humming contactor 250v ac

12/13/2008 5:06 AM

i replaced a burnt out contactor that operated a 1.5 kw single phase pump ,this is the third the contactor is being replaced,the contactor i replaced with is rated 250v

though when i measured voltage across the coil it reads 214v could this drop be the reason the contactors keep humming then burning?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: humming contactor 250v ac

12/13/2008 6:57 AM
DEAR READER,

GENERALLY HUMMING OCCURES BECAUSE OF DIRTY MAGNET. CLEAN THE MAGNET OF THE CONTACTOR BY CRC 2 26 / EUIVALANT CLEANER / RUB THE MAGNET CORE CONTACT SURFACES GENTLY BY EMERY PAPER. 99% YOUR PROBLEM WOULD BE SOLVED. THEN COIL SHALL NOT BURN ALSO.

__________________
Exploring the Science of Electricity
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#2
In reply to #1

Re: humming contactor 250v ac

12/13/2008 1:05 PM

Harry please use your wand and turn CAPS LOCK off.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply Off Topic (Score 5)
Associate

Join Date: Jan 2008
Posts: 34
#3

Re: humming contactor 250v ac

12/13/2008 11:42 PM

I'd like a little more information. What exactly is burning up -- is it the coil, the points, or are the arc shields melting?

Register to Reply
2
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#4

Re: humming contactor 250v ac

12/14/2008 1:39 AM

Same with harry potter comments, dirty coil could caused the humming sound, can you also check the frequency if you are fitting correct one either 50 hz or 60 hz it should correspond on your supply frequency, consider also the magnetic contactor rating if it is rated equivalent to your 1.5 kW motor. what about the voltage drop during certain period of time? maybe the time you take across the line read 214v what about when the time the contactor burnt? could be 180 volts who knows. to summaries the following has to take into accounts; dirty contactor, frequency, rating of the magnetic contactor and voltage drop. if all of this are in order, then you should haven't problem.

Kind regards

Roman

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#5

Re: humming contactor 250v ac

12/14/2008 8:46 AM

Past experiences lead me to suggest a capacitor across the coil terminals. This will eliminate the A.C sine wave and allow for constsat voltage to pull the coil in.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6
In reply to #5

Re: humming contactor 250v ac

12/14/2008 6:10 PM

How does placing a capacitor across the coil terminals eliminate the AC sine wave?

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#8
In reply to #6

Re: humming contactor 250v ac

12/15/2008 8:47 AM

>>How does placing a capacitor across the coil terminals eliminate the AC sine wave?

By absorbing some of the energy in the sine wave as it charges and then discharges. Not perfect but it will help.

Of course the one thing missing from this whole thread is "what is the current draw?"

It's good that the contactor is rated for 250v but if the circuit is drawing too much current the contactor isn't going to last too long. Going to have to know this to size a capacitor properly as well.

__________________
Eric
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#7

Re: humming contactor 250v ac

12/15/2008 4:00 AM

Good day,

can you supply contactor specs?

make, rating, incoming 'fuse' or breaker size & how you connected it?

__________________
tHe days of good inglisH haz wented.
Register to Reply
Power-User

Join Date: Nov 2008
Posts: 158
Good Answers: 1
#9

Re: humming contactor 250v ac

12/15/2008 4:43 PM

Let's start with the knowns, which are very little. If your coil rated voltage is 250, its one I never heard of in 30 years! The COIL voltage, as with 99% of applications, needs to be + or - 10 % of the rated voltage. Need to know the AMPERAGE & HORSEPOWER ratings of the switching poles of the contactor as well as its rated voltage. Then I can help you. Also, need to know the environmental conditions and the ACTUAL measured amperage of the pump under max. load.

Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#10

Re: humming contactor 250v ac

12/15/2008 11:24 PM

Yep, sure can. If the coil is rated at 50hz and you have 60hz that will make it even worse. A 240v 50hz coil requires 277 at 60hz. If your voltage is bad the motor won't like it too much either.

AC contactors have a shading ring that holds the pole faces together as the field decays at zero crossing with low voltage the average poleface gap increases which increases the reluctance of the magnetic circuit. This in turn increases the average current in the coil, also the average contact pressure is reduced. So as you can see low control voltage leads to failure of both coil and contacts. Find the cause of low voltage and fix it. In large installations with large contactors it is often caused by a daisy chained neutral. In a stand alone 1.5kw application long runs of too small wire is the usual culprit, but check all joints and control devices. I could give you work arounds to protect the contactor but it is futile if the result is only to burn out the motor.

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#11
In reply to #10

Re: humming contactor 250v ac

12/16/2008 1:59 AM

Hi 4119, I would seriously appreciate if you could spend the time to explain how you worked out the 50/60hz & voltage thing.

kind regards,

leon.

__________________
tHe days of good inglisH haz wented.
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard