# 22A-D2P3N104) . The AB drives for one specific area are powered by the same circuit . On 3 different occasions , 3 different drives crapped out in the 3 different areas of the building , one in each panel . After the 480V circuit was LOTO and the drive replaced and the power restored , the other drive that was NOT worked on came back up dead , totally caput , and also had to be replaced . Why this is happening is driving us mechanics crazy . I'm thinking maybe a power surge when power is restored (but why wouldn't it affect the newly installed one ?) . Others are thinking it's an AB ploy to get us to buy more drives . There is a 4th. panel that hasn't had any problems yet . Any input would be great . Thanks in advance .

Tim

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#1

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/11/2008 9:00 PM

Depends on what failed--- Shorted input diode or filters would point to bad AC input line. Perhaps not enough input impedance. Typically small drives need to be isolated from stiff power sources. An input reactor or drive isolation transformer is the best solution.

Output transistors shorted could point to motor problems, or application problem.

Avoid starting into a rotating load, or having a overhauling load, causing the motor to become a generator, basically overpowering the drive. Either of these conditions can be handled by most drives with the proper setup.

As far as an A/B ploy... I would think planned failures, or inferior products would prevent repeat business, not encourage it.

Good luck.

Register to Reply Good Answer (Score 2)
3
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#2

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/12/2008 1:16 AM

Not knowing your system makes a decent answer difficult. Generically, the info Mevel123 gave you is quite right.

I know the AB Flex drives and have about 40 of them in my plant. I have a few of the bigger flex 70 units but mostly the little ones. I like the Flex 4 and 40 both...not as tough as the old 1336 but pretty reliable...but I have definitely killed a few and had to sort out some load issues. Even had the local AB rep in ripping him a new one trying to figure out some issues I was sure was his. They weren't.

Obviously I don't know your line or load characteristics. Maybe you need reactor packs on. I will say that out of the maybe 50 times I've heard my AB rep and local sales geek tell me "you should probably put a reactor on there" I never have and I've solved each problem child. Been about 13 or 14 months since I've lost a drive.

A few things I have experienced: Meggering... don't megger these things...they really don't like it and even if they appear to survive they are usually done for if you meg a 480 circuit at 1000v. Might take them a bit to die but they definitely are degraded if your guys start insulation testing without fully isolating the drive.

Hard ramping up or down is tough on the flex but for 500 bucks you sometimes take the lumps for the benefits. Depending on your load the Flex will fault off on buss overvolt if you ramp down real hard and too fast with a heavy load. Regardless of what your AB rep says this definitely appears to shorten the life span. I.E. I had a 5 horse drive running acme screws that I was running at about 110hz. Run past a prox and ramp down hard to another preset at 45hz. Ramp set at .2sec. Ran great...killed 3 drives in 3 months. Changed the ramp to .4 and haven't smoked a drive on that system for 20 months. Ramping too hard without the right torque boost curve is also hard on it. If you get right on the edge of stall you very well may be causing degradation and cause premature failure.

Now the other little animal that can be tough to solve with these and other drives. SWR...reflected power. Several things can contribute to a wicked problem. Crappy wire... long wire runs ... and mismatched motor. I had one little drive that I stuck off in an existing can, hooked up to the existing 12gauge wiring, and ran the existing old 2hp Baldor about 50 or 60 feet away. A week later the drive was dead for no obvious reason. Replaced it and 2 weeks later it faulted on F13.. ground fault. Couldn't find anything. Megged it eight different ways...nothing. A few days later blew a hole through the insulation at a spot where the wiring was bent. Fixed that...blew another hole in it again a a couple weeks later... yanked in new wire with lots of choice words. Blew again!!..smoked a happy little orange wire nut at the motor for no apparent reason. Then it smoked the motor. Grabbed a new one off the shelf. Took 3 weeks to kill that one. Stuck a Fluke scopemeter on and found I was getting about 1150 volts in a really weird looking wave. Put on a true inverter duty motor, moved the drive to a new spot about 20ft away and have never had another fault in 3 years.

Anyhow... have a laugh at your guys that think it's an AB ploy... or do what you can to stoke their conspiracy theory thoughts... and really look at the system. There is some decent info out there for isolating problems but a good common-sense troubleshooting approach while researching inverter characteristics will usually do it.

Good luck to you.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply Good Answer (Score 3)
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#3
In reply to #2

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/12/2008 9:19 AM

GA from me. I have nothing to add.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#4
In reply to #2

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/12/2008 6:07 PM

Well it's not exactly an AB ploy.

has to do with making the drives smaller & lighter. smaller heat sinks & caps. this leaves them more susceptible to damage from abuse.

Switchmans comments are very true. even on simple on/off applications, program in a little ramp up/down time if possible. Brown outs from neighboring loads

avoiding powering up & down: contactor controlling inverter is a bad plan

long runs of the output wiring=bad, the control is not as critical, mount a can as close to the motor as possible.

inverter duty motors=good

oversized drives=good, a 2 hp running a 1 hp motor, will fault out & keep running until the motor is totally fried.

Register to Reply
Associate

Join Date: Aug 2008
Location: Rochester , NY
Posts: 35
#5

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/16/2008 6:50 PM

Thanks everyone for replying with your helpful info . Although some of the stuff you talk about is a little over my head , you have given me some good ideas on how to rectify this problem . One question , how do the line reactors actually work ? I noticed in a different part of the building a drive cabinet is loaded with them . Always knew they were there , just didn't know exactly how they worked . Thanks again everyone for taking the time .

Tim

Register to Reply
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#6
In reply to #5

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/16/2008 7:39 PM

Reactors add impeadance to the AC line. Impeadance is used to reduce the rate of change of current.

Simply put- It filters the AC line; or if used on output of drive it will filter the current waveform 'seen' by the motor, and reduce harmonics that tend to be wasted power.

Adding impeadance is sometimes refered to as 'softening' the line. A stiff AC line will produce spikes for every disturbance on the line. (ie. switching loads)

Imagine a car without shock absorbers- It runs fine on a smooth road at any speed. Add bumps to the road, and you must slow down to keep control, or add shocks to absorb the bumps. A stiff AC line gets 'upset' for every bump, and these spikes 'wear out' the drive input filtering.

There is a whole science on AC line analysis-and it is very complicated, and very unecessary for most industrial troubleshooting concerns. However matching the drive to the ac supply is important-- Typically drives have a spec for max input supply KVA.

Also a big concern is large ratio step down transformers-- For instance a drive will work fine on a 460 to 240V xfmr; but the same drive will not work on a 2300 to 240V xfmr without adding additional filtering (swamping networks)

Hope this helps

Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#7
In reply to #6

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/17/2008 1:20 PM

Much more simply

motors are inductive loads

Capacitors are used to balance the load

if the load is inductive the voltage wave leads the current waveform

if the load is capacitive the current leads the voltage wave form

A simple way to remember is ELI E=voltage, L=inductor, I=current

ICE I=current, C=capacitive, E=Voltage

The more balanced the load the more efficent the transfer of energy.

if the balance is really off you will let all the smoke out of the drive or windings.

you would then need to contact KrisDel for replacement smoke [tongue firmly in cheek]

Register to Reply
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#8
In reply to #7

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/17/2008 8:00 PM

He was asking about reactors- Not capacitors.

Line reactors are not used for load balancing. I do agree with what you say regarding load balancing capacitors and power factor, but disagree with the "Much more simply" statement.

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#9
In reply to #8

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/18/2008 5:13 AM

Er Uhh

Yeah actually reading woud be good......

I shall post a silly picture now to mask my embarassment

Register to Reply
Associate

Join Date: Aug 2008
Location: Rochester , NY
Posts: 35
#10

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/19/2008 4:58 PM

Mevel , thank you for the explaination on reactors , very well put and easy to understand . Garth , no need to be embarrased , even a "wrong" answer here is helpful in my gaining electrical knowledge . .....And the smoke comment , that's funny . Gonna have to remember that one !!! Thanks again .

Tim

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#11
In reply to #10

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/19/2008 9:15 PM

Well no actual embarrassment

just my way of apologizing to mevel

another way to break the tension in those high stress moments of a breakdown during production or start-up, especially if something real expensive just quit. walk up to the boss with your best poker face & say

"there was an incident"

keeping your wits about you when the whole place is falling apart is a very important skill. Act like you know what you're doing, even when you don't have a clue. Production & mgt. need to be reassured, you're on it. Real hard to figure out the problem when there's 5 bosses looking over your shoulder & everyone's convinced the sky is falling.

AB touchscreens & PLC's are the conspiracy. Todays touchscreen won't work on a 5 year old system unless you have current software which can be a bit pricey and may require programer to fix the conflicts....

Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#12

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/23/2008 12:48 PM

Sorry about being a bit behind the curve on this one but I finally found where I had stuck this link from Allen Bradley about reactors. Might not directly help but it's decent info.

http://www.ab.com/support/abdrives/documentation/techpapers/Line%20Reactors%20and%20AC%20Drives1.pdf

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Anonymous Poster
#13

Re: Allen-Bradley 480VAC Motor Drives Conking Out

12/06/2010 5:41 PM

The same problem happened in my shop. The factory rep said to remove the internal board ground clip. this seems to have solved our problem. (This is on the left side of the drive) I have 10 of these drives in and around my plant. An input line reactor is a must for these drives.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

5BANJO5 (2); Anonymous Poster (1); Garthh (4); Mevel123 (3); Switchman (2); Vulcan (1)